Bonding (again)

Discuss Bonding (again) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

glendower

I recently qualified and the first job I have been asked to do is put 5 spotlights in a bathroom that is being renovated. Nice straight forward job a nice little earner as they say. On looking at the new bathroom which as been re-plastered had the first fix of plumbing, the floor tiled and the shower tiled noticed that there was no bonding. Question Can I do the alteration to the lighting circuit and ignore the fact that the plumber as not bonded the pipe work. I have one set of minor works forms which ask to conform that there is bonding and one set that does not ask the question?
To answer my own question I say that the the pipe work must be bonded and I want to tell the customer to get the bathroom installation company to do it but would like to be absolutely certain because of the problems/delays that will be caused trying to put bonding in now.:mad:
 
Glen

yes it needs bonding, and no you cant ignore it

130-07-01 says 'no alteration etc.......unless the earthing and bonding are also adequate'

Of course, you could always go 17th, put all of the bathroom circuits on an RCD and then you dont need supplementary bonding.!!!!!!:D
 

Reply to Bonding (again) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock