Sparky83

Hi all,

Quick question with regards to adding new sockets to a circuit under the new regs,

Am i right in thinking that if you go to a house that has no rcd protection on it you cannot add sockets or enlarge the circuit etc without adding an rcbo to the circuit first to bring it in line with the new regs, obviously i'm talking about when the new regs are in full force.

Reason i ask is a friend of mine has some big fish tanks and he has all the various components on double rcd sockets so if a pump were to go it wouldn't take out the whole tank, so i wanted to know that if he was to want some new sockets added to the circuit would the circuit require require a rcbo at the fuse board to bring it in line with the 17th edition.??? :confused:

thanks guys
 
As I understand it, if you alter a circuit then it needs to comply with the new regs. Therefore, adding a socket into the ring or adding a spur would constitute a change to the circuit and it would therefore need to meet regs. So, assuming the cable isn't buried more than 50mm deep or has nio earthed mechanical protection then yes, an RCBO would be required in order to comply with the regs. Either that or the circuit would have to be move to the RCD protected side of a split load board.
 
As I understand it, if you alter a circuit then it needs to comply with the new regs. Therefore, adding a socket into the ring or adding a spur would constitute a change to the circuit and it would therefore need to meet regs. So, assuming the cable isn't buried more than 50mm deep or has nio earthed mechanical protection then yes, an RCBO would be required in order to comply with the regs. Either that or the circuit would have to be move to the RCD protected side of a split load board.

thought they were doing away with split load boards?
 
Hi all,

Quick question with regards to adding new sockets to a circuit under the new regs,

Am i right in thinking that if you go to a house that has no rcd protection on it you cannot add sockets or enlarge the circuit etc without adding an rcbo to the circuit first to bring it in line with the new regs, obviously i'm talking about when the new regs are in full force.

Reason i ask is a friend of mine has some big fish tanks and he has all the various components on double rcd sockets so if a pump were to go it wouldn't take out the whole tank, so i wanted to know that if he was to want some new sockets added to the circuit would the circuit require require a rcbo at the fuse board to bring it in line with the 17th edition.??? :confused:

thanks guys

any alterations/additions must comply with the new regs!

so if you were to spur off a ring main and add a new socket (assuming the cable is buried, less than 5cm etc etc)

then the SPUR cable and the SOCKET would have to be on an RCD, it doesnt automatically follow that the rest of the exisiting circuit has to be retrospectively upgraded with an RCD:p

alternatively: - spur off with a surface mounted cable (in mini trunking for example) and mark the socket 'fish tank only' - then it doesnt need an RCD;)
 

Reply to Extra sockets in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock