Is it ok to have PV system into shared (household) RCD?

Discuss Is it ok to have PV system into shared (household) RCD? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

The easiest and cheapest work round option from what I can see is to remove the right hand RCD and mcb's and replace those 3 with RCBO's then use the two slots from the RCD for the solar and charger so only costing you for 5 Hager rcbos. This would then solve the issue with the wrong MCB that has been fitted!
Personally I would do what @westward10 suggests earlier and replace the whole lot with a new SPD protected type A rcbo populated board with some spare ways in for future expansion!
Sy
The EVSE RCD must interrupt all live conductors, so a single module Hager RCBO won't meet that requirement.
 

Reply to Is it ok to have PV system into shared (household) RCD? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock