Search the forum,

Discuss Subpanel feeder breaker size? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
0
This is a solar tie in generating 22 amps max current, hence the 25a/2p breaker on the subpanel but is there any reason the breaker feeding the subpanel has to be an 80a/2p? Can it be a 50a/2p?

Attachments​

  • Protecting the feeder IMG_0010 - EletriciansForums.net
    IMG_0010.jpeg
    514.6 KB · Views: 2
 
This is one for one of our USA members such as @Megawatt

Having two MCB (breakers) in series will not give you good selectivity, i.e. the ability for a downstream fault to be cleared only by the downstream breaker (25A in your case), usually the upstream breaker (here 80A) will also go on a hare fault that reaches the "instant" magnetic trip point of the upstream breaker.

Achieving good selectivity with breakers requires the upstream one to be one of the fancier MCCB that has a short-term delay that gives the downstream one a chance to clear first. That is unusually outside of industrial installations.

If your sub-panel has nothing but the solar panels and some trivial other circuits I can't see what a 50A feed is a problem, but this side of the pone the regulations differ.

Also it is odd not to show the N-E link on the main panel (i.e local earthing/grounding of the supply neutral/cold line).
 
This is a solar tie in generating 22 amps max current, hence the 25a/2p breaker on the subpanel but is there any reason the breaker feeding the subpanel has to be an 80a/2p? Can it be a 50a/2p?

Attachments​

  • Protecting the feeder IMG_0010 - EletriciansForums.net
    IMG_0010.jpeg
    514.6 KB · Views: 2
It all depends on the rating of the panel like 60 amp or 125 amp panels. You can never exceed the rating of the panel so having said that you can use what size breaker you want to as long as the wiring corresponds to the breaker and the loads being used.
 

Reply to Subpanel feeder breaker size? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

This is a solar tie in generating 22 amps max current, hence the 25a/2p breaker on the subpanel but is there any reason the breaker feeding the...
Replies
0
Views
455
I would like to ask advice on a breaker size. Back in 2001 I turned my garage into a woodworking shop with several 240v machines. To power them I...
Replies
2
Views
1K
Hi, So I'm replacing a small old off grid with a new 7.5kw off grid, & being poor seek best value for my mppt, after long searches I find this...
Replies
1
Views
686
I recently had my 50yr old 100A main panel replaced with a 200A Siemens panel (MC2040B1200EFC). It is the incarnation with the 200A main breaker...
Replies
4
Views
2K
Good afternoon - we're considering adding an additional breaker to our "main service panel" which is where the meter is located. That panel has 6...
Replies
1
Views
720

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock