Julie, hope you had a good Christmas.. ive been having more thoughts on my TT earthing arrangement at my pond. The pond supply is protected by a single 30ma RCD back at the solar/battery backed up supply DB in the garage.. which trips at 66.2 ms when rcd test carried out at pond fuse box. This rcd is the only shock protection. Should the rcd fail to trip with fault introduced I'll have circa 7 amps of earth fault current flowing through my earth rod at 36ohms which will not trip the pond supply breaker which is 16amps at the pond end 20amp at the garage supply end. I guess I do have the individual fuses on the pond equipment themselves for example pond uv light which on a 2amp fuse so this would blow within 400ms? How can I make this more robust if needed? Another rcd at the pond end?

I kind of share the same concerns, when an RCD is present as additional protection then I am quite comfortable, but like in this case - the rcd is fault protection (411.4.204/411.5.2 sort of thing) just having this one device just doesn't feel enough.

By the regulations of course it is sufficient, the imbalance would be detected by the RCD, so providing it works all is good.

However, in general for ADS you have the MCB/fuse on the circuit itself, and if that doesn't operate, then the upstream main fuse will eventually operate, this along with the inherent reliably of fuses (and MCBs to an extent), plus the RCD for additional protection gives a really comfortable feeling that a fault will be cleared by at least one of the three things there.

I just don't get that when you have just the one device, especially as RCDs just haven't the same inherent reliably as other devices.

The standard solution is as used for TT installations, you have a higher current 300ms RCD upstream, and a 30mA instantaneous RCD on the circuit itself. In your case as they would be both on the same circuit, they could both be standard 30mA inst RCDs , either, or both could operate and the use of two would just provide redundancy in the event one failed to operate correctly.

But as indicated above it is actually compliant with the one RCD for fault protection
 
I kind of share the same concerns, when an RCD is present as additional protection then I am quite comfortable, but like in this case - the rcd is fault protection (411.4.204/411.5.2 sort of thing) just having this one device just doesn't feel enough.

By the regulations of course it is sufficient, the imbalance would be detected by the RCD, so providing it works all is good.

However, in general for ADS you have the MCB/fuse on the circuit itself, and if that doesn't operate, then the upstream main fuse will eventually operate, this along with the inherent reliably of fuses (and MCBs to an extent), plus the RCD for additional protection gives a really comfortable feeling that a fault will be cleared by at least one of the three things there.

I just don't get that when you have just the one device, especially as RCDs just haven't the same inherent reliably as other devices.

The standard solution is as used for TT installations, you have a higher current 300ms RCD upstream, and a 30mA instantaneous RCD on the circuit itself. In your case as they would be both on the same circuit, they could both be standard 30mA inst RCDs , either, or both could operate and the use of two would just provide redundancy in the event one failed to operate correctly.

But as indicated above it is actually compliant with the one RCD for fault protection
My fuses at the pond are glass quick blow fuses so guess they offer better disconnection times but think I will definitely consider a second 30ma rcd at the pond for redundancy. But for additional protection I think if I do any kind of maintenance in and around the pond I will isolate the whole lot from the garage.
Just so I'm understanding correctly with my TT system at the pond and rcd failure and local mcb and fuses not operating im right in saying the fault current will just continue to flow through the mass of earth to transformer and be unnoticed until shock recieved at the pond equipment?
 
My fuses at the pond are glass quick blow fuses so guess they offer better disconnection times but think I will definitely consider a second 30ma rcd at the pond for redundancy. But for additional protection I think if I do any kind of maintenance in and around the pond I will isolate the whole lot from the garage.
Just so I'm understanding correctly with my TT system at the pond and rcd failure and local mcb and fuses not operating im right in saying the fault current will just continue to flow through the mass of earth to transformer and be unnoticed until shock recieved at the pond equipment?
Yes, if the fault is L to E.
L to N would cause the Ocpd to operate.

You would have a current of around 9 amps with rod and parallel paths connected
 
Last edited:
Yes, if the fault is L to E.
L to N would cause the Ocpd to operate.

You would have a current of around 9 amps with rod and parallel paths connected
Ok so assuming the body resistance of 1000ohms and resistance in parallel with earth rod a dangerous current would flow through the body if class 2 pond equipment it touched during fault!'
 
Ok so assuming the body resistance of 1000ohms and resistance in parallel with earth rod a dangerous current would flow through the body if class 2 pond equipment it touched during fault!'
No, not with class 2 appliances, as they are double insulated.
 
My fuses at the pond are glass quick blow fuses so guess they offer better disconnection times but think I will definitely consider a second 30ma rcd at the pond for redundancy. But for additional protection I think if I do any kind of maintenance in and around the pond I will isolate the whole lot from the garage.
Just so I'm understanding correctly with my TT system at the pond and rcd failure and local mcb and fuses not operating im right in saying the fault current will just continue to flow through the mass of earth to transformer and be unnoticed until shock recieved at the pond equipment?
Why would the RCD fail … yes it can happen but then it may not.
Without it you have no protection on the TT System
 

Reply to Bonding of extraneous conductive frame in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
717
Hi all, just a quick one on an earthing arrangement for a radial circuit on a wooden workshop I have just had installed. I have run a 3 core 2.5mm...
Replies
7
Views
336
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
551
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top