Induced voltage on neutral wire

Discuss Induced voltage on neutral wire in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
Hi everyone,

When checking my consumer unit voltages with the full board off, I stumbled across something head scratching.

Measuring the feed from the DNO, L-N I read 242.3 V. Measuring L-E I measured 242.3 V and N-E I measured a steady 30 mV.

When measuring the live side of the main of the main switch to the dead side of the main switch, I measured 55 V. This as you see in substations is impressed Voltage. At least so I believe.

The head scratching thing I found, is that with each final circuits neutral wire disconnected from the consumer unit (but earth wires connected and live wires connected to the open MCBs (fed from two open RCDs)) I found that each circuits Neutral wire measured 240 V with respect to the DNO Live.

as each of these circuits has appliances in, the only thing I can think of, is that im measuring again an impressed Voltage on the neutral through the cabling and through the appliances, socket ring, light radial etc.

Is this a normal occurance? Anyone come across this before?
 
If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E.
this could give you a true voltage reading as you were getting.
 

Reply to Induced voltage on neutral wire in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock