Hi Guys,
Thanks for all your responses, The only reason i asked about testing at a light switch is to double check and make sure that the maximum Zs i recorded was actually the maximum Zs, seem s a bit stupid on my behalf but im kinda new to testing my work off. I am aware that with the theory and the actual Zs should be at the furthest part of the circuit as this has the highest resistance reading. Just wanted to 100% check and make sure my reading's were correct.

In response to you previous question tony, the tester uses 3 wire only, and it has ''non trip'', when you dis-connect the neutral lead from the tester it says ''lead''. You must be right in saying put neutral + earth leads onto earth terminal and live to live. I'll give it a try....

Thanks Guys