Re: testing for Ze and PFC. Question 1 - Yes you can't get a reading of Ze at the supply. Yes & No is the answer for the Zs of each circuit as the earth in the T+E (if it has earth) may be connected to frame of farm buildings, old lead water pipes etc etc. It could get a earth of sorts that way. Have you tried a plug in tester just to see if it reads an earth?
Question 2 - Turn both isolators off the CUs and measure the PFC.
Question 3 - I would phone electricity board and see if PME is available first. You may be surprised even if the place is in the sticks. Depends how good supply transformer is though. |