View Single Post
Old 17-04-2008   #8 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: testing for Ze and PFC.

Quote:
Originally Posted by Ross Trician View Post
evening chaps,
just to fill you in on a few more bits and to make things a bit clearer.

The incoming supply mis 3 phase which then uses the individual phases to feed various isolators and dis boards etc.

these are somer of the test results I did get.

ring was, L-L, 0.69 ohms. N-N was 0.66 ohms, cpc-cpc was 0.98 ohm.
L-N figure 8 1.34 ohm.
L-E fihure 8 was 1.56 ohm.
R1+R2 was 0.45ohms.
Ring Zs was 3.64ohms

Shakey, you say that the pfc is the right reading but needs to be doubled because it is 3 phase, can you tell me what difference that makes at the C/U as it is only fed with a live and neutral.

also can some of you who are more knowledgeable than me confirm I am interpreting this right,
in GN3 it states the max Zs for a type 1, 16 Amp, bs3871 CB is 3 ohms?
and for 32Amp CB it is 1.5ohms.
therefore the ZS readings I have are too high and presumably due to there being no earthing arangments???

also you say about putting a spike in for the whole system, would this then not make me "responsible" for the whole system?
my thoughts were to simply provide the earthing for the instalation I am working on and if they wish to "put right" the rest of the system then that would be a seperate issue.

I am initially working to the 16th, going on the 17th update course in couple of weeks.
could I put an rcd unit inline after the isolator to cover the whole system rather than changing both boards, advice on you ideas of instalation experience appreciated.

thanks Ross
Ross read reg 130-07-01 in the 16th

aint got in front of me but basically

"no alteration or addtion shall be carried out etc etc...... unless the earthing and bonding arrangements are also adequate"

this is no different to installing a spur in the kitchen, and having to install missing main bonds first......its just the regs

you cant just earth 'your bit', you have to earth at the origin, and yes you then take responsibility for the whole installation, because you have 'altered' the supply earthing arrangements

Imagine (for some reason) you changed a system from TNCS to TNS, then circuits which may have complied with disconnection times before may not now, and because you are the person doing the work, that becomes your responsibility

Putting an RCD covering large parts of the installation wont work either, for the same reasons as you cant do it under the 17th
  Reply With Quote