All sorted now 2 x new isolator's, and was has been installed in our shop so the first thing to trip will be on our premises.
One thing i don't understand though. Is when we overpower the incoming supply (Which i am told is 74kvA (Our 5 beds use 72kvA apparently when all in full use)) it blows the 100A incoming fuses, rather than trip the breakers which are rated at 25A (3 ph). Why is that??