Quote:
Originally Posted by jibspark I should think im gonna sound pretty stupid now but at first glance i would have said 200ms as it should be protected by a 30mA RCD.
Where have i gone wrong? |
not all socket outlets need to be on an RCD
it could be under the supervision/control of a skilled/instructed person, or it could be labelled for one specific item of equipment, in which case no RCD and 0.4 S applies