Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | A forum for electricians in the UK > General Electrical Forum Topics > Commercial and Industrial Electrical
Forgot Password? Join Us!

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
Old 04-05-2008, 07:48 PM   #1 (permalink)
dnsltd
Junior Member
 
Join Date: May 2008
Location: Royal Forest of Dean
Posts: 8
View dnsltd's Photo Album
Default Help needed with 3 phase!

I bought into a sunbed business last year, for my partner and the electrics are a shower of ****e....there isa problem with the ampageanddespite the fact the shop does need a larger supply, we can run approx 80% on what we have....which at the moment is a better option than paying e-on loads of cash to upgrade the supply.
Anyway, the shop below us (where the meter is - which we own) is not ours, and access is a nightmare. Can we request the meter to be relocated FOC into our premises?

Bear with me now, as i am being explained the following via phone....
There is a main isolator from the incoming mains. Then the meter. Then a 2nd isolator, contating three fuses (3 phase obv) all rated @ 30A . This has been bul****ted / bodged to 90A via 3 x 30A fusewires...nice! then off we go into our premises and a 3 phase board.

The 2nd isolator has rotted / burnt away over time (Obv the connections we're rating at less than the fuse wire!) so we now have a phase down. I am planning on replacing the isolator, then installing a 2nd in line in our shop so any future issues can be resolved inhouse. What i need to know asap is what cable will be feeding the burnt isolator if they were 30A fuses (16mm meter tails?)? Why is the board trip's not isolating firstly? I appreciate this is as difficult for you to answer as it is for you to understand!

The shop is 3 hrs from me so it's not a matter of poppingto see for myself!

Any help appreciated!

Craig

dnsltd is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-05-2008, 08:09 PM   #2 (permalink)
rumrunner
Senior Member
 
rumrunner's Avatar
 
Join Date: Dec 2007
Posts: 397
View rumrunner's Photo Album
Default Re: Help needed with 3 phase!

Sounds like you nead to get someone who knows what there doing round there pronto ,
all the best with it
rumrunner is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-05-2008, 08:23 PM   #3 (permalink)
dnsltd
Junior Member
 
Join Date: May 2008
Location: Royal Forest of Dean
Posts: 8
View dnsltd's Photo Album
Default Re: Help needed with 3 phase!

I'd agree, but trouble is bank holiday, and all that! I need to drive up there now and see what's going on and sort it if possible. Unless tehre's any sparks in Mansfield who fancy some work for a fair price!
dnsltd is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-05-2008, 10:28 PM   #4 (permalink)
rumrunner
Senior Member
 
rumrunner's Avatar
 
Join Date: Dec 2007
Posts: 397
View rumrunner's Photo Album
Default Re: Help needed with 3 phase!

Hi ,
I think you first course of action should be to replace the defective fittings first ,even if only as a tempory measure ,then with a sensable load applied at least the place shouldnt burn down!
then you can investigate how to upgrade to accomodate your sumbeds ,also if the public are using the premisis ,i would consider closing untill the remedial work is done at least

im not trying to be negative ,but it does sound like a accident waiting to happen
all the best with it
rumrunner is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-05-2008, 02:56 PM   #5 (permalink)
dnsltd
Junior Member
 
Join Date: May 2008
Location: Royal Forest of Dean
Posts: 8
View dnsltd's Photo Album
Default Re: Help needed with 3 phase!

All sorted now 2 x new isolator's, and was has been installed in our shop so the first thing to trip will be on our premises.
One thing i don't understand though. Is when we overpower the incoming supply (Which i am told is 74kvA (Our 5 beds use 72kvA apparently when all in full use)) it blows the 100A incoming fuses, rather than trip the breakers which are rated at 25A (3 ph). Why is that??

Cheers
dnsltd is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-05-2008, 04:48 PM   #6 (permalink)
rumrunner
Senior Member
 
rumrunner's Avatar
 
Join Date: Dec 2007
Posts: 397
View rumrunner's Photo Album
Default Re: Help needed with 3 phase!

Quote:
Originally Posted by dnsltd View Post
All sorted now 2 x new isolator's, and was has been installed in our shop so the first thing to trip will be on our premises.
One thing i don't understand though. Is when we overpower the incoming supply (Which i am told is 74kvA (Our 5 beds use 72kvA apparently when all in full use)) it blows the 100A incoming fuses, rather than trip the breakers which are rated at 25A (3 ph). Why is that??

Cheers
IT might not be a problem ,now the defective isolators are replaced ,with a phase down and burnt out connections all sort of strange things happen

are the are the sunbeds single phase ,if they are it might be worth asking your sparks to test the power factor ,and dont turn them all on in one go from the main isolator ,the inrush will affect the supply fuses not the 32a ones ,maybee thats what happened

#Glad you took the advise and got it done quick
all the best with it all


Last edited by rumrunner; 05-05-2008 at 05:57 PM.
rumrunner is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Google Search
Google

All times are GMT +1. The time now is 04:18 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Home Loan : Credit Cards : Free mobile phone's stuffs : Credit Cards : Credit Cards UK

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18