Default Tripped Breaker (Saw mill)

Hey,

I'm a student going into electrical in BC, Canada.The mill I'm at has me looking at a problem. The situation is that when a log goes into the canter, and it gets jammed, the breaker trips and the PLC goes too. At the moment I do not have much information on anything else.

I was wondering that since the machine is getting jammed up, it draws more current, which causes the breaker to trip from this increase.

lukas86 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-05-2008   #2 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,048
View Shakey's Photo Album
Default Re: Tripped Breaker (Saw mill)

The breaker trps to stop the motor burning out, it is going straight into an overload situation and the breaker is doing its job
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 16-05-2008   #3 (permalink)
lukas86
Junior Member
 
Join Date: May 2008
Location: BC, Canada
Posts: 11
View lukas86's Photo Album
Default Re: Tripped Breaker (Saw mill)

Thanks,

I was confident that was the case, but wanted to be sure.
lukas86 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 16-05-2008   #4 (permalink)
rumrunner
Respected Member
 
rumrunner's Avatar
 
Join Date: Dec 2007
Posts: 522
View rumrunner's Photo Album
Default Re: Tripped Breaker (Saw mill)

Quote:
Originally Posted by Shakey View Post
The breaker trps to stop the motor burning out, it is going straight into an overload situation and the breaker is doing its job
I agree with shakey ,but i would also check that the motor is drawing the same current on all 3 phases and that the overload is set exact to the current on the data plate, also check for loose connections.
all the best with it

the folowing link may be usefull as well Welcome to www.wiringmanual.com

Last edited by rumrunner; 16-05-2008 at 12:58 AM.
rumrunner is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 20-05-2008   #5 (permalink)
lukas86
Junior Member
 
Join Date: May 2008
Location: BC, Canada
Posts: 11
View lukas86's Photo Album
Default Re: Tripped Breaker (Saw mill)

I was told by my supervisor that all 3 phases are drawing the same current and the overload "should" be set exact to the current.

What I was told happens that when a log gets jammed in the canter, the breaker trips immediately. There is no delay of a few seconds before the breaker trips. I believe the breaker is 2000 Amps, and the current draw from the canter is close to that. To get over this tripped breaker situation, would it be safe to put in a slightly greater breaker size or will this burn out the motors too fast? I do not know the whole situation, but if a breakers job is to stop current flow when there's a problem, I don't want to tell my supervisor that this is the only option to fix this situation. I'm not sure if they can modify the intake to the canter either. I was wondering if anyone had any other ideas or options.
lukas86 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 20-05-2008   #6 (permalink)
wayne
Respected Member
 
wayne's Avatar
 
Join Date: Feb 2008
Posts: 753
View wayne's Photo Album
Default Re: Tripped Breaker (Saw mill)

the overload isnt the problem ,its the size of your logs !
2000 amps thats a big log!
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 20-05-2008   #7 (permalink)
lukas86
Junior Member
 
Join Date: May 2008
Location: BC, Canada
Posts: 11
View lukas86's Photo Album
Default Re: Tripped Breaker (Saw mill)

The logs stay fairly constant size the whole time. This isn't a small saw mill I work at. The canter is fairly large and most of the equipment in this mill runs on breakers that are rated 1600/2000 Amps. There may be one or more pieces of equipment per breaker, but most of the larger pieces (ie. the canter) are on their own breakers.
lukas86 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 19-07-2008   #8 (permalink)
tony.towa
Senior Member
 
tony.towa's Avatar
 
Join Date: Jul 2008
Location: Warwickshire
Posts: 257
View tony.towa's Photo Album
Default Re: Tripped Breaker (Saw mill)

I agree with the previous replies that have been posted. The breaker is doing its job in protecting the cables and motor. If a log jams the motor the increase in current is likely to be that quick that the breaker will trip out without a noticeable delay. If this is becoming a regular occurance check your motor running current under load and compare it with the manufacturers spec. If that is ok it sounds like the logs you are putting through are too big for the equipment. Mind you I do agree 200amps is one hell of a log!!!

tony.towa is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 01:15 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Debt Consolidation : Debt : Cheap Magazines : AdSense Optimization Tutorials : Car Credit

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31