Old 02-06-2008   #1 (permalink)
KNIPEX
Junior Member
 
Join Date: Jun 2008
Posts: 23
View KNIPEX's Photo Album
Default 3 Phase Supply, Need A Seperate Earth

Hi guys im after a bit of help please.

if im running a 4core 25mm armoured to a three phase distboard do i need a seperate earth to go with it or can i use the armourings???

i thought you had to run a seperate earth half the size of the cable so a 16mm earth.

all cable calcs say u need a seperate earth so im confused

is there any regs on this please???

thanks in advance.

no replies


Last edited by KNIPEX; 02-06-2008 at 06:50 PM. Reason: Automerged Doublepost
KNIPEX is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 02-06-2008   #2 (permalink)
Bane
Respected Member
 
Bane's Avatar
 
Join Date: Jan 2008
Posts: 665
View Bane's Photo Album
Default Re: 3 Phase Supply, Need A Seperate Earth

I'd say run a seperate earth.
Bane is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 02-06-2008   #3 (permalink)
wayne
Respected Member
 
wayne's Avatar
 
Join Date: Feb 2008
Posts: 757
View wayne's Photo Album
Default Re: 3 Phase Supply, Need A Seperate Earth

i usually do ,but just done a large job of 10 db,s swa as earth (client spec)so no help here

section543.2 gives "types of protective conductors,have a read ,post your thoughts

Last edited by wayne; 02-06-2008 at 08:51 PM. Reason: Automerged Doublepost
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-06-2008   #4 (permalink)
wayne
Respected Member
 
wayne's Avatar
 
Join Date: Feb 2008
Posts: 757
View wayne's Photo Album
Default Re: 3 Phase Supply, Need A Seperate Earth

further to my last post ,our technical dept just did a calc for me ,turns out it needed an earth cable due to length
i would suggest further you have a look at the whole of chapter 54 if you want to rely on the swa as a cpc
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-06-2008   #5 (permalink)
ian.settle1
Senior Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 294
View ian.settle1's Photo Album
Default Re: 3 Phase Supply, Need A Seperate Earth

Quote:
Originally Posted by wayne View Post
further to my last post ,our technical dept just did a calc for me ,turns out it needed an earth cable due to length
i would suggest further you have a look at the whole of chapter 54 if you want to rely on the swa as a cpc
Wayne do you have a different posting as I can not see any mention of the length of the cable run.
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-06-2008   #6 (permalink)
Bane
Respected Member
 
Bane's Avatar
 
Join Date: Jan 2008
Posts: 665
View Bane's Photo Album
Default Re: 3 Phase Supply, Need A Seperate Earth

Maybe he meant size?

Anyway, fu*k that. I answered a question right!!!
Bane is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-06-2008   #7 (permalink)
wayne
Respected Member
 
wayne's Avatar
 
Join Date: Feb 2008
Posts: 757
View wayne's Photo Album
Default Re: 3 Phase Supply, Need A Seperate Earth

ian ,
this thread doesnt mention cable run ,i was posting about a cable i was sizing up,sorry if i confused you
what the tech dept probably found out was the r1+r2values were too high and the easiest solution was a seperate earth
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-06-2008   #8 (permalink)
Bane
Respected Member
 
Bane's Avatar
 
Join Date: Jan 2008
Posts: 665
View Bane's Photo Album
Default Re: 3 Phase Supply, Need A Seperate Earth

Oh you trickster Wayne
Bane is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-06-2008   #9 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,048
View Shakey's Photo Album
Default Re: 3 Phase Supply, Need A Seperate Earth

I ripped out 4 core 25mm SWA the other week feeding a 3 phase sub board

probably about 60 metres, they were certainly using the armour as the cpc.....

Wayne, so what is the value of R2 for the armour of SWA? (and i'm not being 'funny' that is a genuine question)

I think this would have more to do with the adiabatic fourmula, because R1+R2 would only be relevant if you knew the breeaker (and its corresponding Zs) protecting the SWA

Now, just thinking logically here chaps, if you have TNS at your house, chances are its being feed from SWA, with the armour being used as the earth........
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-06-2008   #10 (permalink)
wayne
Respected Member
 
wayne's Avatar
 
Join Date: Feb 2008
Posts: 757
View wayne's Photo Album
Default Re: 3 Phase Supply, Need A Seperate Earth

both mccb and zs are known
resistance values for swa can be obtained from cable manufacturers

wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 05:45 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: News : Apply for Credit Card : Remortgages : Internet Advertising : Advertising

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32