Default Office consumer units!

Another question.

I've seen this done before but just want to check out your thoughts! I'm wiring a building with three seperate floors for three seperate levels of offices all rented by different companies when finished. There is one control room for the whole building. Bearing in mind this is not a complex job and not on the large scale the Hydro Authority are supplying a three phase feed to the building but each floor will be single phase with its own meter!

As I have been informed that all circuits have to be protected by seperate RCBO's, I'm thinking to give me more room in the consumer unit it would be best just to use a 3 phase MEM board and link the busbars at the incomer!

What do you think?

Cheers
andrew692003 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-02-2010   #2 (permalink)
baldsparkies
Senior Member
 

Join Date: Mar 2009
Posts: 335
Thanks: 8
Thanked 54 Times in 52 Posts
Default Re: Office consumer units!

Why not go for single phase boards on each floor, also how about 17th edition dual rcd boards instead of rcbo's its much cheaper. Or as a compromise you could go for high integrity boards and offer rcbo's to any dedicated circuits as required.
baldsparkies is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-02-2010   #3 (permalink)
bugsy
Respected Member
 

Join Date: Jan 2010
Location: Hertfordshire
Posts: 758
Thanks: 6
Thanked 113 Times in 104 Posts
Default Re: Office consumer units!

Small panel board at the incommer feeding C.U. on each floor spn over the three phases
bugsy is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-02-2010   #4 (permalink)
andrew692003
Member
 

Join Date: Jul 2009
Location: Highlands
Posts: 45
Thanks: 0
Thanked 5 Times in 5 Posts
Default Re: Office consumer units!

Don't want to use single phase boards as they are to small I probably have about 15 circuits to each floor, not seen the dual RCD's so I'll check that out today. I'm still thinking just use an MEM board as I'll be using probably at least 100x100 metal trunking and I think it would make the job a lot neater also money seems to be no object on this project.

Thanks for the replies tho lads, much appreciated.

Cheers
andrew692003 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-02-2010   #5 (permalink)
sparks1234
Respected Member
 

Join Date: Mar 2009
Posts: 846
Thanks: 0
Thanked 75 Times in 71 Posts
Default Re: Office consumer units!

You dont necessarily need to use RCd protection, depends on the use of the building and who is in it, beware of useing RCD on IT equipment etc etc
sparks1234 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-02-2010   #6 (permalink)
bugsy
Respected Member
 

Join Date: Jan 2010
Location: Hertfordshire
Posts: 758
Thanks: 6
Thanked 113 Times in 104 Posts
Default Re: Office consumer units!

Small mccb panel board , swa to C.U.s you can get sracking kits up to 24 ways
bugsy is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-02-2010   #7 (permalink)
gizmo
Junior Member
 

Join Date: Jan 2009
Posts: 16
Thanks: 5
Thanked 1 Time in 1 Post
Default Re: Office consumer units!

Am i right in thinking that you want to use one three phase board for all three floors ? One simple little problem with that, METERING ! I'd go for single phase supply to each floor. Meters in the control room, and dist boards on each floor
gizmo is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-02-2010   #8 (permalink)
bugsy
Respected Member
 

Join Date: Jan 2010
Location: Hertfordshire
Posts: 758
Thanks: 6
Thanked 113 Times in 104 Posts
Default Re: Office consumer units!

Firstly where is the meter at present
Secondly when each floor is sub let will the landlord be charging for useage
If the sublet floors are going to be metered by the supply authority the contact network engineering who will advise you install a ryefield board they will then ask you to cable to each floor (swa) and install 300mm of 150mm trunking they will then install their meters

If the landords paying the supply authority and charing on any of the foregoing can be considered
bugsy is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 4 Weeks Ago   #9 (permalink)
adamh
Senior Member
 

Join Date: Dec 2007
Location: stockport
Posts: 145
Thanks: 0
Thanked 5 Times in 5 Posts
Default Re: Office consumer units!

the guy wants to use a 3 phase board for each floor but link the switch out so l1l2l3 are all fed from the single incomer, nothing wrong with that but you can buy a switch that will fit with this done internally.
adamh is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 4 Weeks Ago   #10 (permalink)
bugsy
Respected Member
 

Join Date: Jan 2010
Location: Hertfordshire
Posts: 758
Thanks: 6
Thanked 113 Times in 104 Posts
Default Re: Office consumer units!

right 3 way tpn mccb panel board 3 x 63a mccb+25mm swa (check with calcs)_4 way (or 6/8/) tpn db via check meter
bugsy is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply
  

Bookmarks



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Domestic Consumer Units in flats with 2 electrical feeds GreenElec Electrical Forum | General Electrical Forum 6 22-08-2009 10:00 PM
Consumer Units in Cupboards chloebear Electrical Forum | General Electrical Forum 4 13-03-2009 08:57 AM
Positioning of new consumer units. JulesHurley Electrical Wiring, Theories and Electrical Regulations 31 21-01-2009 07:46 PM
cheap consumer units diditrain Electrical Forum | General Electrical Forum 8 19-08-2008 05:54 AM
2 x consumer units bozo555 Electrical Forum | General Electrical Forum 3 23-07-2008 09:29 AM



Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Plastering Forum | Flooring Forum | Plumbing Forum |
(c) 2008 Electricians Forum | Electrical Forum | Electrical Advice | Electricians Jobs | A forum for electricians in the UK