Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Commercial and Industrial Electrical
Forgot Password? Join Us!

Commercial and Industrial Electrical Discussions on Three Phase, Motors, Trunking, electronics and other industrial electrics

Reply
 
LinkBack Thread Tools Display Modes
Old 26-06-2008   #1 (permalink)
THE DUKE
Junior Member
 
Join Date: Jun 2008
Posts: 1
View THE DUKE's Photo Album
Default Star Delta Motor Cable Size

Can anybody advice on cable size for 250Kw star delta motor, star delta starter supplied with 240mm 4 core SWA protected by 500a fuses. Would like to keep cables at 240mm but terminal box looks a bit small for 2 x 240mm SWA cables motor is rated at 400v 430Amp

Regard

ps this is my first time on forum like what I see so far

THE DUKE is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-06-2008   #2 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,048
View Shakey's Photo Album
Default Re: Star Delta Motor Cable Size

i am figuring on VERY rough calcs at about 360A per phase , which would make (again -off the top of my head calcs) cable size around 100mm

240mm looks like someone has been VERY generous

have you done any calcs for this?
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 27-06-2008   #3 (permalink)
wattsup
Senior Member
 
Join Date: Jun 2008
Posts: 153
View wattsup's Photo Album
Default Re: Star Delta Motor Cable Size

mm, you need a splitter box beneath the incomer

no such thing as 100mm, its 240mm or maybe 95mm, or perhaps 175mm?

give me the motor output in hp , the running current and start details, i will give you cable size and protection fuses

Last edited by wattsup; 27-06-2008 at 01:55 AM. Reason: Automerged Doublepost
wattsup is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 27-06-2008   #4 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 244
View Spudmiester's Photo Album
Default Re: Star Delta Motor Cable Size

Again with VERY rough calcs and no information on de-rating factors I recon on 120mm 3core x2 and separate earth to give you more room in terminal box.
Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 30-06-2008   #5 (permalink)
benji
Junior Member
 
Join Date: Jun 2008
Posts: 29
View benji's Photo Album
Default Re: Star Delta Motor Cable Size

250kw star delta why not ditch the starter and get a soft start unit you'll save money in the long term
yours benji
benji is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-07-2008   #6 (permalink)
daisy
Junior Member
 
Join Date: Mar 2008
Posts: 12
View daisy's Photo Album
Default Re: Star Delta Motor Cable Size

I like benji,s idea. Anyway a common way of calculating the cable size is to realize the current in the cables between starter and motor when running is 0.58 times the supply current. But dont forget , as someone as already said the correction factors. If you are installing in conduit you already have one factor ,grouping. The six cables are loaded so in affect you have two curcuits. Best of luck.
Daisy
By the way did i say that is some motor?

daisy is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 05:34 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Cheap Car Insurance : Personal Loans : Problem Mortgage : Internet Advertising : Free Credit Report

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32