    Default never done one before

    i normally just do domestic stuff but my mate asked me to stick a cable and plug on a three phase motor in his factory but i havent done anything with motors since college and even then i didnt pay a great deal of attention, but i thought id have a crack anyway
    its a 2.5 kw motor,
    what sort of cable should i use and do i connect in star or delta and will type c 16a mcbs be enough

  2. #2
    Electricians Arms Member Amp David's Avatar
    Join Date
    Oct 2009
    Location
    Glossop
    Posts
    641
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: never done one before

    I worked it out as 5.33 amps, without any consideration for power factor.

  3. #3
    Electricians Arms Member DurhamSparky's Avatar
    Join Date
    Jan 2010
    Location
    Durham
    Posts
    1,444
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: never done one before

    use 5 core flex cable!! yeah 16a will suffice!

    not sure about the correct terminations inside the motor normally its just L1 L2 L3....! i used to just follow the test leads on a phase meter!!! quite funny when it goes wrong direction!!


    simples!!
    Last edited by DurhamSparky; 10-03-2010 at 05:10 PM.

  4. #4
    Member opm electrical's Avatar
    Join Date
    Aug 2009
    Location
    yarm
    Posts
    96
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: never done one before

    so a length of 2.5, 5 core flex should cover it then.

    will there be a separate terminal for the neutral
    Last edited by opm electrical; 10-03-2010 at 05:22 PM. Reason: Automerged Doublepost

  5. #5
    Electricians Arms Member DurhamSparky's Avatar
    Join Date
    Jan 2010
    Location
    Durham
    Posts
    1,444
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: never done one before

    yes there should be!!

    mind you all my 3 phase experience was on royal navy vessels were both earth and neutral were non existant!!

    seriously!!

  6. #6
    Respected Member bugsy's Avatar
    Join Date
    Jan 2010
    Location
    Hertfordshire
    Posts
    1,201
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: never done one before

    Before you rush out and buy the cable and plug you should determine the requirements, is it three phase or three phase and n also what socket are you going to plug into.
    Terminations will be marked L1.L2.L3 , N if it requires N and Earth

  7. #7
    Electricians Arms Member gaffer's Avatar
    Join Date
    Apr 2009
    Location
    offshore/Channel Islands
    Posts
    357
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: never done one before

    Use some SY bit more robust IMHO.
    Last edited by gaffer; 10-03-2010 at 05:56 PM. Reason: Automerged Doublepost

  8. #8
    Electricians Arms Member benji's Avatar
    Join Date
    Jun 2008
    Posts
    215
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: never done one before

    neutral ? what neutral

    yours benji

  9. #9
    Electricians Arms Member Hawk81's Avatar
    Join Date
    Feb 2010
    Location
    Northern Ireland
    Posts
    373
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: never done one before

    4 core cable needed not 5. No neutral at a 3 phase motor. Wire it in star. On that size of motor it would only be wired in delta if it has a variable speed drive was use to run this motor. I would use a 4 core sy and make sure to earth the steel braid at 1 end at least. A 10amp tripple pole mcb will do this well. If the motor goes the wrong direction just swap 2 of the phases around.

    Quote Originally Posted by bugsy View Post
    Before you rush out and buy the cable and plug you should determine the requirements, is it three phase or three phase and n also what socket are you going to plug into.
    Terminations will be marked L1.L2.L3 , N if it requires N and Earth
    Most motors do not come marked L1 L2 L3. They come marked U1 U2 U3. and on the other side V1 V2 V3. Only ever seen a single phase motor that required a neutral.
    Last edited by Hawk81; 10-03-2010 at 07:52 PM. Reason: Automerged Doublepost

  10. #10
    Moderator Notsosmart's Avatar
    Join Date
    Mar 2009
    Location
    Bedfordshire
    Posts
    934
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: never done one before

    Quote Originally Posted by bugsy View Post
    Before you rush out and buy the cable and plug you should determine the requirements, is it three phase or three phase and n also what socket are you going to plug into.
    Terminations will be marked L1.L2.L3 , N if it requires N and Earth

    You hould be very careful in answering questions posed on this forum, if you do not know the correct response 100% then I believe you should not be replying.

    Quote Originally Posted by Hawk81 View Post
    4 core cable needed not 5. No neutral at a 3 phase motor. Wire it in star. On that size of motor it would only be wired in delta if it has a variable speed drive was use to run this motor. I would use a 4 core sy and make sure to earth the steel braid at 1 end at least. A 10amp tripple pole mcb will do this well. If the motor goes the wrong direction just swap 2 of the phases around.

    Most motors do not come marked L1 L2 L3. They come marked U1 U2 U3. and on the other side V1 V2 V3. Only ever seen a single phase motor that required a neutral.
    Agree completely Hawk.
    Rules are for the obedience of fools and the guidance of wise men.
    Douglas Bader
    (He did loose his legs though!)

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24