Default new shop in leeds

hi everyone, just been too look at a nice job in leeds which should give me plenty of work
shop is approx 15m x 35m ish with a mezanine floor at one end.

couple of questions as ive done a bit bit not that much comemrcial stuff.

1. there are going to be a max of 12 refrigerators, do i split this into 3 or 4 circuits or....?

2. 4 air conditioners, thinking of suppliying these seperately
3. small cafe area to the back of the shop, with 3 phase cooker. and a seperate socket circuit just for this area, aswell as its own lighting circuit.
4. thinkin of keeping mezanine sockets and lighting on there own circuits.
5. office with computer on its own socket circuit.
6. tills on there own circuit

that ll do for now, guess you get the idea'ish! dont know what lighting but theres gonna be a lot of it, so im allowing 6 circuits for this. as well as e/lighting circuit.
thinking of using a 36way 3 phase board and after counting circuits so far (not all mentioned here) ive got 29 ways so...

also, down the sides of the shop is wooden display units incorporating the refrigerators etc going all the way down to the bottom. fridges gonna plug in above these units and be out of sight via a pelmet. im thinking of running 2x4" trays down either side of the shop just obove these units and was wondering what the best way of terminating into socket outlets would be? dont wanna run swa everywhere as its all out of sight and in no danger so wanna use standard pvc, (peel off the tray into metal clad sockets/via grommets or...)

also the lighting is gonna run on these trays as well then peel off upwards into conduit going up the wall and across to relevant "clix" outlets for the lighting, again wanna do this in pvc.

your comments suggestions are greatly appreciated

rich

sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #2 (permalink)
ian.settle1
Respected Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 573
View ian.settle1's Photo Album
Default Re: new shop in leeds

What type of shop is it?
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #3 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 624
View sparkyork's Photo Album
Default Re: new shop in leeds

its sort of like a health food shop with yoga rooms and stuff, food stuff downstairs.
sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #4 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: new shop in leeds

cant immediately fault any of the above although im sure someone can give you further advice ,looks like your'e going to be busy
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #5 (permalink)
tony.towa
Respected Member
 
tony.towa's Avatar
 
Join Date: Jul 2008
Location: Warwickshire
Posts: 539
View tony.towa's Photo Album
Default Re: new shop in leeds

Not trying to teach granny to suck eggs but check on the 'fridges' going down the wall. Some suppliers are now providing units with air con like external units needing an external isolator and they specify the internal connection must be via a BS4343 SP&N interlocked socket.
tony.towa is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #6 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 624
View sparkyork's Photo Album
Default Re: new shop in leeds

yeah looks like im gonna busy for a while!! ill get some pics up of it at the minute, just one big empty concrete box!

good point that tony, ive spoke to customer tonight and ive already asked for the rating of the fridges, so when he gets back to me i can confirm what you mentioned. again it kinda begs the question..if ive got a tray running horizontally down the wall is it gonna be ok running it all in standard T &E and possibly terminating these cables into an isolator then onto bs4343 socket? to be fair im more used to terminating swa into these accesories, but cant see the point in using this when its all out of harms way etc

rich
sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #7 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Re: new shop in leeds

Quote:
Originally Posted by tony.towa View Post
Not trying to teach granny to suck eggs but check on the 'fridges' going down the wall. Some suppliers are now providing units with air con like external units needing an external isolator and they specify the internal connection must be via a BS4343 SP&N interlocked socket.

Tony is correct was going to say the same ! Also the air cons I have done have been three phase and I have just used an Isolator.
Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #8 (permalink)
lee mcgregor
Junior Member
 
lee mcgregor's Avatar
 
Join Date: Apr 2008
Posts: 19
View lee mcgregor's Photo Album
Default Re: new shop in leeds

hi rich, i currently do quite alot of scotmid shops over scotland ie little "coop shops " with the same ideas we have a seperate board for refridgerators as normally they have this board next to refridgerator control panels and also take up quite alot of room and good i suppose to keep lighting and power in one board also being sub mains seperate earths run to each board , also we put small 10 way board into office with computers i suppose to stop people turning off by mistake,also tills we run 4mm radial clean supplies coming down to tills in chrome poles if coming over ceilings along with a ring main if other sockets are require over others tills for cleaners or any other day to day use, lights: a key switch at front door or however they get in, lighting up a passage to bank of switches for shop or switch with contactors ,refridgerators same idea as above each unit but hidden under pelmets and using either 16a 240 3 pin sockets or 32a 415 5pin sockets depends on size of them i suppose we feed these seperate in swa's all going back to boards on tray, Air cons spurs we put a couple of rings for them . theyve started getting us to extract from above where the bake the bread out onto shop floor as they think customers smelling this helps sell bread etc haha.. lighting through shop we normally use 150w hqi fittings metal halides" jcc made " straight down on shop floors and up aisles and tilting on permiter onto fridges . hope this has helped mate in any way .. heres a pictures of kinda the same fittings (HQI-TS DL150 Downlight) or (HQI-TS DL70 Downlight) 70 w version also used these but would recommend the 150w

aaareebaaaa

Last edited by lee mcgregor; 23-07-2008 at 09:16 PM.
lee mcgregor is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #9 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 624
View sparkyork's Photo Album
Default Re: new shop in leeds

cheers lee really appreciate the input, gonna be speaking to customer 2moro now as its a bit late now. will find out whats going on with the fridges and air con setup, have to agree jcc do some pretty nice fittings as well, infact the customer was in manchester when i last spoke to him seeing about getting the manufacturer to come up with a lighting plan (i was never any good at all the formulae attached to working out height of fittings appossed to lumenicity and all that! lol)

is there anything wrong with using t & e for the supplies for stuff? what conditions generally have to be in place that recommend the use of armoureds? ps dont know if i mentioned but theres gonna be about 12 fridges

cheers everyone

rich
sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 23-07-2008   #10 (permalink)
lee mcgregor
Junior Member
 
lee mcgregor's Avatar
 
Join Date: Apr 2008
Posts: 19
View lee mcgregor's Photo Album
Default Re: new shop in leeds

if single phase and out of reach for joe public no dont see why not but if three phase then swa. we also had to wire all t+e in low smoke cable the white ****e thats impossible to strip haha might want to find out as for all shops and council stuff thats what they ask for .


aaareebaaaa

Last edited by lee mcgregor; 23-07-2008 at 09:32 PM.
lee mcgregor is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
electricians mate wanting work in leeds area nelly9908 Electricians Unite - Jobs In Your Area 1 2 Weeks Ago 05:02 PM
Shop refurb into a sunbed shop. mercanlandy Wiring, Theories and the Regulations 3 04-10-2008 08:23 PM

Google Search
Google

All times are GMT +1. The time now is 04:45 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38