Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Commercial and Industrial Electrical
Forgot Password? Join Us!

Commercial and Industrial Electrical Discussions on Three Phase, Motors, Trunking, electronics and other industrial electrics

Reply
 
LinkBack Thread Tools Display Modes
Old 10-01-2008   #1 (permalink)
Torris
Junior Member
 
Join Date: Jan 2008
Posts: 4
View Torris's Photo Album
Default Crabtree RCCB's

Hi
This is my first time on a forum and this is my problem.

I carried out some testing on a domestic premises, the consumer unit main switch is a Crabtree RCCB 2 pole rated at 80A with 100mA trip.
I carried out an RCD test at a random socket with my tester set to 100mA and tested on both cycles on 1/2I with no trip 1I with no trip and 5I with a trip at 6.3ms strangely it is the first time i have worked on a RCCB. My first instinct is to condem the RCCB, but as Im not 100% sure could anyone give there opinion, Am I missing something?

Thanks in advance

Torris

Torris is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-01-2008   #2 (permalink)
TonyM58
Guest
 
Posts: n/a
View TonyM58's Photo Album
Default Re: Crabtree RCCB's

Another forum, i saw a similar problem. When the guy plugged a class II radio into the circuit and retested at a different socket the RCD tests were ok! (dont know if was crabtree)

Is your tests the same at each socket, and what results do you get if you go directly to the output of the RCCB?

Oh, and the other thing, i believe i am right in saying the x5 IdeltaN test is ONLY applicable at 30mA or less, so you should not be testing a 100mA on x5 anyway!
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-01-2008   #3 (permalink)
EasyFox
Respected Member
 
Join Date: Sep 2007
Posts: 443
View EasyFox's Photo Album
Default Re: Crabtree RCCB's

Firstly no 5x test on 100mA (the fluke wont even let you do the test)

Secondly a 100mA rccb/rcd shouldnt be used to reduce the risk of electric shock (412-06-02) as it doesnt offer protection against direct contact unlike a 30mA would so shouldnt be used for socket circuits.

100mA & higher are normally used for protection against fire in the event of earth leakage, or used on TT systems as main switch (if rcbo's are used on individual circuits) or the 100mA S type time delay are used on split load boards.

So in answer to your question I'd check you are testing at correct range (S type or not) then do as Tont58 said test the rccb in isolation from all circuits, if it fails again swap it out.

Last edited by EasyFox; 10-01-2008 at 10:49 PM. Reason: left "socket circuits" out of post
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 20-01-2008   #4 (permalink)
Riggs
Junior Member
 
Join Date: Jan 2008
Location: Plymouth
Posts: 2
View Riggs's Photo Album
Default Re: Crabtree RCCB's

Be careful on the split load crabtree boards as usually the 100ma RCD is a timed delay type as EasyFox stated. A normal RCD tester will not let you carry out the tests. You will require a time delay tester for the RCD tripping times.
Riggs is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-01-2008   #5 (permalink)
Minky
Junior Member
 
Join Date: Dec 2007
Posts: 19
View Minky's Photo Album
Default Re: Crabtree RCCB's

RE:-Crabtree RCCB's,i came across a 80A/30mA RCD yesterday and found it failed the 30mA test at 1x and 5x,the device would not function when the test button was pressed,but after resetting it,it would let current flow.The type was a StarBreaker,and was part of a split-load kit.Have to swap the RCD,and would certainly not recommend this type of board.
Minky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 27-01-2008   #6 (permalink)
ian.settle1
Respected Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 573
View ian.settle1's Photo Album
Default Re: Crabtree RCCB's

Quote:
Originally Posted by TonyM58 View Post
Another forum, i saw a similar problem. When the guy plugged a class II radio into the circuit and retested at a different socket the RCD tests were ok! (dont know if was crabtree)

Is your tests the same at each socket, and what results do you get if you go directly to the output of the RCCB?

Oh, and the other thing, i believe i am right in saying the x5 IdeltaN test is ONLY applicable at 30mA or less, so you should not be testing a 100mA on x5 anyway!
Tony

You are correct you only do the X5 test on RCD/RCBO's up to and including 30mA when used for supplementry protection (Reg 412-06-02)

ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
MK or crabtree? kakusei General Electrical Discussion 10 05-09-2008 10:09 AM
Crabtree & 17th EasyFox Electrical Tools and Products 1 08-02-2008 01:03 PM
Problem with crabtree starbreaker RCCB? bleward General Electrical Discussion 2 14-09-2007 11:56 PM

Google Search
Google

All times are GMT +1. The time now is 05:48 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38