Old 27-01-2008   #1 (permalink)
snatch
Junior Member
 
Join Date: Jan 2008
Posts: 3
View snatch's Photo Album
Default lighting

recently upgraded the workshop lighting. 3 banks of lights. each bank being supplied by a different phase. used a three gang switch to operate with all three phases. a question has been raised if this is against regs having all three phases in one light switch. i can understand the reasoning but is it against regs?

snatch is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-01-2008   #2 (permalink)
TonyM58
Guest
 
Posts: n/a
View TonyM58's Photo Album
Default Re: lighting

Dont see that its AGAINST the regs, although there should be a warning notice on the switces with 'Danger - 400Volts present' or similar, the same as you would with sockets on different phases
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-01-2008   #3 (permalink)
snatch
Junior Member
 
Join Date: Jan 2008
Posts: 3
View snatch's Photo Album
Default Re: lighting

thank you for your reply. i have put a notice up saying 400v on switch. i too can not see anything against regs. nice to get one over on people who slag you off but never seem to do.

only just joined this forum and can already see its a good a tool.

thanks once again.
snatch is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-01-2008   #4 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 588
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Re: lighting

yeah, hope you use it alot, join in with the fun. any questions ask................tony lol

Me, Sheffield Lad, looking for new employer, 1 years experience + 17th + 16th + EAL dis + 2377 please PM / email me if interested....

If You Build It, They Will Come!!!!!
LukeScotty is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 30-01-2008   #5 (permalink)
rumrunner
Respected Member
 
rumrunner's Avatar
 
Join Date: Dec 2007
Posts: 485
View rumrunner's Photo Album
Default Re: lighting

Hi snatch,
im not saying theres anything wrong with what you have done ,but in years to come if the label falls off or a inexperianced electrician happens to mess with it ,it could be hazardous i suppose
I think i wold be inclined to play safe and use a contactor to switch the lights.
all the best
rumrunner
rumrunner is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 30-01-2008   #6 (permalink)
ian.settle1
Senior Member
 
ian.settle1's Avatar
 
Join Date: Jan 2008
Location: Wirral
Posts: 275
View ian.settle1's Photo Album
Default Re: lighting

Quote:
Originally Posted by rumrunner View Post
Hi snatch,
im not saying theres anything wrong with what you have done ,but in years to come if the label falls off or a inexperianced electrician happens to mess with it ,it could be hazardous i suppose
I think i wold be inclined to play safe and use a contactor to switch the lights.
all the best
rumrunner
Rumrunner

Labels have been stuck on switches like this for many years gone by and will be done for many years to come.

One problem using a contactor is supply to contactor coil fails and hey presto no lights at all, the way stated one phase goes down at least two rows of light still lit.
ian.settle1 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-02-2008   #7 (permalink)
rumrunner
Respected Member
 
rumrunner's Avatar
 
Join Date: Dec 2007
Posts: 485
View rumrunner's Photo Album
Default Re: lighting

hi ian,
im not saying theres anything wrong with what you have done ,and i presume you have a nice clean dry workshop ,in some places ,like say a foundry ,farm and damp dirty places,labels are not much good for long,and why would a coil burn out ,your much more likley to burn a switch out ,especially with an heavy inductive load such as flouresent lighting,use 3 contactors if you want to ensure some lights will stay on if theres a fault,you can even fit a time clock easy then ,just in case you forget to turn them off ,do your bit for the planet and all that
rumrunner
rumrunner is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 18-04-2008   #8 (permalink)
Malcg
Junior Member
 
Join Date: Apr 2008
Posts: 19
View Malcg's Photo Album
Default Re: lighting

Hi

You have 400v across terminals in the multi-switch at several points in very close proximity and inductive loads.

I am pretty sure your switch accessory will NOT be rated for 400v so your in breach of Section 5, BS 7671 by inappropriate selection.

Why not have three single switches with one phase each?
Malcg is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 19-04-2008   #9 (permalink)
Darius-parky
Member
 
Join Date: Mar 2008
Location: Plymouth, Devon
Posts: 77
View Darius-parky's Photo Album
Default Re: lighting

I am sure engraving "Danger 400v" on a switch will only cost few £s. Doing a safe and professional job like that will convince the client to accept the costs.
Darius-parky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 19-04-2008   #10 (permalink)
wayne
Respected Member
 
wayne's Avatar
 
Join Date: Feb 2008
Posts: 731
View wayne's Photo Album
Default Re: lighting

part of ongoing mantainance is replacing labels ,anally retentive i know!!!!!

wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 05:28 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Starting Over : Problem Mortgage : Loans : Debt Consolidation : Credit Counseling

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29