Discuss Motor Keeps going after it's turned off. at Electricians Forums; Newman 3 phase induction motor (Bradbury liftmaster MK1) on a four post ramp - . When the ramp is raised it sometimes keeps going - bloke says he can't switch ...
  1. #1
    Member
    Join Date
    Jul 2009
    Posts
    19
    Thanks
    16
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Motor Keeps going after it's turned off.

    Newman 3 phase induction motor (Bradbury liftmaster MK1) on a four post ramp - . When the ramp is raised it sometimes keeps going - bloke says he can't switch it off by regular switch - has to do it at the main isolator. I haven't been there yet, any ideas?

  2. #2
    Band Member
    johnboy6083's Avatar
    Join Date
    May 2010
    Location
    South east
    Posts
    3,031
    Thanks
    420
    Thanked 525 Times
    in 428 Posts
    Tagged
    0 Thread(s)

    Default Re: Motor Keeps going after it's turned off.

    Contactor sticking?
    malcolmsanford likes this.
    By the time youve gained enough experience to satisfy the old boys, your too old and knackered to use it!

  3. The Following User Says Thank You to johnboy6083 For This Useful Post:

    eddybs23 (25-09-2011)

  4. #3
    Electricians Arms Member
    malcolmsanford's Avatar
    Join Date
    Jul 2010
    Location
    Kent working back out there yet again
    Posts
    7,331
    Thanks
    792
    Thanked 1,674 Times
    in 1,400 Posts
    Tagged
    0 Thread(s)

    Default Re: Motor Keeps going after it's turned off.

    Poor connection on the contactor which is making it stick might have to change the contactor or strip it down and clean the points of contact with some fine emery paper if it's the old open type.

    Check to see if the push button is ok, should be have a contact coil on it, but could still give you problems.

  5. The Following User Says Thank You to malcolmsanford For This Useful Post:

    eddybs23 (25-09-2011)

  6. #4
    Band Member
    johnboy6083's Avatar
    Join Date
    May 2010
    Location
    South east
    Posts
    3,031
    Thanks
    420
    Thanked 525 Times
    in 428 Posts
    Tagged
    0 Thread(s)

    Default Re: Motor Keeps going after it's turned off.

    Also could be the raise button sticking? Maybe the contol box needs the buttons and the contacts behind them cleaning and re-assembling
    By the time youve gained enough experience to satisfy the old boys, your too old and knackered to use it!

  7. #5
    Member
    Join Date
    Aug 2010
    Posts
    14,035
    Thanks
    696
    Thanked 1,480 Times
    in 1,164 Posts
    Tagged
    0 Thread(s)

    Default Re: Motor Keeps going after it's turned off.

    If it was a sticking raise PB then the raise would cut back in when power was restored.
    Does it have a stop PB? Most don’t, you normally have to keep your finger on the PB as a safety precaution.
    Will have to think about this one.

  8. The Following User Says Thank You to Guest5000 For This Useful Post:

    eddybs23 (25-09-2011)

  9. #6
    Member
    Join Date
    Jun 2011
    Location
    Swansea/Aberdeen
    Posts
    467
    Thanks
    11
    Thanked 53 Times
    in 49 Posts
    Tagged
    0 Thread(s)

    Default Re: Motor Keeps going after it's turned off.

    It looks to me as though the action of turning the isolator off is dropping out the raise contactor,so I'd guess it's a control issue (which I think we've worked out already!!!).
    How does the lift work?motor up and down or does the motor power a hydraulic lift then it just releases the pressure to lower it?

    My one was electric power,hold the button in then release wherever up and down.

    A lot of them are very crude,literally the push button has a plastic stalk on the back that pushes the contactor in physically to operate it,usually interlocked then to prevent arcing if up and down are operated simultaneously. I'd go for jonboy's idea of a good physical clean up first,something sticking etc.

  10. The Following User Says Thank You to vaughant For This Useful Post:

    eddybs23 (25-09-2011)

  11. #7
    Electricians Arms Member

    Join Date
    Jan 2011
    Location
    China (Zhuhai)
    Posts
    16,179
    Thanks
    56
    Thanked 1,534 Times
    in 1,354 Posts
    Tagged
    0 Thread(s)

    Default Re: Motor Keeps going after it's turned off.

    Quote Originally Posted by malcolmsanford View Post
    Poor connection on the contactor which is making it stick might have to change the contactor or strip it down and clean the points of contact with some fine emery paper if it's the old open type.

    Check to see if the push button is ok, should be have a contact coil on it, but could still give you problems.
    Far better to clean contacts with ''Glass Sticks'' (glass-fibre strands held tightly together by glued fibre tape, or in a purpose made height adjustable pen type construction) The finish is as good as a new contact surface. I haven't used fine emery paper for maybe 25 years now... You can purchase from any good electronic stores, or where i get mine from, RS.

    Yes the fault could well be in the push-button, the contacts within the push-button unit could be stuck/wedged in the contact position while the spring release is still sending the button back to it's normal position, making it seem like it's working normally.
    SW1970 likes this.

  12. The Following 2 Users Say Thank You to Engineer54 For This Useful Post:

    eddybs23 (25-09-2011), JD6400 (25-09-2011)

  13. #8
    Member
    Join Date
    Jul 2009
    Posts
    19
    Thanks
    16
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: Motor Keeps going after it's turned off.

    Thanks all - as stated - contactor sticking - lift installed 1964 and some very crude switching via pulleys and springs etc. all surrounded by hydraulic fluid and, filth!

  14. #9
    Member
    Join Date
    Aug 2010
    Posts
    14,035
    Thanks
    696
    Thanked 1,480 Times
    in 1,164 Posts
    Tagged
    0 Thread(s)

    Default Re: Motor Keeps going after it's turned off.

    Quote Originally Posted by eddybs23 View Post
    all surrounded by hydraulic fluid and, filth!
    Always a good combination.

    Well done and thanks for getting back to us.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Domestic EICR turned into a nightmare
    By kingeri in forum Electrical Forum: General Electrical Forum
    Replies: 17
    Last Post: 17-02-2013, 08:29 PM
  2. Rcd tripping when lights turned off
    By sidekick in forum Electrical Forum: General Electrical Forum
    Replies: 15
    Last Post: 21-11-2012, 02:47 PM
  3. I turned a job down - have I done the right thing?
    By RoyWorcester in forum Electrical Forum: General Electrical Forum
    Replies: 14
    Last Post: 24-07-2011, 07:13 PM
  4. lights dim when turned off
    By ngoodson1969 in forum Electrical Forum: General Electrical Forum
    Replies: 17
    Last Post: 13-03-2010, 05:58 PM

Visitors found this page by searching for:

bradbury mk1 liftmaster

bradbury ramp oil

bradbury liftmaster mk1 operation

bradbury liftmaster mk1 ramp

bradbury liftmaster mk1 hardwired

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.