    Hi all

    I hope you can help.

    In short:

    I think I am being spun a line from my supplier.

    I am contracting the installation of a 1.2MVA generator (outside the building), and my supplier is claiming new regulations stipulate a busbar must be used instead of the normal cabling to run to the building. Of course it's more expensive, bigger trench etc etc

    It's a complicated relationship, and therefore difficult to get other suppliers involved.

    The questions I have are:

    Are there new regulations that stipulate a busbar must be used irrespective of generator output?

    Assuming there are no reg changes

    What is the maximum distance you can run cables before you need to use a busbar.
    Is there a benefit to using a busbar over cable?

    Thanks in advance.
    Last edited by mikeruss; 19-05-2009 at 10:50 AM.

  2. #2
    Electricians Arms Member benji's Avatar
    Join Date
    Jun 2008
    Posts
    215
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Busbar - 1.2MVA generator install

    anymore info.ie.what would the length of the run be,what is the gen.feeding,what switchgear are you using and where is the switchgear
    yours benji

  3. #3
    Electricians Arms Member stretchyboy's Avatar
    Join Date
    Apr 2009
    Posts
    152
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Busbar - 1.2MVA generator install

    ditto benji, we need more info to see what the choices are.

    Are you hoping to cable a long distance? would it need parralel feed cables and does this make the BB more viable?

    I haven't heard of anything relating to a must for BB use in this situation

  4. #4
    Junior Member rhyslittle's Avatar
    Join Date
    May 2010
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Red face Re: Busbar - 1.2MVA generator install

    Found some pretty useful info on diesel generators here at Generators for sale, Generators for rent, Power protection | Shenton Group

  5. #5
    Junior Member tonynulty's Avatar
    Join Date
    May 2010
    Location
    South Wales
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Busbar - 1.2MVA generator install

    1.2 mega watt is a big generator, the current this generator can produce on 415volts is very very high, to carry a current like this will probably require a busbar system, if you try to carry this type of current in cables you may need to parralell 4 250mm cables up, or whatever, not good practice.

  6. #6
    Electricians Arms Member davelerave's Avatar
    Join Date
    Sep 2009
    Location
    ROI
    Posts
    428
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Busbar - 1.2MVA generator install

    ya what's the limit on number of paralleled cables?

  7. #7
    Super Moderator Lenny's Avatar
    Join Date
    Dec 2008
    Location
    South Wales
    Posts
    5,524
    Thanks
    2
    Thanked 7 Times in 2 Posts

    Default Re: Busbar - 1.2MVA generator install

    Fair play, that is a massive genset.....be worth a read of appendix 8 in ol' red should you go down this route.
    Last edited by Lenny; 29-05-2010 at 08:20 PM.
    electricians forum pens


    Make sure you buy one, it's for charity.

  8. #8
    Junior Member tonynulty's Avatar
    Join Date
    May 2010
    Location
    South Wales
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Busbar - 1.2MVA generator install

    I dont think there is a specified limit as long as the load is covered,but the problem is connecting at each end, if you use 4 250mm 4core cables, thats 16 connections 4 on each phase + neutral, almost impossible connecting depending on the size of termination box.

  9. #9
    Junior Member tonynulty's Avatar
    Join Date
    May 2010
    Location
    South Wales
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Busbar - 1.2MVA generator install

    I dont think your supplier is giving you crap, its easier and better practice to carry this kind of load using busbars.

    if you parralell cables up they all have to be fed from the same set of fuses or breakers, you cannot feed these cables from different switch fuses because if 1 set of fuses becomes tired and blows the other 3 cables will be trying to carry the load , cables will be overloaded
    Last edited by tonynulty; 29-05-2010 at 08:37 PM.

  10. #10
    Electricians Arms Member johnboy6083's Avatar
    Join Date
    May 2010
    Location
    Rochester, Kent
    Posts
    218
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Busbar - 1.2MVA generator install

    use 500 singles in AWA, thats what we did on the powerstation i just finished at!

    or busbar!
    By the time youve gained enough experience to satisfy the old boys, your too old and knackered to use it!

Similar Threads

  1. new rcbo to old busbar
    By petewan in forum Electrical Forum | General Electrical Forum
    Replies: 4
    Last Post: 18-08-2009, 09:39 PM
  2. connecting a busbar
    By philaxgt500 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 3
    Last Post: 16-12-2008, 11:05 PM
  3. Busbar Refrence method??
    By Gordy Watt in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 0
    Last Post: 05-05-2008, 02:52 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24