Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > Electricians Courses & Training > Electrical Courses Feedback
Forgot Password? Join Us!

Electrical Courses Feedback Positive & negative feedback about the various electricians courses and training centres. Visitors to the site are reminded that the details contained within user comments are uncorroborated and as such should not be read as fact but as the opinion of the person who left the comment.

Reply
 
LinkBack Thread Tools Display Modes
Old 08-03-2008   #1 (permalink)
treelectric
Junior Member
 
Join Date: Mar 2008
Location: Gloucestershire
Posts: 8
View treelectric's Photo Album
Default 2391 practical

Just had a go at the 2391 practical, and messed it up. have a lot of experience and did my theory home work, but time was the problem.
It was a periodic inspection and I thought this meant a 10% inspection, followed by all the usual instrument tests, then writing out certificates. Actually I was told it was a FULL periodic, whatever this is.( I haven't managed to find the description in GN3 or BS7671. Can any one help with this)?
Anyway I was informed by the examiner that this meant taking off ALL the covers from all circuit outputs, including final ring circuit, and then of course putting them all back on again before the live tests, which incidentally had to include Ze.
I actually spent a whole hour of my test taking covers off and putting them on again, which didn't seem to me like a test of my understanding and ablity.
However, that is the nature of it, so I would be pleased to hear from anyone who has succesfully done this, and especially would appreciate some tips on how to organise to get all done in the time allowed.
Is the order of tests really fixed? In this exam situation, starting with a live circuit, it would be more time efficient to start with Ze test, then at least most of the calculations could be done, even if there wasn't time to put everything back together. I would really welcome some feedback on this.

treelectric is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-03-2008   #2 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,028
View Shakey's Photo Album
Default Re: 2391 practical

Ok,

the PIR board is always a full inspection. So, as you found out that means ALL covers off (except the trunking!) The 10 percent is sampling, which you can do in the real world depending on the condition of the installation, but not in the exam.

You have 120 miniuts which terminates when you hand in your completed PIR, although the examiner does have a bit of tolerence with the time.

The tests are in order as stated in GN3. So its

Continuity (bonding and CPC's) so your R1+R2's and your ring tests
Insulation
Polarity
EFLI's
RCD,s and functionals

your EFLI's wil include Ze,
PEFC and PSCC (on both the main AND sub boards)
and your Zs' measurements

These can be done in any order, but i would generally go Ze, recconect the earth then straight into PEFC, then PSCC.

Note that you DONT have to mesure Zs on all the circuits, just the socket outlets on the ring, and socket outlet on the radial off the sub board. In accordance with the EAWR's, C&G state on all of the other circuits you can measure OR calculate Zs. So you have Ze, and R1+R2, so save time and calculate!

As a rough guide to timing, you should aim to complete your visuals, refit covers, and be nulling you meter for the bonding tests at around the 30 minuite point. Take one hour to do your tests, then aim to start your report with about 20-30 minuites to go

And remember:

No matter what, NEVER EVER switch on the main isolator on the three phase board with the busbar cover removed - this is an instant fail!!!!



hope this helps
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-03-2008   #3 (permalink)
treelectric
Junior Member
 
Join Date: Mar 2008
Location: Gloucestershire
Posts: 8
View treelectric's Photo Album
Default Re: 2391 practical

Yes it does help, especially as I wasn't sure if I could calculate Zs on non socket outlets or had to measure them. Your advice about finishing the inspection in 30 min does give me something to aim for, as that was the problem when I did it.
I was told I could calculate pscc and pefc if I wanted.
treelectric is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-03-2008   #4 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,028
View Shakey's Photo Album
Default Re: 2391 practical

Quote:
Originally Posted by treelectric View Post
Yes it does help, especially as I wasn't sure if I could calculate Zs on non socket outlets or had to measure them. Your advice about finishing the inspection in 30 min does give me something to aim for, as that was the problem when I did it.
I was told I could calculate pscc and pefc if I wanted.

Ok, if you have Ze, then you can calculate PEFC, but how are you gonna calculate PSCC? You dont know the impedence of the line to neutral loop so dont see how, (unless its TNCS of course!) but even then, only on the three phase board.

Rememebr you need PFC's on both boards, so if you are gonna calculate PEFC on the sub board, then its Ze plus R1+R2 of the submain cable supplying the sub board.- but even if it is TNCS you would need Rn of the submain cable to be able to calculate PSCC. Personally, I would always measure PFC's, it only takes two minuites!

With the Zs for all the non s/o circuits, C&G specifically say that you can calculate OR measure


and good luck!

Last edited by Shakey; 09-03-2008 at 09:46 PM.
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-03-2008   #5 (permalink)
treelectric
Junior Member
 
Join Date: Mar 2008
Location: Gloucestershire
Posts: 8
View treelectric's Photo Album
Default Re: 2391 practical

yes, I do see what you mean, but my old meter gives me Z between live and phase, as well as Ze so usually just calculate it. Maybe on the next try I'll use the meter they supply as I noted it did pscc and pefc.
Do you need Zs at the actual sub board? Or do you put the Ze for the main board into the schedule of test results for the 2nd board? To me it would seem much more logical to take another Ze at the sub board, as you could in a real situation have a long run of cable between the two, and that could make a significant difference to disconnection times. And for the sub main, the connection cable between the two would be part of the external
impedance loop. Am I right?
And thanks again.
treelectric is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-03-2008   #6 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,028
View Shakey's Photo Album
Default Re: 2391 practical

Quote:
Originally Posted by treelectric View Post
yes, I do see what you mean, but my old meter gives me Z between live and phase, as well as Ze so usually just calculate it. Maybe on the next try I'll use the meter they supply as I noted it did pscc and pefc.
Do you need Zs at the actual sub board? Or do you put the Ze for the main board into the schedule of test results for the 2nd board? To me it would seem much more logical to take another Ze at the sub board, as you could in a real situation have a long run of cable between the two, and that could make a significant difference to disconnection times. And for the sub main, the connection cable between the two would be part of the external
impedance loop. Am I right?
And thanks again.
Ok,

your meter actually measures Z anyway, so if you connect it line to Earth its Ze, line to neutral would be Z. And meters measuring PFC's do the same, between line and earth its PEFC and line and neutral its PSCC

now for the submain, take your measurement, but wether its Ze or Zs its the same reading at the point! Your Ze is only the external EFLI, and we disconnect the incoming earth so we are ONLY reading that part of the circuit which is external.

Now if you wanted to measure Ze at the sub board, you wouldnt disconnect the incoming earth to the suboard, and even if you did, you would still get parralel paths through your main and supplementary bonds etc etc.

And it wouldnt be Ze because its not external to the installation, because it includes R1+R2 of the submain. So actually when you measure the incoming to the sub board, you are measuring Ze + (R1+R2) , which of course is Zs!!!

and of course, the disconnection times (through the Zs measured at the submain circuits) ALREADY includes 'true' Ze + (R1+R2 submain) + (R1+R2 particular submain final circuit)

So, on both of your schedules of test results it is acceptable to put the same value of Ze (because you will only have one value of Ze)

although it is also acceptable to include R1+R2 (and the Zs value) of the submain cable as if it was another final circuit

i always tell people: its YOUR paperwork, and as long as you explain what you have entered, and it is logical, then you cant (or shouldnt ) be criticised for it

hey this getting good aint it!!!

Last edited by Shakey; 16-03-2008 at 09:22 AM.
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-03-2008   #7 (permalink)
treelectric
Junior Member
 
Join Date: Mar 2008
Location: Gloucestershire
Posts: 8
View treelectric's Photo Album
Default Re: 2391 practical

Yes, theres some useful stuff coming out of this. Thanks.
treelectric is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 16-03-2008   #8 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,028
View Shakey's Photo Album
Default Re: 2391 practical

Quote:
Originally Posted by treelectric View Post
Yes, theres some useful stuff coming out of this. Thanks.
no probs, any other queries you have, fire away
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 2 Weeks Ago   #9 (permalink)
flukey
Junior Member
 
flukey's Avatar
 
Join Date: Jul 2008
Posts: 29
View flukey's Photo Album
Default Re: 2391 practical

hi
noticed that you mention using your own meter during the pir??
when i took my 2391 we were told we couldnt use our own meters so had the added problem of using a meter your not familiar with
flukey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 2 Weeks Ago   #10 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,028
View Shakey's Photo Album
Default Re: 2391 practical

Quote:
Originally Posted by flukey View Post
hi
noticed that you mention using your own meter during the pir??
when i took my 2391 we were told we couldnt use our own meters so had the added problem of using a meter your not familiar with
well thats just the training centre then, there is nothing in C&G rules to stop you using your own meter

Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 08:13 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Free Advertising : Mortgages : Home Equity Loan : Wedding Flower Bouquet : Debt Consolidation

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28