New DB in garage conversion
Hi , now that im legally allowed to bodge electrics
my first notifiable work is a new Install on a garage conversion...
my plan at customer request! install new 4way DB in garage prior to conversion to a kitchen.
i intend to run new 25mm supply cables / 16mm earth from Meter out of a service connector and a 100a dp isolator, i then want to keep them low to the ground (out of sight) and enclose the cables in 25mm metal conduit and take them the short 6m distance around the front of house 90o bend and into the garage where the new DB will be! the customer wants to keep it all seperate from his house as he wants to install 2x washers and 2x dryers plus a lighting , cooker and power circuit!! i suggested extending the ring but he said no! seperate just in case he reverts back when he sells up in future!!
can you envisage any probs with my set up i plan..! i not tried to fit 2x 25mm cables in 25mm conduit yet so before i buy any any body else done it?
steve
- 09-02-2010 #2Respected Member
- Join Date
- Jan 2010
- Location
- Hertfordshire
- Posts
- 1,201
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: New DB in garage conversion
You might find it a bit tight ( 2x25mm + 16mm cpc?) in 25mm conduit.and a couple of 90 bends!
Is there a service block there at the moment?
If there is I would suggest tails from the block to a switded fuse swa from the switced fuse to C.U. all outgoing ways of c.u. rcbo
You need to do the calcs for correct cable sizes
- 09-02-2010 #3Electricians Arms Member
- Join Date
- Jan 2010
- Location
- Durham
- Posts
- 1,444
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: New DB in garage conversion
thought as much..!! is there any thing wrong with running the Earth seperatly in 20mm conduit?
the conduit incoporates only 2x 90 bends.. one at bottom of meter box and one at angle from garage approx 3m distance between..
looked at SWA but its more of a favour to this guy than a profit job!!! he wants cheapest i can do..! only reason i mentioned the 25mm tails is that i have 10m of brown and blue hanging in garage from a job i never needed them on
- 09-02-2010 #4Administrator
- Join Date
- Mar 2008
- Location
- In MY world.
- Posts
- 5,466
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: New DB in garage conversion
I would try and mechanically protect them if possible, especially being outside at low level.
The only sensible way i think is to use 16 or 25 SWA.
But, it doesnt play nice on 90 degree bends.
- 09-02-2010 #5Electricians Arms Member
- Join Date
- Jan 2010
- Location
- Durham
- Posts
- 1,444
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: New DB in garage conversion
cheers guys...! wellll the main house is wired in 16mm tails as it is protected by a 60 a fuse! might go with the 16mm swa
Similar Threads
-
***Useful Information for Apprentices***
By amberleaf in forum Electrical Forum | General Electrical ForumReplies: 239Last Post: 2 Weeks Ago, 11:24 AM -
Running Cables to the Garage
By walec in forum Electrical Forum | General Electrical ForumReplies: 3Last Post: 11-01-2010, 06:59 PM -
Garage conversion
By tickover in forum Electrical Forum | General Electrical ForumReplies: 3Last Post: 07-01-2010, 11:55 AM -
Garage Conversion, Notifiable?
By TPES in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 1Last Post: 05-12-2009, 07:54 AM -
running power to garage
By seppe in forum Electrical Forum | General Electrical ForumReplies: 17Last Post: 05-11-2008, 09:28 AM



LinkBack URL
About LinkBacks



Reply With Quote







Bookmarks