Results 1 to 9 of 9
Electricians & Electrical Forum - Bonding again

Bonding again

Discuss Bonding again at Electricians Forums; Just a quick one, for those who have more experience and knowledge than I. External gas meter, 22mm copper runs externally along wall around corner into kitchen also up the ...
  1. #1
    Member
    Join Date
    Aug 2007
    Posts
    161
    Thanks
    2
    Thanked 5 Times
    in 5 Posts
    Tagged
    0 Thread(s)

    Default Bonding again

    Just a quick one, for those who have more experience and knowledge than I.
    External gas meter, 22mm copper runs externally along wall around corner into kitchen also up the wall
    and into landing for combi boiler. Water rises in kitchen in copper.
    Question: Can you bond both services with one piece of 10mm earth cable, providing you do not break the cable at the first bonding clamp ? Do you bond the gas inside the kitchen even though it also runs outside
    and up the wall ? or can you bond it in the meter cupboard and then run it along and into the kitchen for the water ? Please help, as I wish to finish as soon as possible and have a rest.
    Many thanks, Pat

  2. #2
    Electricians Arms Member
    Join Date
    Dec 2009
    Posts
    556
    Thanks
    1
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Re: Bonding again

    u can bond with 0ne 10mm if there is no break in the cable

  3. #3
    The Innkeeper Sintra's Avatar
    Join Date
    Aug 2009
    Location
    Belfast/London
    Posts
    10,395
    Thanks
    432
    Thanked 1,239 Times
    in 933 Posts
    Tagged
    0 Thread(s)

    Default Re: Bonding again

    For a service pipe, the main bonding conductor should be connected as near as possible to the point where the service enters the building. The connection must be before any branched pipework and on the consumers side of any meter. If possible the connection should be made within 600mm of the meter outlet. Where the meter is outside, the bonding connection should be made at the point of entry of the service into the building. 544.1.2
    Where a main bonding conductor loops in and out to connect to an extraneous-conductive-part, the conductor should be unbroken at the connection. 528.3.3

    Hope this helps.
    "I'm an Electrician, not a Magician"

  4. #4
    Member
    Join Date
    Mar 2010
    Location
    east riding of yorkshire
    Posts
    584
    Thanks
    16
    Thanked 13 Times
    in 10 Posts
    Tagged
    0 Thread(s)

    Default Re: Bonding again

    sintra i love your replies, theyre always very professional and informative
    (not that everybody elses arent)

  5. #5
    acat
    Guest

    Default Re: Bonding again

    I reckon hes got it the wrong way round anyone that can give a reply like that quoting the relevant regs is a magician not an electrician


    Chris

  6. #6
    Electricians Arms Member
    pennywise's Avatar
    Join Date
    Jul 2009
    Location
    London
    Posts
    2,804
    Thanks
    126
    Thanked 196 Times
    in 164 Posts
    Tagged
    0 Thread(s)

    Default Re: Bonding again

    He's like my old lecturer, swear he only spoke in binary too

  7. #7
    AEC
    AEC is offline
    Member
    Join Date
    Jan 2010
    Location
    Northern Britain
    Posts
    71
    Thanks
    0
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: Bonding again

    Good quote re regs there.

    But I think the issue lies with th looney plumber / gas fitter.

    With the pipe outside the property, if you were to bond the gas in the kitchen that would be after the branch. Taking the cable outside and connecting to the pipe then means external influences on connection an bonding clip.

    Although the 600mm cant be achived, because pipe outside and pipes inside after branch, I would connect in this case in meter box. Know this was done away with several Editions ago but think this might be best option.

    Anyone any thoughts?

  8. #8
    Member
    Join Date
    Feb 2010
    Location
    Blackpool
    Posts
    538
    Thanks
    12
    Thanked 33 Times
    in 31 Posts
    Tagged
    0 Thread(s)

    Default Re: Bonding again

    i would always bond the gas and water from a separate 10mm earth (even with no break) and in this case i would definately bond the gas in the meter cupboard

  9. #9
    Electricians Arms Member
    JASON's Avatar
    Join Date
    Mar 2008
    Location
    Button Pressing
    Posts
    8,086
    Thanks
    899
    Thanked 944 Times
    in 665 Posts
    Tagged
    0 Thread(s)

    Default Re: Bonding again

    To add more confusion, i generally try and bond water first and then to gas if done in one run.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Main Bonding and Cross Bonding question?
    By chrisgc in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 43
    Last Post: 17-07-2012, 08:07 PM
  2. Cross bonding of water pipes/Supplementry bonding?
    By Kev2632 in forum Electrical Forum: General Electrical Forum
    Replies: 6
    Last Post: 07-06-2012, 08:48 AM
  3. main protective bonding.... supplementry bonding
    By i=p/u in forum Electrical Forum: General Electrical Forum
    Replies: 18
    Last Post: 22-05-2012, 09:50 PM
  4. Domestic Gas Bonding-Check, Water Bonding-Check, Main Earth...???
    By 1shortcircuit in forum Electrical Forum: General Electrical Forum
    Replies: 4
    Last Post: 05-08-2011, 07:05 PM
  5. Main protective bonding and supplementary bonding, help please!
    By Gazap in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 8
    Last Post: 11-05-2011, 11:39 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.