High ze and circuit zs ????

Discuss High ze and circuit zs ???? in the Electrical Forum, General Electrical Forum at Electricians Forums Discussion Boards; Urgent advice please. I have done a consumer unit change where the main earth is 10mm and meter tails are 16mm. I have connected new 25mm tails on consumer side ...
  1. #1
    Electricians Forums Senior
    Join Date
    Feb 2009
    Posts
    277
    Thanks
    28
    Thanked 6 Times in 6 Posts

    Default High ze and circuit zs ????

    Urgent advice please.

    I have done a consumer unit change where the main earth is 10mm and meter tails are 16mm.
    I have connected new 25mm tails on consumer side of isolator switch and 16mm main earth to single pole block onto DNO 10mm earth.

    Problem I have is a Ze of 0.54 and PSCC of 10KA. Is this something I can correct or is it a DNO problem?

    Zs on all circuits is within limit except oven circuit which is 1.52 against max permitted 1.44.
    Obviously will come down if Ze does.


  2. #2
    Electricians Arms Member pennywise's Avatar
    Join Date
    Jul 2009
    Location
    London
    Posts
    2,730
    Thanks
    113
    Thanked 187 Times in 156 Posts

    Default Re: High ze and circuit zs ????

    what earthing system is it?


  3. #3
    Electricians Forums Senior
    Join Date
    Feb 2009
    Posts
    277
    Thanks
    28
    Thanked 6 Times in 6 Posts

    Default Re: High ze and circuit zs ????

    Quote Originally Posted by pennywise View Post
    what earthing system is it?
    Originally thought TNCS but need to take back of kitchen cupboard out tommorrow as it is concealing very old metal clad enclosure and could be TNS ?
    Main earth can be seen clamped to incomming cable below the cupboard.

  4. #4
    Electricians Arms Member
    Join Date
    Mar 2009
    Posts
    1,075
    Thanks
    0
    Thanked 17 Times in 15 Posts

    Default Re: High ze and circuit zs ????

    If its TNS then no problem, max of 0.8 allowed

  5. #5
    Electricians Arms Member pennywise's Avatar
    Join Date
    Jul 2009
    Location
    London
    Posts
    2,730
    Thanks
    113
    Thanked 187 Times in 156 Posts

    Default Re: High ze and circuit zs ????

    I think you may find it to be TN-S having a look should confirm it and if thats the case it's within 0.8.

  6. #6
    Electricians Forums Senior
    Join Date
    Feb 2009
    Posts
    277
    Thanks
    28
    Thanked 6 Times in 6 Posts

    Default Re: High ze and circuit zs ????

    Quote Originally Posted by sparks1234 View Post
    If its TNS then no problem, max of 0.8 allowed
    Thanks Sparks 1234 and Pennywise.
    Ok with the 0.8 for TNS but this still gives a problem with Oven circuit which has Zs 1.52 against max permitted of 1.44 ?

  7. #7
    Electricians Arms Member
    Join Date
    Mar 2009
    Posts
    1,075
    Thanks
    0
    Thanked 17 Times in 15 Posts

    Default Re: High ze and circuit zs ????

    can you lower the breaker at all?

  8. #8
    Forum Admin JASON's Avatar
    Join Date
    Mar 2008
    Location
    Button Pressing
    Posts
    8,132
    Thanks
    940
    Thanked 921 Times in 662 Posts

    Default Re: High ze and circuit zs ????

    Well, if you go by the regs then you would be ok as the CU you have just installed will have full RCD protection, which allows 1667 ohms.
    Spark & A Half.


    Please Read The Electricians Forums Rules Here:
    http://www.electriciansforums.co.uk/...5-10-08-a.html





    <<<<If a member has assisted, please show your appreciation with the "THANKS" button!!!

  9. #9
    Electricians Forums Senior
    Join Date
    Feb 2009
    Posts
    277
    Thanks
    28
    Thanked 6 Times in 6 Posts

    Default Re: High ze and circuit zs ????

    Quote Originally Posted by sparks1234 View Post
    can you lower the breaker at all?
    Not sure of the cooker rating. Very old free standing unit.
    6mm T/E used from 32A breaker and cooker switch has a socket.

    Would lowering to 16A create tripping problems ??

    Long term the Client has sumitted plans to extend property and the kitchen will be moved with new circuits and appliances.

  10. #10
    Electricians Arms Member
    Join Date
    Mar 2009
    Posts
    1,075
    Thanks
    0
    Thanked 17 Times in 15 Posts

    Default Re: High ze and circuit zs ????

    depending on make of board, you can order 25 amp MCB,s, alternatively if you cant get one to fit the board you could put an enclosure next to the consumer unit and down rate it slightly, that is if the cokker loading allows

  11. #11
    Electricians Forums Senior
    Join Date
    Feb 2009
    Posts
    277
    Thanks
    28
    Thanked 6 Times in 6 Posts

    Default Re: High ze and circuit zs ????

    Quote Originally Posted by Jason.S View Post
    Well, if you go by the regs then you would be ok as the CU you have just installed will have full RCD protection, which allows 1667 ohms.
    Thanks Jason.
    17th ed high integrity cu fitted.
    With the intended plans to extend and relocate kitchen etc. Is it enough to just comment on the high reading on the cert and leave it at that. ?

  12. #12
    Electricians Forums Senior
    Join Date
    Feb 2009
    Posts
    277
    Thanks
    28
    Thanked 6 Times in 6 Posts

    Default Re: High ze and circuit zs ????

    Quote Originally Posted by sparks1234 View Post
    depending on make of board, you can order 25 amp MCB,s, alternatively if you cant get one to fit the board you could put an enclosure next to the consumer unit and down rate it slightly, that is if the cokker loading allows
    An additional enclosure next to cu not really an option as just fitted 17th ed high integrity 15 way board to allow for all future build plans on property at client request to avoid all seperate enclosures and add ons etc. Do wylex do 25A

  13. #13
    Forum Admin JASON's Avatar
    Join Date
    Mar 2008
    Location
    Button Pressing
    Posts
    8,132
    Thanks
    940
    Thanked 921 Times in 662 Posts

    Default Re: High ze and circuit zs ????

    Quote Originally Posted by sidekick View Post
    Thanks Jason.
    17th ed high integrity cu fitted.
    With the intended plans to extend and relocate kitchen etc. Is it enough to just comment on the high reading on the cert and leave it at that. ?
    Yes you can and i expect you will need to include the cost of a new radial for the cooker when the other works are being done.
    Spark & A Half.


    Please Read The Electricians Forums Rules Here:
    http://www.electriciansforums.co.uk/...5-10-08-a.html





    <<<<If a member has assisted, please show your appreciation with the "THANKS" button!!!

  14. #14
    Electricians Arms Member pevvers's Avatar
    Join Date
    Jul 2009
    Location
    London
    Posts
    590
    Thanks
    1
    Thanked 11 Times in 11 Posts

    Default Re: High ze and circuit zs ????

    So your R1+R2 on a cooker circuit is nearly a whole ohm?!

    What CSA is the cable, and how long is the run?

  15. #15
    Electricians Arms Member
    Bromd123's Avatar
    Join Date
    Dec 2009
    Location
    Manchester
    Posts
    143
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: High ze and circuit zs ????

    Couldnt this be caused by a bad termination? at the cooker point?
    “Let the future tell the truth, and evaluate each one according to his work and accomplishments. The present is theirs; the future, for which I have really worked, is mine.”

    Nikola Tesla

Page 1 of 2 12 LastLast

Similar Threads

  1. Newbie question... garage circuit connected to ring final circuit.
    By Chris_Peef in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 16
    Last Post: 18-07-2012, 08:03 PM
  2. LED GU10 lighting max number per circuit , circuit design, dimmers
    By lazy username in forum Electrical Forum, General Electrical Forum
    Replies: 23
    Last Post: 06-07-2012, 10:16 AM
  3. Slightly high Zs on large ring circuit
    By PB1 in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 2
    Last Post: 02-12-2011, 08:12 AM
  4. Spurring off from a lighting circuit at the DB to power a door chime circuit.
    By Goody in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 2
    Last Post: 26-07-2011, 07:49 PM
  5. Question regarding high Zs on 3-phase motor circuit using BS88 fuses
    By Steveb555 in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 2
    Last Post: 25-07-2011, 03:54 PM
  6. High continuity reading when testing lighting circuit
    By MWE in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 22
    Last Post: 05-10-2010, 10:54 PM
  7. Study of short circuit pattern in induction motors and it’s effect on circuit brakers
    By Blood-Lover in forum Electrical Forum, General Electrical Forum
    Replies: 0
    Last Post: 02-11-2009, 06:40 AM
  8. 3 phase motor, high resistance & high amps.
    By Dave0098 in forum Commercial and Industrial Electrical
    Replies: 3
    Last Post: 14-10-2009, 02:15 AM
  9. High impedance on working RCD circuit???
    By BuddySpark in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 5
    Last Post: 29-09-2009, 07:55 AM
  10. Are You Experienced?
    By Bane in forum Chit Chat - Off Topic
    Replies: 9
    Last Post: 06-02-2008, 08:38 PM

Visitors found this page by searching for:

No searches found for this page yet.

Tags for this Thread