Discuss High ze and circuit zs ???? in the Electrical Forum, General Electrical Forum at Electricians Forums Discussion Boards; Urgent advice please. I have done a consumer unit change where the main earth is 10mm and meter tails are 16mm. I have connected new 25mm tails on consumer side ...- 22-04-2010 #1Electricians Forums Senior
- Join Date
- Feb 2009
- Posts
- 277
- Thanks
- 28
- Thanked 6 Times in 6 Posts
High ze and circuit zs ????
Urgent advice please.
I have done a consumer unit change where the main earth is 10mm and meter tails are 16mm.
I have connected new 25mm tails on consumer side of isolator switch and 16mm main earth to single pole block onto DNO 10mm earth.
Problem I have is a Ze of 0.54 and PSCC of 10KA. Is this something I can correct or is it a DNO problem?
Zs on all circuits is within limit except oven circuit which is 1.52 against max permitted 1.44.
Obviously will come down if Ze does.
- 22-04-2010 #2Electricians Arms Member
- Join Date
- Jul 2009
- Location
- London
- Posts
- 2,730
- Thanks
- 113
- Thanked 187 Times in 156 Posts
Re: High ze and circuit zs ????
what earthing system is it?
- 22-04-2010 #3Electricians Forums Senior
- Join Date
- Feb 2009
- Posts
- 277
- Thanks
- 28
- Thanked 6 Times in 6 Posts
- 22-04-2010 #4Electricians Arms Member
- Join Date
- Mar 2009
- Posts
- 1,075
- Thanks
- 0
- Thanked 17 Times in 15 Posts
Re: High ze and circuit zs ????
If its TNS then no problem, max of 0.8 allowed
- 22-04-2010 #5Electricians Arms Member
- Join Date
- Jul 2009
- Location
- London
- Posts
- 2,730
- Thanks
- 113
- Thanked 187 Times in 156 Posts
Re: High ze and circuit zs ????
I think you may find it to be TN-S having a look should confirm it and if thats the case it's within 0.8.
- 22-04-2010 #6Electricians Forums Senior
- Join Date
- Feb 2009
- Posts
- 277
- Thanks
- 28
- Thanked 6 Times in 6 Posts
- 22-04-2010 #7Electricians Arms Member
- Join Date
- Mar 2009
- Posts
- 1,075
- Thanks
- 0
- Thanked 17 Times in 15 Posts
Re: High ze and circuit zs ????
can you lower the breaker at all?
- 22-04-2010 #8Forum Admin
- Join Date
- Mar 2008
- Location
- Button Pressing
- Posts
- 8,132
- Thanks
- 940
- Thanked 921 Times in 662 Posts
Re: High ze and circuit zs ????
Well, if you go by the regs then you would be ok as the CU you have just installed will have full RCD protection, which allows 1667 ohms.
Spark & A Half.
Please Read The Electricians Forums Rules Here:
http://www.electriciansforums.co.uk/...5-10-08-a.html
<<<<If a member has assisted, please show your appreciation with the "THANKS" button!!!
- 22-04-2010 #9Electricians Forums Senior
- Join Date
- Feb 2009
- Posts
- 277
- Thanks
- 28
- Thanked 6 Times in 6 Posts
Re: High ze and circuit zs ????
Not sure of the cooker rating. Very old free standing unit.
6mm T/E used from 32A breaker and cooker switch has a socket.
Would lowering to 16A create tripping problems ??
Long term the Client has sumitted plans to extend property and the kitchen will be moved with new circuits and appliances.
- 22-04-2010 #10Electricians Arms Member
- Join Date
- Mar 2009
- Posts
- 1,075
- Thanks
- 0
- Thanked 17 Times in 15 Posts
Re: High ze and circuit zs ????
depending on make of board, you can order 25 amp MCB,s, alternatively if you cant get one to fit the board you could put an enclosure next to the consumer unit and down rate it slightly, that is if the cokker loading allows
- 22-04-2010 #11Electricians Forums Senior
- Join Date
- Feb 2009
- Posts
- 277
- Thanks
- 28
- Thanked 6 Times in 6 Posts
- 22-04-2010 #12Electricians Forums Senior
- Join Date
- Feb 2009
- Posts
- 277
- Thanks
- 28
- Thanked 6 Times in 6 Posts
Re: High ze and circuit zs ????
- 22-04-2010 #13Forum Admin
- Join Date
- Mar 2008
- Location
- Button Pressing
- Posts
- 8,132
- Thanks
- 940
- Thanked 921 Times in 662 Posts
Re: High ze and circuit zs ????
Spark & A Half.
Please Read The Electricians Forums Rules Here:
http://www.electriciansforums.co.uk/...5-10-08-a.html
<<<<If a member has assisted, please show your appreciation with the "THANKS" button!!!
- 22-04-2010 #14Electricians Arms Member
- Join Date
- Jul 2009
- Location
- London
- Posts
- 590
- Thanks
- 1
- Thanked 11 Times in 11 Posts
Re: High ze and circuit zs ????
So your R1+R2 on a cooker circuit is nearly a whole ohm?!
What CSA is the cable, and how long is the run?
- 23-04-2010 #15Electricians Arms Member

- Join Date
- Dec 2009
- Location
- Manchester
- Posts
- 143
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: High ze and circuit zs ????
Couldnt this be caused by a bad termination? at the cooker point?
“Let the future tell the truth, and evaluate each one according to his work and accomplishments. The present is theirs; the future, for which I have really worked, is mine.”
Nikola Tesla
Similar Threads
-
Newbie question... garage circuit connected to ring final circuit.
By Chris_Peef in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 16Last Post: 18-07-2012, 08:03 PM -
LED GU10 lighting max number per circuit , circuit design, dimmers
By lazy username in forum Electrical Forum, General Electrical ForumReplies: 23Last Post: 06-07-2012, 10:16 AM -
Slightly high Zs on large ring circuit
By PB1 in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 2Last Post: 02-12-2011, 08:12 AM -
Spurring off from a lighting circuit at the DB to power a door chime circuit.
By Goody in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 2Last Post: 26-07-2011, 07:49 PM -
Question regarding high Zs on 3-phase motor circuit using BS88 fuses
By Steveb555 in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 2Last Post: 25-07-2011, 03:54 PM -
High continuity reading when testing lighting circuit
By MWE in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 22Last Post: 05-10-2010, 10:54 PM -
Study of short circuit pattern in induction motors and it’s effect on circuit brakers
By Blood-Lover in forum Electrical Forum, General Electrical ForumReplies: 0Last Post: 02-11-2009, 06:40 AM -
3 phase motor, high resistance & high amps.
By Dave0098 in forum Commercial and Industrial ElectricalReplies: 3Last Post: 14-10-2009, 02:15 AM -
High impedance on working RCD circuit???
By BuddySpark in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 5Last Post: 29-09-2009, 07:55 AM -
Are You Experienced?
By Bane in forum Chit Chat - Off TopicReplies: 9Last Post: 06-02-2008, 08:38 PM
Visitors found this page by searching for:
No searches found for this page yet.



LinkBack URL
About LinkBacks

Reply With Quote















help with my first big quote, any...
1 Hour Ago in Electrical Forum, General Electrical Forum