Mcb tripping ????
Discuss Mcb tripping ???? in the Electrical Forum, General Electrical Forum at Electricians Forums Discussion Boards; Hi guys has anyone had this problem before ? I changed a old board to a 10 way wylex with 2 rcds the testing was all ok apart from the ...- 24-07-2010 #1Electricians Forums Member
- Join Date
- May 2010
- Posts
- 93
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Mcb tripping ????
Hi guys
has anyone had this problem before ?
I changed a old board to a 10 way wylex with 2 rcds
the testing was all ok apart from the kitchen, so this was rewired.
Everything is back on all the testing is ok, however as the house
is empty at the moment went back and noticed the downstairs
ring off, thought was odd as I remember turning everything on. Switched it back on and 15 mins later the mcb trips.
Changed the mcb for another, stayed there for a couple of hours all ok switch everything on, all ok, then unplugged everthing again and left.
Went this morning and it had tripped again ! Hardly any load !Took off every socket and checked all ok apart from a fcu had a chunk missing out of the neutral, so fixed that and switched back in all ok at the moment will go back to house tonight to see if has tripped again, not had this problem before if trips again anyone god any ideas what it could.
be ??
Last edited by waitees; 24-07-2010 at 12:56 PM.
- 24-07-2010 #2Electricians Forums Respected
- Join Date
- Apr 2009
- Location
- Gosport
- Posts
- 525
- Thanks
- 76
- Thanked 52 Times in 51 Posts
Re: Mcb tripping ????
Hi mate,
Any sockets outside? UT room? It could be a moisture problem. What loads are permanently on?
- 24-07-2010 #3Electricians Arms Member
- Join Date
- Mar 2010
- Location
- A, A
- Posts
- 552
- Thanks
- 18
- Thanked 30 Times in 21 Posts
Re: Mcb tripping ????
That's really odd. Have you tried a clamp meter to see if any current is being drawn ?
- 24-07-2010 #4Electricians Forums Member
- Join Date
- May 2010
- Posts
- 93
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Mcb tripping ????
Hello mate
It only does two rooms and two hall sockets, fcu was for elec rad in toilet, which Is always off, it has also a tv on it a few lamps. Couple of other fcu for wall lights but there all off and got right fuses.
Everything is off and still trips ???? After a while not straight away, as I am not there not sure how long it takes maybe a few hours ?
- 24-07-2010 #5Electricians Forums Respected
- Join Date
- Apr 2009
- Location
- Gosport
- Posts
- 525
- Thanks
- 76
- Thanked 52 Times in 51 Posts
Re: Mcb tripping ????
I,d do an insulations test on the rad, maybe the is where the problem lies. If it is not an overload fault (as you said all loads are off) then it is more likely an intermittent earth fault.
- 24-07-2010 #6Electricians Forums Member
- Join Date
- May 2010
- Posts
- 93
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Mcb tripping ????
But surely if there is a problem with the rad this would not cause a problem when it's off ?
- 24-07-2010 #7Electricians Arms Member
- Join Date
- Oct 2009
- Location
- sussex
- Posts
- 3,060
- Thanks
- 321
- Thanked 460 Times in 375 Posts
- 24-07-2010 #8
- 24-07-2010 #9Electricians Forums Member
- Join Date
- May 2010
- Posts
- 93
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Mcb tripping ????
Tell me about it ! The mcb I changed was from my stock, so going to buy a brand new one and try that !
The rad is turned off and isolated from the fcu.
I have checked every socket which is only 9 and no probs. Very confusing !
- 24-07-2010 #10Appreciated on Electricians Forums
- Join Date
- Dec 2008
- Posts
- 12,661
- Thanks
- 631
- Thanked 2,369 Times in 1,453 Posts
Re: Mcb tripping ????
Going by the descriptions you've given, I'd put my money on the L-N insulation breaking down somewhere in the circuit.
It would be unusual (although not unheard) of to have 2 faulty MCB's like that.
- 24-07-2010 #11Electricians Forums Member
- Join Date
- May 2010
- Posts
- 93
- Thanks
- 0
- Thanked 0 Times in 0 Posts
- 24-07-2010 #12Appreciated on Electricians Forums
- Join Date
- Dec 2008
- Posts
- 12,661
- Thanks
- 631
- Thanked 2,369 Times in 1,453 Posts
Re: Mcb tripping ????
Well, what type of old board was it???
- 24-07-2010 #13Electricians Arms Member
- Join Date
- Sep 2009
- Location
- ROI
- Posts
- 1,134
- Thanks
- 4
- Thanked 56 Times in 53 Posts
Re: Mcb tripping ????
just out of curiosity- what type and size circuit protection before and after
and what type of supply on the installation
- 24-07-2010 #14Electricians Forums Member
- Join Date
- May 2010
- Posts
- 93
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Mcb tripping ????
It was a old wooden wylex with rewirable fuses, 25mm tails 16mm main earth with tns set up
Was on a old 30amp changed to 32 amp breaker
- 24-07-2010 #15Electricians Arms Member
- Join Date
- Sep 2009
- Location
- ROI
- Posts
- 1,134
- Thanks
- 4
- Thanked 56 Times in 53 Posts
Re: Mcb tripping ????
tricky one-
assuming replacement mcb is ok and no disturbing loads taking out the 'B' type
and no overload (unlikely)
i'd be inclined to switch on all connected loads- connect L-N together at board and check at 250v to earth as i seen a few odd things happen with L-E short circuits even with rcd protection if memory serves
L-N short circuit seems most likely though
and of course could be totally wrong
Similar Threads
-
Rcd tripping
By piz in forum Electrical Forum, General Electrical ForumReplies: 16Last Post: 07-08-2012, 07:30 AM -
Rcd tripping
By Kev2632 in forum Electrical Forum, General Electrical ForumReplies: 35Last Post: 01-03-2012, 11:58 PM -
RCD tripping on new cu
By Araman in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 36Last Post: 07-07-2011, 07:29 PM -
MCB tripping
By Robo in forum Electrical Forum, General Electrical ForumReplies: 12Last Post: 26-05-2011, 03:40 PM -
Rcd tripping
By roxy in forum Electrical Forum, General Electrical ForumReplies: 7Last Post: 23-05-2011, 08:24 PM -
Rcd tripping
By pjb1 in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 5Last Post: 01-12-2009, 07:50 PM -
Keeps Tripping
By carl9254 in forum Electrical Forum, General Electrical ForumReplies: 23Last Post: 17-11-2009, 02:11 AM -
fan tripping rcd
By rapidrich in forum Electrical Forum, General Electrical ForumReplies: 3Last Post: 02-11-2009, 10:09 PM -
ELR Tripping
By poji in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 4Last Post: 02-11-2009, 08:46 AM -
Suggest a forum category
By Dan in forum Electrical Forum News, Updates and SuggestionsReplies: 18Last Post: 18-02-2008, 04:27 PM



LinkBack URL
About LinkBacks

Reply With Quote















ELAN downlights
1 Hour Ago in Electrical Forum, General Electrical Forum