Underfloor heating and electric towel rails

Discuss Underfloor heating and electric towel rails in the Electrical Forum, General Electrical Forum at Electricians Forums Discussion Boards; Hi I have been asked by a client to provide and fit electric underfloor heating and electric towel rails but they have asked for the towel rail to come on ...
  1. #1
    Electricians Forums Senior
    Join Date
    Sep 2008
    Posts
    128
    Thanks
    12
    Thanked 0 Times in 0 Posts

    Default Underfloor heating and electric towel rails

    Hi

    I have been asked by a client to provide and fit electric underfloor heating and electric towel rails but they have asked for the towel rail to come on and off with the underfloor heating but also have an easily operated over-ride so towel rails can be switched on/off independently.

    Does anybody know if this can be done and if so any suggestions on the best way to do it?

    Thanks.


  2. #2
    Electricians Arms Member
    Join Date
    Sep 2009
    Location
    ROI
    Posts
    1,134
    Thanks
    4
    Thanked 56 Times in 53 Posts

    Default Re: Underfloor heating and electric towel rails

    i'm not familiar but how is the UFH zoned and is it peak or off-peak input?

    is it just one manual changeover you want for the towel rails or individual manual changeover

  3. Last edited by davelerave; 16-08-2010 at 04:02 PM.

  4. #3
    New to Electricians Forums
    Join Date
    Mar 2009
    Posts
    26
    Thanks
    18
    Thanked 0 Times in 0 Posts

    Lightbulb Re: Underfloor heating and electric towel rails

    As long as you run a cable big enough to handle the load of the UFH and Towel heaters i see no problem with them coming from the same dedicated MCB

    4mm T&e radial? depending on load. The UFH will have its own independent Thermostat though, with a FCU with appropriate fuse. If they want to individually switch the towel rails can you not just supply each one off an individual FCU.

    With regards to UFH and towel rails coming on at the same time---I'm not sure about that---- soneone else on here will know more ---- apologies if i've stated the obvious to you, just tryin to help

  5. #4
    Electricians Arms Member SirKit Breaker's Avatar
    Join Date
    Jul 2009
    Location
    On my way back to Wembley with Bradford City FC
    Posts
    3,766
    Thanks
    286
    Thanked 661 Times in 521 Posts

    Default Re: Underfloor heating and electric towel rails

    The only way i can see to do it is by using a relay and a lot of messing about, the output to the heating element would have to switch the supply to the radiator, Why oh why do customers have to be awkward and different. The fact is UFH is crap and once they get the first bill they wont use it.

    Tell them to buy a heater with a built in timer and have it done with.

    Cheers...........Howard.

    THE IMPOSSIBLE I CAN DO AT ONCE, MIRACLES CAN TAKE A LITTLE LONGER

  6. #5
    Electricians Forums Senior
    Join Date
    Mar 2010
    Location
    norfolk
    Posts
    254
    Thanks
    0
    Thanked 20 Times in 19 Posts

    Default Re: Underfloor heating and electric towel rails

    If the UFH programmer can handle the load (they`re normally 16 amps), you could feed the 20A Switch or fused spur depending on total load - into the UFH programmer with the floor tails connected direct here - then switched feed out to fused spur for towel rail so it can be controlled by programmer

  7. #6
    Electricians Arms Member
    Join Date
    Sep 2009
    Location
    ROI
    Posts
    1,134
    Thanks
    4
    Thanked 56 Times in 53 Posts

    Default Re: Underfloor heating and electric towel rails

    the towel rails will prob be separate 'home runs'

    if all the towel rails and the ufh are single zones all you need is a multipole contactor for towel rails and changeover from ufh controls(auto) to perm feed(manual) using a 2-way switch
    all control wiring fed from same control circuit mcb

    if the ufh is all zoned up prob a multi-input relay to prevent feedback

    if ufh is off-peak input i assume there's no point to this as the towel rails will be peak supply
    Last edited by davelerave; 16-08-2010 at 07:13 PM.

  8. #7
    Electricians Arms Member

    Join Date
    Apr 2010
    Location
    Anglesey North Wales
    Posts
    3,756
    Thanks
    115
    Thanked 700 Times in 523 Posts

    Default Re: Underfloor heating and electric towel rails

    nip out get a honey well central heating programmer , stick 2 small contators on the output ,then they can control the towel rail and UFH as they wish pre programmed on for 123 hours then off easy way to do it oh just change the hot water with a lable towel rail

Similar Threads

  1. Electric Underfloor Heating Wiring
    By action jackson in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 13
    Last Post: 20-01-2012, 04:02 PM
  2. Electric underfloor heating on tiled wooden floor
    By Richard in forum Electrical Forum, General Electrical Forum
    Replies: 8
    Last Post: 05-06-2011, 04:03 PM
  3. Electric underfloor heating vs water pipe underfloor vs central heating
    By LukeScotty in forum Electrical Forum, General Electrical Forum
    Replies: 1
    Last Post: 04-04-2011, 06:04 PM
  4. underfloor electric heating Tiled
    By millar in forum Electrical Forum, General Electrical Forum
    Replies: 9
    Last Post: 09-03-2011, 10:48 PM
  5. Replacing (very) old thermostats for electric underfloor heating
    By zcrar70 in forum Central Heating Systems
    Replies: 6
    Last Post: 20-02-2011, 11:20 PM
  6. Electric Underfloor heating problem
    By henry46 in forum Central Heating Systems
    Replies: 2
    Last Post: 30-11-2010, 10:16 PM
  7. Electric Underfloor Heating
    By Dan in forum Electrical Courses & Electrical NVQ's
    Replies: 0
    Last Post: 26-10-2009, 08:38 PM
  8. electric towel rails
    By Scott F in forum Electrical Forum, General Electrical Forum
    Replies: 6
    Last Post: 09-02-2009, 08:32 PM

Visitors found this page by searching for:

electric towel rail with thermostat and timer

towel radiator timer and thermostat

electric towel rail thermostat

instructions programmers for underfloor and heated towel rail

underfoor heating towel rail mcbelectric underfloor heating timerunderfloor heating towel rails

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31