Discuss Photocell with manual override at Electricians Forums; Hello, Have been asked to fit some garden LED light fittings, supply will be coming from fused spur, total load less than 1A. The customer wants a photocell switch fitted ...
  1. #1
    Member
    Join Date
    Dec 2010
    Posts
    64
    Thanks
    2
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Photocell with manual override

    Hello,

    Have been asked to fit some garden LED light fittings, supply will be coming from fused spur, total load less than 1A. The customer wants a photocell switch fitted but also ability to override and manually switch on/off when desired.

    Anyone dealt with this before, would you have any wiring diagrams, descriptions?

    Many Thanks

  2. #2
    Member truckster's Avatar
    Join Date
    May 2011
    Location
    Bideford in Glorious Devon
    Posts
    732
    Thanks
    11
    Thanked 115 Times
    in 106 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    Use a three position switch, one line to photocell, one to lights and third empty. So you have the option of the p/c operating the lights, a manual on and an off.

  3. #3
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    42,147
    Thanks
    970
    Thanked 5,194 Times
    in 4,843 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    i would wire the photocell normally then wire a switch across the Lin and Lout of the photocell. or use 3core/E from spur, 3rd core to supply L to Lout on photocell via switch.
    Last edited by telectrix; 27-07-2011 at 08:41 AM.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  4. The Following User Says Thank You to telectrix For This Useful Post:

    chronyx (27-07-2011)

  5. #4
    Member truckster's Avatar
    Join Date
    May 2011
    Location
    Bideford in Glorious Devon
    Posts
    732
    Thanks
    11
    Thanked 115 Times
    in 106 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    Tel, that won't give a manual off.

  6. #5
    Electricians Arms Member
    Join Date
    Sep 2009
    Location
    ROI
    Posts
    1,137
    Thanks
    4
    Thanked 56 Times
    in 53 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    i'm wondering why he'd want the manual on -if he has a photocell?


    timer and photocell in series i usually do

  7. #6
    Member truckster's Avatar
    Join Date
    May 2011
    Location
    Bideford in Glorious Devon
    Posts
    732
    Thanks
    11
    Thanked 115 Times
    in 106 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    Ive got a similar arrangement and sometimes we don't want the garden lights on if the missus has her 'pretty' candles lights on the deck

  8. #7
    Electricians Arms Member
    Join Date
    Sep 2009
    Location
    ROI
    Posts
    1,137
    Thanks
    4
    Thanked 56 Times
    in 53 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    ya- i mean overriding the photocell to bring 'on' the lites?


    what's the point of that

  9. #8
    Member truckster's Avatar
    Join Date
    May 2011
    Location
    Bideford in Glorious Devon
    Posts
    732
    Thanks
    11
    Thanked 115 Times
    in 106 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    early evening bbq? just for pretties?

  10. #9
    Member
    Join Date
    Dec 2010
    Location
    Surrey, UK
    Posts
    257
    Thanks
    65
    Thanked 10 Times
    in 10 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    Don't some photocells have an override function built in? If you cycle the switch line on and off within five seconds they switch on permanently.

  11. #10
    Electricians Arms Member
    Join Date
    Sep 2009
    Location
    ROI
    Posts
    1,137
    Thanks
    4
    Thanked 56 Times
    in 53 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    some pirs do

    never seen it on a p'cell

  12. The Following User Says Thank You to davelerave For This Useful Post:

    chronyx (27-07-2011)

  13. #11
    Member
    Join Date
    Aug 2010
    Location
    afghanistan
    Posts
    115
    Thanks
    6
    Thanked 5 Times
    in 5 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    Quote Originally Posted by truckster View Post
    Use a three position switch, one line to photocell, one to lights and third empty. So you have the option of the p/c operating the lights, a manual on and an off.
    Thats the way I've always done it, works a treat. Sometimes people want manual on if they know they have friends coming over so leave the light on all the time.

  14. The Following User Says Thank You to pauljpickering8 For This Useful Post:

    davelerave (27-07-2011)

  15. #12
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    42,147
    Thanks
    970
    Thanked 5,194 Times
    in 4,843 Posts
    Tagged
    0 Thread(s)

    Default Re: Photocell with manual override

    Quote Originally Posted by truckster View Post
    Tel, that won't give a manual off.
    oops. i missed the off requirement. either your way or a donkey jacket over the cell.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. kilx box override switch help
    By morrey9 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 1
    Last Post: 05-10-2012, 01:08 PM
  2. Domestic LED floodlight with PIR and ability to override...
    By mnbf9rca in forum Electrical Forum: General Electrical Forum
    Replies: 5
    Last Post: 23-01-2012, 11:18 PM
  3. din rail timer, light switch override for outside lights
    By ianbrookes in forum Electrical Forum: General Electrical Forum
    Replies: 19
    Last Post: 17-01-2012, 06:47 PM
  4. Landlords override switch
    By mag8485 in forum Electrical Forum: General Electrical Forum
    Replies: 11
    Last Post: 20-10-2010, 06:14 PM
  5. central heating override
    By parkerbloggs in forum Electrical Forum: General Electrical Forum
    Replies: 2
    Last Post: 03-02-2010, 09:50 AM

Visitors found this page by searching for:

photocell override switch

photocell with manual override

photocell with switch override

overide switch for photocell

how to wire an override switch

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.