immersion heater high limit stat probs

Discuss immersion heater high limit stat probs in the Electrical Forum, General Electrical Forum at Electricians Forums Discussion Boards; seem to be getting a lot of problems with the high limit stats on new immersion heaters tripping out have tried several makes they all seem to have the same ...
  1. #1
    New to Electricians Forums
    Join Date
    Aug 2011
    Posts
    15
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Default immersion heater high limit stat probs

    seem to be getting a lot of problems with the high limit stats on new immersion heaters tripping out have tried several makes they all seem to have the same problem is anyone else having the problem or found an answer


  2. #2
    Electricians Arms Member
    Join Date
    Oct 2009
    Location
    sussex
    Posts
    3,075
    Thanks
    321
    Thanked 460 Times in 375 Posts

    Default Re: immersion heater high limit stat probs

    Been back to one twice recently...definately not covered or water too hot,so yes...seems there are problems.


  3. #3
    Appreciated on Electricians Forums Tony's Avatar
    Join Date
    Aug 2010
    Location
    Under the Major Oak
    Posts
    8,918
    Thanks
    372
    Thanked 1,090 Times in 827 Posts

    Default Re: immersion heater high limit stat probs

    You two should compare notes on manufacturers then. You could have uncovered an on going problem.
    © of this material under the terms of the Designs, Patents and Copyright Act (1988) remains the property of the author. No copyright material (pictorial or literary) may be retained on any storage device without the permission of the author.
    Permission to display copyrighted material on this or any other forum is at the discretion of the copyright holder. This permission can be rescinded at any time and without notice.


    Please support the Fatally Flawed campaign by signing the E-Petition.

  4. #4
    Electricians Arms Member truckster's Avatar
    Join Date
    May 2011
    Location
    Bideford in Glorious Devon
    Posts
    730
    Thanks
    11
    Thanked 115 Times in 106 Posts

    Default Re: immersion heater high limit stat probs

    Google it, it's a common query so there must be something to it.
    The early bird gets the worm......but it's the second mouse that gets the cheese!

    Electrician Bideford

    My opinion is exactly that: My opinion and it might not always be correct in every situation.

  5. #5
    New to Electricians Forums Draig Coch's Avatar
    Join Date
    Aug 2011
    Location
    God's country.
    Posts
    17
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Default Re: immersion heater high limit stat probs

    As Tony suggests, we have had the same problem with the sats with the integrated manual reset trip. We got the Co in and they said yep thats what they do sometimes but you can buy from us a more accurate stat that will cost slightly more.

    Now I know a lot of us here will be shouting at the screen - but I want what I paid for to work properly! I know what you mean - however as a fix we are tweaking down the stat temp so the device becomes less likely to trip however you run the risk of turning it too low or the device still tripping again if not done enough. Where's the goldilocks meter when you need one.

    Its easier for us to buy the more expensive stat. Speak to your wholesaler he might have a solution for you in the long term.

Similar Threads

  1. immersion stat
    By denniscoton in forum Business Related
    Replies: 9
    Last Post: 14-09-2012, 09:27 PM
  2. immersion heater
    By i=p/u in forum Electrical Forum, General Electrical Forum
    Replies: 23
    Last Post: 22-06-2012, 05:40 PM
  3. immersion heater
    By Martinm in forum Electrical Forum, General Electrical Forum
    Replies: 5
    Last Post: 15-05-2012, 09:48 PM
  4. immersion stat
    By mikeelec in forum Central Heating Systems
    Replies: 2
    Last Post: 12-12-2010, 01:52 PM
  5. Immersion heater...
    By TyBrent in forum Electrical Forum, General Electrical Forum
    Replies: 11
    Last Post: 14-08-2010, 12:33 PM
  6. immersion heater gone again
    By Phil in forum Electrical Forum, General Electrical Forum
    Replies: 6
    Last Post: 03-07-2010, 05:35 PM
  7. immersion Heater
    By chloebear in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 6
    Last Post: 30-03-2010, 11:33 PM
  8. immersion high limit cut out
    By oldtimer in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 3
    Last Post: 17-03-2010, 02:57 PM
  9. Immersion heater
    By YTSOxford in forum Electrical Forum, General Electrical Forum
    Replies: 4
    Last Post: 03-11-2008, 09:47 PM
  10. Hi Guys
    By jamaicajoe in forum New Member Introductions
    Replies: 2
    Last Post: 08-08-2007, 07:25 PM

Visitors found this page by searching for:

emmersion rod stats

limitations of immersion heaters

best quality immersion heater stat

position of the stats immersion heater

immersion heater twin stat aa929

premium immersion stat

limit stat for smiths heater

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31