Discuss meter position in the Electrical Forum, General Electrical Forum at Electricians Forums Discussion Boards; hi all, could i please get some help. Might be a silly question but does the electric meter need to be near the fuse board? or can i mount an ...- 16-08-2011 #1New to Electricians Forums
- Join Date
- May 2011
- Posts
- 4
- Thanks
- 0
- Thanked 0 Times in 0 Posts
meter position
hi all,
could i please get some help. Might be a silly question but does the electric meter need to be near the fuse board?
or can i mount an isolator by the meter and take a sub main to the fuse board?
thanks.
- 16-08-2011 #2New to Electricians Forums
- Join Date
- Aug 2011
- Location
- West Sussex
- Posts
- 17
- Thanks
- 3
- Thanked 6 Times in 3 Posts
Re: meter position
Hi,
Yes you can install a fused isolator then go out with a sub main to the CU
It say's on the card Electrician and not Magician
- 16-08-2011 #3Appreciated Member


- Join Date
- Sep 2010
- Location
- cheshire/staffordshire
- Posts
- 25,925
- Thanks
- 647
- Thanked 3,583 Times in 3,307 Posts
Re: meter position
but if your tails are over 3 metres, you need a fused isolator at the front end.
TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.
I don't suffer from Insanity. I enjoy every minute of it.
- 16-08-2011 #4Electricians Arms Member
- Join Date
- May 2011
- Location
- Reading
- Posts
- 1,090
- Thanks
- 74
- Thanked 50 Times in 47 Posts
I'm too slow at this haha. At least I knew the answer. That's the main thing
- 16-08-2011 #5New to Electricians Forums
- Join Date
- May 2011
- Posts
- 4
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: meter position
thanks guys, guessing the SEE are just being annoying then.
- 16-08-2011 #6New to Electricians Forums
- Join Date
- Aug 2011
- Location
- West Sussex
- Posts
- 17
- Thanks
- 3
- Thanked 6 Times in 3 Posts
Re: meter position
Hi ric,
What are the SEE up to ?It say's on the card Electrician and not Magician
- 16-08-2011 #7New to Electricians Forums
- Join Date
- May 2011
- Posts
- 4
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: meter position
hi sparky prime,
on the job i'm on there needs to be 3 new supplies brought into the the premises. 1 for shop, 1 for ground floor flat and 1 for 1st floor flat. The supplies were going to be mounted in a communal hall with the meters. i was going to mount isolators by the meters then submain off to positions of CU's . SEE wants to mount meters within 3m of CU. I don't understand why the meter needs to be next to the CU.
Similar Threads
-
3 Phase / Single Meter - change to one communial meter, 4 sub meters, 4 flat supplies
By ianbrookes in forum Electrical Forum, General Electrical ForumReplies: 1Last Post: 10-06-2012, 01:51 PM -
CU Position
By Midwest in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 7Last Post: 10-06-2012, 11:30 AM -
C. U. Position
By boberty in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 10Last Post: 23-10-2011, 01:34 PM -
Equipment needed - amp meter, ir temp. meter & solar radiation meter
By STEL in forum Photovoltaic / Solar Panels & Green Energy ForumReplies: 4Last Post: 02-08-2011, 03:27 PM -
Generation meter position for multiple inverter installs.
By gr7 in forum Photovoltaic / Solar Panels & Green Energy ForumReplies: 3Last Post: 28-06-2011, 08:38 PM -
How close can incoming gas pipe/meter be to electric supply/meter
By jase31 in forum Electrical Forum, General Electrical ForumReplies: 5Last Post: 16-04-2011, 06:46 PM -
suns position
By GPack in forum Photovoltaic / Solar Panels & Green Energy ForumReplies: 9Last Post: 04-04-2011, 02:06 PM -
mid position valve.
By ian in forum Central Heating SystemsReplies: 4Last Post: 09-10-2010, 06:33 PM -
Past papers for 2391?
By LukeScotty in forum Electrical Courses & Electrical NVQ'sReplies: 7Last Post: 16-08-2009, 03:39 PM -
Possible position coming up
By montybaber in forum Electricians Unite - Jobs In Your AreaReplies: 16Last Post: 29-09-2008, 08:05 PM
Visitors found this page by searching for:
No searches found for this page yet.



LinkBack URL
About LinkBacks

Reply With Quote















Napit certs oh dear
8 Minutes Ago in Electrical Forum, General Electrical Forum