    Default Help with Garage Electrics please.

    Hello
    I am new here so apologies if this is the wrong place for this thread or it has been asked before.

    I am upgrading my Garage electrics and would like some advice please.

    It is detached and is currently fed via 6mm SWA from the RCD side of my Consumer unit.
    I want to renew electrics in garage to:
    4 Double metal clad Sockets
    2 Fluorescent Light units
    2 Metal clad Switches (2 way lighting)
    A new Metal 4 way Consumer unit.

    My questions are regarding the consumer unit.
    1) Do i need to buy a dedicated "Garage" Consumer unit or can i buy a Metal Consumer unit and install my own MCB's ?
    2) Do i need a RCD built into the Consumer unit or is the RCD on my Household C/U adequate ?
    3) In the future i will be adding security lights and Garden lights. Should i buy a 4 way unit or do you think a 2way would do ?
    4) I know i need 6A for lights, 16A for the sockets but will another 6A be ok for the outside/Security lights ?

    I want a 4 way unit just to isolate the internal lights from the outside lights for maintainence etc.
    It is also going to be installed by a competant Part P qualified person.

    Hope i've given enough info but if not, i'll try to give more when asked.

    Thanks.

  2. #2
    Junior Member mark_the_spark's Avatar
    Join Date
    Aug 2009
    Posts
    20
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Help with Garage Electrics please.

    1) Do i need to buy a dedicated "Garage" Consumer unit or can i buy a Metal Consumer unit and install my own MCB's ?
    Nope any C.U. will be fine, I take it its not going to subjected to rain etc...
    2) Do i need a RCD built into the Consumer unit or is the RCD on my Household C/U adequate ?
    So long as there is an RCD it should be fine, although you might want to take into consideration nucience tripping if something does wrong
    3) In the future i will be adding security lights and Garden lights. Should i buy a 4 way unit or do you think a 2way would do ?
    Id get a 7-10 way, not a lot of difference in price
    4) I know i need 6A for lights, 16A for the sockets but will another 6A be ok for the outside/Security lights ?
    Yep, that will be fine

    Also please note that when working outside of your equipotential zone (your house) your electrical supplier will sometimes insist on a TT system being installed (your meant to tell them haha) and the garage earthing being seperated from the house earthing.

    PS what size MCB are you using from your house C.U.? 20a?
    Last edited by mark_the_spark; 30-08-2009 at 11:30 PM.

  3. #3
    Junior Member Danno7's Avatar
    Join Date
    Aug 2009
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Help with Garage Electrics please.

    The SWA is coming off of a 16A MCB in my House C/U.

    As for the TT system, i'm sure my installer will tell them, haha !

    Surely if the SWA is run from the RCD side of my C/U, this would surfice, safety wise ?

    My current electrics in the garage have been run from this since my Household Consumer unit upgrade 3 years ago...And well beyond that judging by the state of them ( Bakelite, Vulcan wiring and all !!!!!!)

    Cheers Mark

    Oh !
    Forgot to add, As reguarding Nuscience tripping, Would an RCD in the Garage C/U be overkill considering there is one in the Household C/U, or would this help ?

    Thanks
    Last edited by Danno7; 31-08-2009 at 12:42 AM. Reason: Automerged Doublepost

  4. #4
    Administrator Jason.S's Avatar
    Join Date
    Mar 2008
    Location
    In MY world.
    Posts
    5,466
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Help with Garage Electrics please.

    Quote Originally Posted by Danno7 View Post
    Oh !
    Forgot to add, As reguarding Nuscience tripping, Would an RCD in the Garage C/U be overkill considering there is one in the Household C/U, or would this help ?

    Thanks
    IDEALLY you would have the house end MCB on the non rcd side of your CU.

    This then would make the garage totally separate from the house and have its own RCD main switch, which would then avoid tripping the house RCD should a fault occur in the garage.

    And no, its not a good idea to have 2 x 30mA rcd's in line.

  5. #5
    Junior Member Danno7's Avatar
    Join Date
    Aug 2009
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Help with Garage Electrics please.

    Thanks for the advice.
    I will leave the SWA on the RCD of my House C/U.

    And will get a Metal 5-7 way unit for my garage (non-RCD).

    Thanks all

  6. #6
    Junior Member Danno7's Avatar
    Join Date
    Aug 2009
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Help with Garage Electrics please.

    Quick additional question.

    The garage C/U will be connected by SWA to the household c/u and it's earth system, i know i need to install an Earthing rod as this garage installation will technically be a TT system.
    I do then disconnect the SWA earth on the Garage c/u end ? Yes ?

    By the way, it will all be installed by a semi Competent person...Myself, embarking on my 1st Big(ish) install. I have my part P, VRQ level 2 and Just need to get all the theory into practice.
    Because i am not yet joined to napit or nic, could i get local authority to check, test and sign this off or should i get a Full Part P qualifies electrician in to test and check/sign off ? And Would this be allowed ?

    Thanks.
    Last edited by Danno7; 02-09-2009 at 12:39 AM.

  7. #7
    Electricians Arms Member TPES's Avatar
    Join Date
    Aug 2008
    Posts
    748
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Help with Garage Electrics please.

    You wont be able install everything yourself and then get a part P registered spark to sign it off, If you know someone who is registered it would be ideal to work alongside them, that way they can see any work your doing is complying . They would need to see the whole install though.

    Rather than paying out for them to come over and give you a hand you could offer them your time, labouring. on there own work.

Similar Threads

  1. garage supply
    By lurch in forum Electrical Forum | General Electrical Forum
    Replies: 5
    Last Post: 21-08-2009, 12:41 AM
  2. Detached Garage
    By Dazzol2009 in forum Electrical Forum | General Electrical Forum
    Replies: 11
    Last Post: 24-06-2009, 01:56 AM
  3. garage cu + Napit
    By tuckermot in forum Electrical Forum | General Electrical Forum
    Replies: 16
    Last Post: 05-03-2009, 10:34 PM
  4. Garage power
    By YTSOxford in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 2
    Last Post: 09-12-2008, 05:02 PM
  5. running power to garage
    By seppe in forum Electrical Forum | General Electrical Forum
    Replies: 17
    Last Post: 05-11-2008, 09:28 AM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24