- 30-08-2009 #1
Help with Garage Electrics please.
Hello
I am new here so apologies if this is the wrong place for this thread or it has been asked before.
I am upgrading my Garage electrics and would like some advice please.
It is detached and is currently fed via 6mm SWA from the RCD side of my Consumer unit.
I want to renew electrics in garage to:
4 Double metal clad Sockets
2 Fluorescent Light units
2 Metal clad Switches (2 way lighting)
A new Metal 4 way Consumer unit.
My questions are regarding the consumer unit.
1) Do i need to buy a dedicated "Garage" Consumer unit or can i buy a Metal Consumer unit and install my own MCB's ?
2) Do i need a RCD built into the Consumer unit or is the RCD on my Household C/U adequate ?
3) In the future i will be adding security lights and Garden lights. Should i buy a 4 way unit or do you think a 2way would do ?
4) I know i need 6A for lights, 16A for the sockets but will another 6A be ok for the outside/Security lights ?
I want a 4 way unit just to isolate the internal lights from the outside lights for maintainence etc.
It is also going to be installed by a competant Part P qualified person.
Hope i've given enough info but if not, i'll try to give more when asked.
Thanks.
- 30-08-2009 #2
Re: Help with Garage Electrics please.
1) Do i need to buy a dedicated "Garage" Consumer unit or can i buy a Metal Consumer unit and install my own MCB's ?
Nope any C.U. will be fine, I take it its not going to subjected to rain etc...
2) Do i need a RCD built into the Consumer unit or is the RCD on my Household C/U adequate ?
So long as there is an RCD it should be fine, although you might want to take into consideration nucience tripping if something does wrong
3) In the future i will be adding security lights and Garden lights. Should i buy a 4 way unit or do you think a 2way would do ?
Id get a 7-10 way, not a lot of difference in price
4) I know i need 6A for lights, 16A for the sockets but will another 6A be ok for the outside/Security lights ?
Yep, that will be fine
Also please note that when working outside of your equipotential zone (your house) your electrical supplier will sometimes insist on a TT system being installed (your meant to tell them haha) and the garage earthing being seperated from the house earthing.
PS what size MCB are you using from your house C.U.? 20a?Last edited by mark_the_spark; 30-08-2009 at 11:30 PM.
- 31-08-2009 #3
Re: Help with Garage Electrics please.
The SWA is coming off of a 16A MCB in my House C/U.
As for the TT system, i'm sure my installer will tell them, haha !
Surely if the SWA is run from the RCD side of my C/U, this would surfice, safety wise ?
My current electrics in the garage have been run from this since my Household Consumer unit upgrade 3 years ago...And well beyond that judging by the state of them ( Bakelite, Vulcan wiring and all !!!!!!)
Cheers Mark
Oh !
Forgot to add, As reguarding Nuscience tripping, Would an RCD in the Garage C/U be overkill considering there is one in the Household C/U, or would this help ?
ThanksLast edited by Danno7; 31-08-2009 at 12:42 AM. Reason: Automerged Doublepost
- 31-08-2009 #4Administrator
- Join Date
- Mar 2008
- Location
- In MY world.
- Posts
- 5,466
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Help with Garage Electrics please.
IDEALLY you would have the house end MCB on the non rcd side of your CU.
This then would make the garage totally separate from the house and have its own RCD main switch, which would then avoid tripping the house RCD should a fault occur in the garage.
And no, its not a good idea to have 2 x 30mA rcd's in line.
- 31-08-2009 #5
Re: Help with Garage Electrics please.
Thanks for the advice.
I will leave the SWA on the RCD of my House C/U.
And will get a Metal 5-7 way unit for my garage (non-RCD).
Thanks all
- 01-09-2009 #6
Re: Help with Garage Electrics please.
Quick additional question.
The garage C/U will be connected by SWA to the household c/u and it's earth system, i know i need to install an Earthing rod as this garage installation will technically be a TT system.
I do then disconnect the SWA earth on the Garage c/u end ? Yes ?
By the way, it will all be installed by a semi Competent person...Myself, embarking on my 1st Big(ish) install. I have my part P, VRQ level 2 and Just need to get all the theory into practice.
Because i am not yet joined to napit or nic, could i get local authority to check, test and sign this off or should i get a Full Part P qualifies electrician in to test and check/sign off ? And Would this be allowed ?
Thanks.Last edited by Danno7; 02-09-2009 at 12:39 AM.
- 02-09-2009 #7
Re: Help with Garage Electrics please.
You wont be able install everything yourself and then get a part P registered spark to sign it off, If you know someone who is registered it would be ideal to work alongside them, that way they can see any work your doing is complying . They would need to see the whole install though.
Rather than paying out for them to come over and give you a hand you could offer them your time, labouring. on there own work.
Similar Threads
-
garage supply
By lurch in forum Electrical Forum | General Electrical ForumReplies: 5Last Post: 21-08-2009, 12:41 AM -
Detached Garage
By Dazzol2009 in forum Electrical Forum | General Electrical ForumReplies: 11Last Post: 24-06-2009, 01:56 AM -
garage cu + Napit
By tuckermot in forum Electrical Forum | General Electrical ForumReplies: 16Last Post: 05-03-2009, 10:34 PM -
Garage power
By YTSOxford in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 2Last Post: 09-12-2008, 05:02 PM -
running power to garage
By seppe in forum Electrical Forum | General Electrical ForumReplies: 17Last Post: 05-11-2008, 09:28 AM
Visitors found this page by searching for:
Nobody landed on this page from a search engine, yet!



LinkBack URL
About LinkBacks




Reply With Quote







Bookmarks