Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Electrical Tools and Products
Forgot Password? Join Us!

Electrical Tools and Products Discuss topics related to electrical tools, brands, wholesalers, and other products in the UK.

Reply
 
LinkBack Thread Tools Display Modes
Old 11-06-2008   #1 (permalink)
ecclescake
Junior Member
 
Join Date: Jun 2008
Location: salford
Posts: 9
View ecclescake's Photo Album
Default Lock nut spanner

I've had one of these for about 2 years now and its still going strong they are well worth the money. I bought mine off elite tool company on e-bay or Specialist bush spanner distributor - Easy Life | Tools

ecclescake is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-06-2008   #2 (permalink)
Cirrus
Moderator
 
Cirrus's Avatar
 
Join Date: Sep 2007
Posts: 1,081
View Cirrus's Photo Album
Default Re: Lock nut spanner

Yeah, very useful for commercial / industrial work. A must-have tool I think.
Cirrus is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-06-2008   #3 (permalink)
wayne
Respected Member
 
wayne's Avatar
 
Join Date: Feb 2008
Posts: 725
View wayne's Photo Album
Default Re: Lock nut spanner

different to the ones ive seen and used in the past ,these might work!!

wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 08:13 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Remortgages : Personal Loans : Secured Loan : Secured Loans : Best Credit Cards

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28