Hi,

In the building i work we done yearly 3hr discharges of our emergenvy lights, my question is, if for instance we do a test on say floor 6, we would knock of the breakers for them circuits and we would check after 3hrs etc etc, but how long after a full discharge can people be aloud to work in the area again?

As if the emergency light batteries are drained, they would not stay on for the correct amount of time for people to exit the floor should there be a power cut for instance.

I have tried looking for the regulation to answer this but cant really find it. Any help would be great,

Cheers
Shawn
Sparky83 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2010   #2 (permalink)
Mark_Burgess
Junior Member
 

Join Date: May 2009
Posts: 27
Thanks: 6
Thanked 11 Times in 3 Posts
Default Re: Full Discharge Emg Lighting testing

Can the test be arranged for the last 3 hours of the working day? Could solve the problem if thats possible.
Mark_Burgess is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2010   #3 (permalink)
Tester Steve
Member
 

Join Date: Aug 2009
Posts: 53
Thanks: 1
Thanked 11 Times in 11 Posts
Default Re: Full Discharge Emg Lighting testing

Yep, used to get paid double bubble to do this on a Sunday untill they twigged it could be done 3 hours before end of work !!

Steve
Tester Steve is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2010   #4 (permalink)
Jason.S
Super Moderator
 
Jason.S's Avatar
 

Join Date: Mar 2008
Location: In MY world.
Posts: 4,383
Thanks: 154
Thanked 530 Times in 475 Posts
Default Re: Full Discharge Emg Lighting testing

Quote:
Originally Posted by Tester Steve View Post
Yep, used to get paid double bubble to do this on a Sunday untill they twigged it could be done 3 hours before end of work !!

Steve

Bummer
__________________
Whatever happens, don't blame me.
--------------------------------------------------------------------------------------
All opinions expressed by myself, are not necessarily those of Electricians Forums.
Jason.S is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-02-2010   #5 (permalink)
pevvers
Senior Member
 
Snake Champion! Card Toss Champion! Tetrollapse Champion!
Tournaments Won: 1

Join Date: Jul 2009
Posts: 213
Thanks: 10
Thanked 23 Times in 19 Posts
Default Re: Full Discharge Emg Lighting testing

Quote:
Originally Posted by Sparky83 View Post
but how long after a full discharge can people be aloud to work in the area again?
IIRC, BS5266 quotes 24 hours after a full drain down test, otherwise you would have to give everybody torches...
pevvers is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-02-2010   #6 (permalink)
scotsparky
Respected Member
 
scotsparky's Avatar
 

Join Date: Apr 2009
Location: Glasgow
Posts: 1,048
Thanks: 16
Thanked 96 Times in 93 Posts
Default Re: Full Discharge Emg Lighting testing

if there is a few EM circuits on each floor i would think about doing 1 circuit on each floor each day. This means that at any time at least some fully charged em light fittings

eg. 3 em circuits 1 circuit each day so 2thirds are always fully charged and so no disruption to staff.
__________________
If you hear a bang its me please get an ambulance!!

Last edited by scotsparky; 04-02-2010 at 01:03 AM..
scotsparky is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-02-2010   #7 (permalink)
Sparky83
Member
 

Join Date: Feb 2008
Posts: 43
Thanks: 1
Thanked 4 Times in 4 Posts
Default Re: Full Discharge Emg Lighting testing

Quote:
Originally Posted by pevvers View Post
IIRC, BS5266 quotes 24 hours after a full drain down test, otherwise you would have to give everybody torches...

Cheers for the replies guys, i forgot tomention that the building (not all areas) has 24hr workers, so in some areas there are poeple there all the time.

Does any body have a link to a pdf or something of BS5266, i have looked myself but cant seem to find one.

Cheers
Shawn
Sparky83 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 4 Weeks Ago   #8 (permalink)
pevvers
Senior Member
 
Snake Champion! Card Toss Champion! Tetrollapse Champion!
Tournaments Won: 1

Join Date: Jul 2009
Posts: 213
Thanks: 10
Thanked 23 Times in 19 Posts
Default Re: Full Discharge Emg Lighting testing

PM me mate, and I may be able to sort something out....
pevvers is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 4 Weeks Ago   #9 (permalink)
acat
Respected Member
 
acat's Avatar
 

Join Date: Apr 2009
Location: Ceredigion
Posts: 1,196
Thanks: 50
Thanked 195 Times in 189 Posts
Send a message via MSN to acat
Default Re: Full Discharge Emg Lighting testing

http://www.root3automation.com/pdf/E...egulations.pdf



Hope that one is of help to you.


Chris
__________________
I dont need 9 lives I need 90
acat is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply
  

Bookmarks



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
***Useful Information For The Working Sparky*** amberleaf Electrical Forum | General Electrical Forum 205 3 Weeks Ago 03:21 PM
Testing Festoon lighting billygoat Inspection, Testing and Certification of Electrical Installations 8 25-11-2009 07:52 PM
Emergency Lighting Testing requirements claret73 Inspection, Testing and Certification of Electrical Installations 6 10-11-2009 02:52 PM
Testing lighting circuit with no CPC Doug Inspection, Testing and Certification of Electrical Installations 14 24-10-2009 10:01 PM
lighting chain testing Preacher man Electrical Forum | General Electrical Forum 2 12-09-2007 10:09 PM



Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0

u.m Network: Contractor Forum | Tilers Forum | Plastering Forum | Flooring Forum | Plumbing Forum |
(c) 2008 Electricians Forum | Electrical Forum | Electrical Advice | Electricians Jobs | A forum for electricians in the UK