- 08-02-2010 #51
Re: outdoor heater circuit with pir....
We use these on pub smoking areas, up to 2hr time out function and you can cancel the timer anytime you like. They do a PIR version too

Outdoor Pushbutton Timer - Energyoutdoor - Products - Elkay
- 08-02-2010 #52
Re: outdoor heater circuit with pir....
I would definitely be doing this in conduit & singles & run everything to/from a large (300x220) weatherproof adaptable box
and you only need a single contactor with your latest setup as you are switching the common supply
and weatherproof switches would handle the 6-7 amps per heater, these probably wouldn't do that much on load switching, the contactor would be doing that
- 08-02-2010 #53
Re: outdoor heater circuit with pir....
hi one thing to watch is the amp rating on the pir, may be to small for the heaters
- 09-02-2010 #54Senior Member
- Join Date
- Nov 2009
- Location
- North of Bristol
- Posts
- 296
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: outdoor heater circuit with pir....
I like Monty Python as much as the next man, but there's a limit....................
- 09-02-2010 #55
Re: outdoor heater circuit with pir....
Firstly a BIG THANKS to everyone so far for your input, glad to of got so many people's cog's turning, plus I don't know if i can click thanks too everyone on the thread lol
So if I wired as in my last drawing, but used an enclosure housing a 1 pole contactor (only used a 2 because I can't find a 1 pole on the internet so far, but any suggestions would be gratefully accepted....) a din rail rather than all the junction boxes, and 2 outdoor light switches (which your telling me would handle the ampage fine) then the drawing all looks good
and the pir in the drawing could be a cheap unit as found in most outdoor security lights as its only switching not carrying the load.....
if thats all correct I think I'm sorted, this is for an outdoor smoking area at my house, I have alot of parties on the weekend and currently have a gas heater, and from experience once everyones in the party spirit they leave it on alot, hence the pir so my electric bill doesn't go crazy.....just so you know the background, I feel you all deserve it after the response lol
- 09-02-2010 #56
Re: outdoor heater circuit with pir....
good luck
how's about an invite to one of these parties then
- 09-02-2010 #57
- 09-02-2010 #58
Re: outdoor heater circuit with pir....
They can do a maximum of a 16amp resistive and inductive based loads, 3.680Kw.
Last edited by pennywise; 09-02-2010 at 06:12 PM.
- 09-02-2010 #59
Re: outdoor heater circuit with pir....
food for thought:
you'll be regularly switching an operating current of about 13A, which is less than the rated current of the device but it could reasonably degrade quickly as it will be breaking on-load currents. that 16A rating could also mean rated at an operating current of 16A for 6 hours, and not switching on-load currents on and off every 5 minutes when someone stands up
bear in mind the surge startup currents of these heaters could be substantially more, especially if they are infra-red
- 09-02-2010 #60
Re: outdoor heater circuit with pir....
so out of interest then one of these items would be fine as a make shift control, for both lamps until I get everything together for the final thing, and they'd handle it without a problem????? I'm guessing yes but the chances of the bloke at the screwfix counter knowing the answer is pretty slim lol
so your saying that no these wouldn't do the job?!? just thought they'd do for a makeshift while all the other bits come as I can pick one up at screwfix tomorrow if need be, and yeah I had read somewhere heater have a surge on startup, and if you want to spend alot of money you can buy soft start switches with in-built pir/timerLast edited by reese646; 09-02-2010 at 06:18 PM. Reason: Automerged Doublepost
Similar Threads
-
Section - 301- Questions - Testing ,
By amberleaf in forum Electrical Forum | General Electrical ForumReplies: 742Last Post: 5 Hours Ago, 03:30 PM -
test and inspection sequence
By shaky in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 14Last Post: 10-01-2010, 07:12 PM -
wiring external pir floods off unused immersion circuit
By brucelee in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 8Last Post: 16-12-2009, 11:02 AM -