here's the question
scenario: a TN-S system, where the main earthing terminal is external to the distribution board.
the cable connected to the suppliers earth and the main earthing terminal is the main earthing conductor.
what is the title given to the protective conductor connecting the main earthing terminal to the distribution board (this is also the earth fault path for each cpc)
is it a main bonding conductor, or would it still be classed as the main earthing conductor?
your thoughts are appreciated...
- 09-02-2010 #2
- 09-02-2010 #3Senior Member
- Join Date
- Dec 2009
- Location
- Wolverhampton
- Posts
- 132
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: earthing conductor query
I usually refer to this as the main earthing conductor, as well as the bit the other side of the MET, although the definition in the BRB states that this is between earth and the MET only. Given the apparent absence of a defined name for this bit of cable and given what it does I hearby christen it the main CPC.
- 09-02-2010 #4
Re: earthing conductor query
LOL - I'll make city and guilds aware of the revelation

as defined, main bonding conductors are used to connect extraneous conductive parts, not exposed conductive parts, so that should rule that option out
and the main earthing conductor is clearly defined as the connection from the suppliers means of earthing to the MET
here's a surprising one
definition:
Circuit protective conductors (CPC’s)
A protective conductor connecting exposed-conductive-parts of equipment to the main earthing terminal
I would say that's fairly definitive - a susprising answer but definitiveLast edited by uksel; 09-02-2010 at 04:20 PM. Reason: Automerged Doublepost
- 09-02-2010 #5Administrator
- Join Date
- Mar 2008
- Location
- In MY world.
- Posts
- 5,466
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: earthing conductor query
I would go with MEC from Earth point to CU via MET.
If there was no MET installed then it would be no different.
- 09-02-2010 #6
Re: earthing conductor query
According to BRB figure 2.1 (Page32) it should be called "earthing conductor"
- 09-02-2010 #7
Re: earthing conductor query
that's a drawing of a TT system mate
- 09-02-2010 #8
- 09-02-2010 #9
Re: earthing conductor query
right you are, so with 'B' being the main earthing terminal (external to the db), doesn't show connection to a CU or DB
if it's connecting to the exposed conductive part of the CU i.e. mettalic covering, then it's bonding.
but i'm asking specifically what the conductor that connects the MET to the earth bar in a DB.
purely on definition i'd say CPC
on practicality and it's function i'd say main earthing conductor
Similar Threads
-
***Useful Information For The Working Sparky***
By amberleaf in forum Electrical Forum | General Electrical ForumReplies: 208Last Post: 4 Weeks Ago, 03:14 PM -
Industrial Building Earthing?
By SparkSmog in forum Commercial and Industrial ElectricalReplies: 9Last Post: 13-05-2009, 10:38 PM -
Earthing testing
By kpvarghese in forum Electrical Forum | General Electrical ForumReplies: 0Last Post: 13-05-2009, 02:21 PM -
Earthing 2 CUs
By YTSOxford in forum Electrical Forum | General Electrical ForumReplies: 7Last Post: 11-11-2008, 10:39 PM -
Backup generator (earthing)
By wattsup in forum Electrical Forum | General Electrical ForumReplies: 2Last Post: 26-06-2008, 05:45 PM



LinkBack URL
About LinkBacks




Reply With Quote








Bookmarks