    Question Sun Tan Booth Issues . . . . ??

    I have recently hooked up a sun tan booth for a friend of mine. The people he bought it off claimed that "all it needs is a cooker plug". Once I had looked around it and saw a 10mm T&E hanging from the control box. As the booth is in his garage, I started with a shower enclosure C.U with RCD and a 40a Type B breaker and then ran 10mm SWA to a D.P 40a Switch by the booth. Then connected the T&E into the switch. Problem is when the timer runs out and switches the booth off it trips the 40a MCB. Do I need to start thinking contactors and a Type C MCB???

    Cheers

  2. #2
    UNG
    UNG is offline
    Electricians Arms Member UNG's Avatar
    Join Date
    Jul 2009
    Location
    Nr Wigan, Lancs
    Posts
    633
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Sun Tan Booth Issues . . . . ??

    Although you are using a 40A breaker you don't say what the equipment load is?

  3. #3
    Respected Member bugsy's Avatar
    Join Date
    Jan 2010
    Location
    Hertfordshire
    Posts
    1,201
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Sun Tan Booth Issues . . . . ??

    The tanning booth's we have installed require 32a supply, we always feed them via a 32a RCBO and install 32a isolator adjacent the booth, check the loading and install RCBO and isolator accordingley

  4. #4
    Member Joe S's Avatar
    Join Date
    Apr 2009
    Posts
    37
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Sun Tan Booth Issues . . . . ??

    Quote Originally Posted by bugsy View Post
    The tanning booth's we have installed require 32a supply, we always feed them via a 32a RCBO and install 32a isolator adjacent the booth, check the loading and install RCBO and isolator accordingley

    To be fair, if its tripping a 40a MCB then it'll trip a 32a. Not sure unless the actual unit is faulty or the switch is knackered in the booth and its breaking down while trying break the contact??

  5. #5
    Respected Member bugsy's Avatar
    Join Date
    Jan 2010
    Location
    Hertfordshire
    Posts
    1,201
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Sun Tan Booth Issues . . . . ??

    Im not suggesting you install 32a OCPD and RCBO, that was just an example of the set up, you need to verify loading and install appropriate OCPD and RCBO

  6. #6
    Electricians Arms Member pennywise's Avatar
    Join Date
    Jul 2009
    Posts
    1,434
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Sun Tan Booth Issues . . . . ??

    I would be checking the connections on the timer, but you've probably already done that.

  7. #7
    Electricians Arms Member wirepuller's Avatar
    Join Date
    Oct 2009
    Posts
    669
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Sun Tan Booth Issues . . . . ??

    I had an odd one with some storage heater fans wired through a timer years ago,they switched on fine but every time the clock switched them off it blew the mcb.Eventually traced to a nail through one of the cables...barely shorting...just a flicker on the megger....but you'd expect it to blow when switching on,which it never did yet it was every time on switching off. Just a thought that it could be a similar thing.

  8. #8
    Member Joe S's Avatar
    Join Date
    Apr 2009
    Posts
    37
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Sun Tan Booth Issues . . . . ??

    Quote Originally Posted by bugsy View Post
    Im not suggesting you install 32a OCPD and RCBO, that was just an example of the set up, you need to verify loading and install appropriate OCPD and RCBO

    I wasn't having a go mate, just thinking out loud, lol.

    Quote Originally Posted by wirepuller View Post
    I had an odd one with some storage heater fans wired through a timer years ago,they switched on fine but every time the clock switched them off it blew the mcb.Eventually traced to a nail through one of the cables...barely shorting...just a flicker on the megger....but you'd expect it to blow when switching on,which it never did yet it was every time on switching off. Just a thought that it could be a similar thing.

    I was thinking timer all the way. May have to sit down with a cuppa and take things off and inspect them. Everytime I work for mates it costs me, how does that work?!? LOL.
    Last edited by Joe S; 18-03-2010 at 07:31 AM. Reason: Automerged Doublepost

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24