    Default New sockets solution - Opinion?

    The local housing company I do a lot of work for has asked me to put 2 sockets in a bedroom (currently without any!) in one of their houses (surface trunking). After a quick look at the site the solution seemed to be to drill through the wall behind a hallway socket, and use an RCD fused connection unit to spur from the ring and create a new spur with 2 double 13A sockets on.

    The existing board is re-wirable fuses, and the landlord is not going to want to pay the money to have this upgraded. So my solution is with the RCD fused spur.

    What's your opinion on this? In my eyes this complies with all regulations and is perfectly acceptable.

  2. #2
    Electricians Arms Member
    rocker's Avatar
    Join Date
    Feb 2010
    Location
    Newport, Sunny Wales
    Posts
    3,198
    Thanks
    465
    Thanked 334 Times
    in 247 Posts
    Tagged
    0 Thread(s)

    Default Re: New sockets solution - Opinion?

    If you're using surface trunking theres no need regs wise for RCD anyway, or have I read you wrong?

  3. #3
    Member
    Join Date
    Feb 2010
    Location
    Llantrisant, South Wales
    Posts
    213
    Thanks
    1
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Re: New sockets solution - Opinion?

    Agree with Rocker, I would just put an FCU in and run the sockets off that.

  4. #4
    Member
    Join Date
    Mar 2009
    Location
    Surrey
    Posts
    36
    Thanks
    0
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: New sockets solution - Opinion?

    Yes it will be going surface trunking. However there will be no protection. My understanding is that all additional sockets need to be protected by an RCD. Yes the cables might be on the surface, but there could still be a fault with an appliance which could cause harm. It's in a kids bedroom you see so I really want to provide as much protection as possible!

  5. #5
    Guest123
    Guest

    Default Re: New sockets solution - Opinion?

    All sockets >20A must be have additional protection by 30mA RCD.

    411.3.3

  6. #6
    Member
    Join Date
    Mar 2009
    Location
    Surrey
    Posts
    36
    Thanks
    0
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: New sockets solution - Opinion?

    That would be the one

  7. #7
    Guest123
    Guest

    Default Re: New sockets solution - Opinion?

    There are exceptions, but none would be applicable in your situation.
    Last edited by Guest123; 30-05-2010 at 04:49 PM.

  8. #8
    Electricians Arms Member

    Join Date
    May 2008
    Location
    EU
    Posts
    6,139
    Thanks
    419
    Thanked 890 Times
    in 680 Posts
    Tagged
    0 Thread(s)

    Default Re: New sockets solution - Opinion?

    Quote Originally Posted by sambuca2907 View Post
    T

    In my eyes this complies with all regulations and is perfectly acceptable.

    Is the earthing and bonding Ok ?

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Opinion on new MFT
    By stephen evans in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 13
    Last Post: 02-10-2013, 11:55 AM
  2. your opinion
    By dingledong in forum Electrical Forum: General Electrical Forum
    Replies: 1
    Last Post: 04-12-2011, 07:53 PM
  3. Domestic Best solution
    By SimpleSimon in forum Electrical Forum: General Electrical Forum
    Replies: 5
    Last Post: 22-02-2011, 03:14 PM
  4. need an opinion
    By Bumblescumps in forum Electrical Forum: General Electrical Forum
    Replies: 3
    Last Post: 13-10-2010, 12:00 PM
  5. Looking for the best solution!
    By Mcnabb5 in forum Electrical Forum: General Electrical Forum
    Replies: 0
    Last Post: 18-06-2009, 06:40 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.