No Main Bonding to Gas/Water

Discuss No Main Bonding to Gas/Water in the Electrical Wiring, Theories and Electrical Regulations at Electricians Forums Discussion Boards; Hi Guys, I have an ergent problem, my usual contractor asked me to wire a new boiler he was installing, and i forgot to check the main bonding before commencing ...
  1. #1
    Electricians Forums Member
    Join Date
    Apr 2009
    Posts
    53
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default No Main Bonding to Gas/Water

    Hi Guys,

    I have an ergent problem, my usual contractor asked me to wire a new boiler he was installing, and i forgot to check the main bonding before commencing works! I have only replaced a single socket outlet with a s/f spur and connect the a flex to the boiler and upgraded the supplementary bonding.

    When it came to filling out the minor works certificate and inspecting adequacy of earthing and bonding i noticed that there was none present!! further more i could not identify the main earthing to the house!! although i got a low ZS (0.72ohms) reading back for that circuit!? so this gives me the impression of a TNS/TNC-S earthing system --note the incoming supply is next to the CU--

    How do i stand issueing a certificate etc, i was told by niceic technical helpline that because i had made the circuit live i was now intitled to upgrade the earthing and main bonding at my exspense --How can that be right!!??--

    Could someone please give me some advice that is not cut and paste from the regs book.

    Thanks


  2. #2
    Appreciated on Electricians Forums
    Join Date
    Dec 2008
    Posts
    12,661
    Thanks
    631
    Thanked 2,369 Times in 1,453 Posts

    Default Re: No Main Bonding to Gas/Water

    131.8, does say that earthing and bonding arrangements for the installation should be adequate before carrying out any work, as there is none present at your install, I would say this is not adequate and you should really have mentioned it beforehand.


    Also EDQ 5 in here requires it too.

    Alterations and Additions in Domestic and Similar Premises

  3. Last edited by Guest123; 26-07-2010 at 05:51 PM.

  4. #3
    Electricians Forums Member
    Join Date
    Jan 2010
    Location
    scotland but from Northern Ireland orginally
    Posts
    43
    Thanks
    0
    Thanked 2 Times in 2 Posts

    Default Re: No Main Bonding to Gas/Water

    Basically mate put this one down to experience. You've done the work and you need to make sure the earthing is up to standard unfortunately you've been caught out and I'm sure after this you'll not be again. NICEIC is right.

    You can refuse to connect the boiler till the client agrees to pay you to upgrade the earthing but not really good for business. my advice would be just bite the bullet, run in your earth to standards and remember to check next time. however unfair it may seem.

  5. #4
    Electricians Forums Member
    Join Date
    Apr 2009
    Posts
    53
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: No Main Bonding to Gas/Water

    same regulation niceic guy at technical quoted on me. like i said though, i didn't check before and the deed is now done. I always thought that if it were very minor works such as those i was undertaking, and providing the level of safety is not less than it already was before you started then you were ok. I hate grey area's!

    So any idea's on some loop hole around this that will save me the cost of installing the main bonding?

    Ta

  6. #5
    Electricians Forums Member
    Join Date
    Apr 2009
    Posts
    53
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: No Main Bonding to Gas/Water

    Thanks Gaulty, I think your right!... unfortunately

  7. #6
    Electricians Forums Member
    Join Date
    Jan 2010
    Location
    scotland but from Northern Ireland orginally
    Posts
    43
    Thanks
    0
    Thanked 2 Times in 2 Posts

    Default Re: No Main Bonding to Gas/Water

    no probs, look on it another way if someone ends up fried and you where the last one in and provided a test certificate that was satisfactory you're goin to end up in jail! Think i'd rather pay the money for a drum of earth cable and run in the bonding just chalk it down as a learning curve.

  8. #7
    Electricians Arms Member
    Join Date
    Oct 2009
    Location
    sussex
    Posts
    3,061
    Thanks
    321
    Thanked 460 Times in 375 Posts

    Default Re: No Main Bonding to Gas/Water

    Quote Originally Posted by Ridgey88 View Post
    . I always thought that if it were very minor works such as those i was undertaking, and providing the level of safety is not less than it already was before you started then you were ok.

    So any idea's on some loop hole around this that will save me the cost of installing the main bonding?

    Ta
    The thing is the work you have carried out relies on main bonding as much as the existing installation to be safe in the event of a fault. Therefore by not ensuring adequate main bonding you are carrying out an unsafe installation.

  9. #8
    Electricians Arms Member
    Join Date
    Sep 2008
    Location
    Southampton
    Posts
    296
    Thanks
    2
    Thanked 11 Times in 11 Posts

    Default Re: No Main Bonding to Gas/Water

    Stable door after horse has bolted. Basic stuff your own fault get another job

Similar Threads

  1. Bonding main water PVC
    By dippers in forum Electrical Forum, General Electrical Forum
    Replies: 10
    Last Post: 17-07-2012, 09:02 PM
  2. New house, no main water bonding
    By ash_s3 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 36
    Last Post: 22-03-2012, 07:35 AM
  3. Bonding to main gas and water
    By aaelectric in forum Electrical Forum, General Electrical Forum
    Replies: 12
    Last Post: 29-01-2012, 02:15 PM
  4. Main Bonding of Water Pipe
    By JUD in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 9
    Last Post: 22-11-2011, 10:13 PM
  5. 30 metre run of Main Protective Bonding Conductor to Gas Main and Water Main
    By Les Macaulay in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 22
    Last Post: 18-10-2011, 08:38 AM
  6. Main bonding to gas and water
    By peterb2428 in forum Electrical Forum, General Electrical Forum
    Replies: 3
    Last Post: 13-07-2011, 11:47 AM
  7. Main Gas & Water Bonding
    By Colin Integrale in forum Electrical Forum, General Electrical Forum
    Replies: 14
    Last Post: 06-04-2011, 10:48 PM
  8. no main bonding to water
    By Benny_Boy in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 6
    Last Post: 05-05-2010, 12:12 AM
  9. Main water Bonding
    By EddieB in forum Electrical Forum, General Electrical Forum
    Replies: 9
    Last Post: 09-04-2009, 03:15 PM
  10. Hi, everyone !
    By mary0755 in forum New Member Introductions
    Replies: 2
    Last Post: 08-08-2007, 07:32 PM

Visitors found this page by searching for:

do you need to provide bonding to gas and water when none is present before carrying out minor works

does the main earth bonding have to be replaced after a boiler replacement

do you need main bonding when doing minor works

earth bonding gas and water regulations

verifying main bonding to gas and water

earth bonding to gas and water

what are gas and water bond works and how much does it cost

Tags for this Thread