Discuss No Main Bonding to Gas/Water in the Electrical Wiring, Theories and Electrical Regulations at Electricians Forums Discussion Boards; Hi Guys, I have an ergent problem, my usual contractor asked me to wire a new boiler he was installing, and i forgot to check the main bonding before commencing ...- 26-07-2010 #1Electricians Forums Member
- Join Date
- Apr 2009
- Posts
- 53
- Thanks
- 0
- Thanked 0 Times in 0 Posts
No Main Bonding to Gas/Water
Hi Guys,
I have an ergent problem, my usual contractor asked me to wire a new boiler he was installing, and i forgot to check the main bonding before commencing works! I have only replaced a single socket outlet with a s/f spur and connect the a flex to the boiler and upgraded the supplementary bonding.
When it came to filling out the minor works certificate and inspecting adequacy of earthing and bonding i noticed that there was none present!! further more i could not identify the main earthing to the house!! although i got a low ZS (0.72ohms) reading back for that circuit!? so this gives me the impression of a TNS/TNC-S earthing system --note the incoming supply is next to the CU--
How do i stand issueing a certificate etc, i was told by niceic technical helpline that because i had made the circuit live i was now intitled to upgrade the earthing and main bonding at my exspense --How can that be right!!??--
Could someone please give me some advice that is not cut and paste from the regs book.
Thanks
- 26-07-2010 #2Appreciated on Electricians Forums
- Join Date
- Dec 2008
- Posts
- 12,661
- Thanks
- 631
- Thanked 2,369 Times in 1,453 Posts
Re: No Main Bonding to Gas/Water
131.8, does say that earthing and bonding arrangements for the installation should be adequate before carrying out any work, as there is none present at your install, I would say this is not adequate and you should really have mentioned it beforehand.
Also EDQ 5 in here requires it too.
Alterations and Additions in Domestic and Similar Premises
Last edited by Guest123; 26-07-2010 at 05:51 PM.
- 26-07-2010 #3Electricians Forums Member
- Join Date
- Jan 2010
- Location
- scotland but from Northern Ireland orginally
- Posts
- 43
- Thanks
- 0
- Thanked 2 Times in 2 Posts
Re: No Main Bonding to Gas/Water
Basically mate put this one down to experience. You've done the work and you need to make sure the earthing is up to standard unfortunately you've been caught out and I'm sure after this you'll not be again. NICEIC is right.
You can refuse to connect the boiler till the client agrees to pay you to upgrade the earthing but not really good for business. my advice would be just bite the bullet, run in your earth to standards and remember to check next time. however unfair it may seem.
- 26-07-2010 #4Electricians Forums Member
- Join Date
- Apr 2009
- Posts
- 53
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: No Main Bonding to Gas/Water
same regulation niceic guy at technical quoted on me. like i said though, i didn't check before and the deed is now done. I always thought that if it were very minor works such as those i was undertaking, and providing the level of safety is not less than it already was before you started then you were ok. I hate grey area's!
So any idea's on some loop hole around this that will save me the cost of installing the main bonding?
Ta
- 26-07-2010 #5Electricians Forums Member
- Join Date
- Apr 2009
- Posts
- 53
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: No Main Bonding to Gas/Water
Thanks Gaulty, I think your right!... unfortunately
- 26-07-2010 #6Electricians Forums Member
- Join Date
- Jan 2010
- Location
- scotland but from Northern Ireland orginally
- Posts
- 43
- Thanks
- 0
- Thanked 2 Times in 2 Posts
Re: No Main Bonding to Gas/Water
no probs, look on it another way if someone ends up fried and you where the last one in and provided a test certificate that was satisfactory you're goin to end up in jail! Think i'd rather pay the money for a drum of earth cable and run in the bonding just chalk it down as a learning curve.
- 26-07-2010 #7Electricians Arms Member
- Join Date
- Oct 2009
- Location
- sussex
- Posts
- 3,061
- Thanks
- 321
- Thanked 460 Times in 375 Posts
- 26-07-2010 #8Electricians Arms Member
- Join Date
- Sep 2008
- Location
- Southampton
- Posts
- 296
- Thanks
- 2
- Thanked 11 Times in 11 Posts
Re: No Main Bonding to Gas/Water
Stable door after horse has bolted. Basic stuff your own fault get another job
Similar Threads
-
Bonding main water PVC
By dippers in forum Electrical Forum, General Electrical ForumReplies: 10Last Post: 17-07-2012, 09:02 PM -
New house, no main water bonding
By ash_s3 in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 36Last Post: 22-03-2012, 07:35 AM -
Bonding to main gas and water
By aaelectric in forum Electrical Forum, General Electrical ForumReplies: 12Last Post: 29-01-2012, 02:15 PM -
Main Bonding of Water Pipe
By JUD in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 9Last Post: 22-11-2011, 10:13 PM -
30 metre run of Main Protective Bonding Conductor to Gas Main and Water Main
By Les Macaulay in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 22Last Post: 18-10-2011, 08:38 AM -
Main bonding to gas and water
By peterb2428 in forum Electrical Forum, General Electrical ForumReplies: 3Last Post: 13-07-2011, 11:47 AM -
Main Gas & Water Bonding
By Colin Integrale in forum Electrical Forum, General Electrical ForumReplies: 14Last Post: 06-04-2011, 10:48 PM -
no main bonding to water
By Benny_Boy in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 6Last Post: 05-05-2010, 12:12 AM -
Main water Bonding
By EddieB in forum Electrical Forum, General Electrical ForumReplies: 9Last Post: 09-04-2009, 03:15 PM -
Hi, everyone !
By mary0755 in forum New Member IntroductionsReplies: 2Last Post: 08-08-2007, 07:32 PM



LinkBack URL
About LinkBacks

Reply With Quote















Solar Energy and it's Uses
1 Minute Ago in Electrical Wiring, Theories and Electrical Regulations