    Default Does three go into one?

    Had a look in a customers cu to check that the cable for the new leccy shower was up to the job. I noticed that there were 2 32A breakers fitted and assumed that they were two ring circuits. Then I spotted the third wire in one of them. The cu was replaced 3 years ago by a registered electrician who issued the appropriate certificates.( which I haven't seen yet)

    Am I missing something? Is it ok to have a spur direct from the breaker? ( I've left the BRB and OSG in me toolbag in a customers garage. It was friday and the pub was open what can I say).

    I must admit I haven't tested the circuits so I am guessing that it is a ring with a spur. I have seen this before and last time it was three 2.5mm radials stuffed into one 32A rewireable by a diy 'expert'.
    To cut to the chase... can you spur straight from the breaker?

  2. #2
    The Innkeeper Sintra's Avatar
    Join Date
    Aug 2009
    Location
    Belfast/London
    Posts
    10,367
    Thanks
    431
    Thanked 1,236 Times
    in 931 Posts
    Tagged
    0 Thread(s)

    Default Re: Does three go into one?

    Yes you can.

    An unfused spur can feed either one single or one double socket outlet only and can be taken from the fuse or mcb in the consumer unit. p362 appx 15, 433.1.5
    Last edited by Sintra; 11-09-2010 at 10:18 PM.
    "I'm an Electrician, not a Magician"

  3. The Following User Says Thank You to Sintra For This Useful Post:

    Gaz Bryan (11-09-2010)

  4. #3
    Guest123
    Guest

    Default Re: Does three go into one?

    Yep. Existing socket, JB, or breaker.

  5. The Following User Says Thank You to Guest123 For This Useful Post:

    Gaz Bryan (11-09-2010)

  6. #4
    Member
    Join Date
    Feb 2010
    Location
    buckley
    Posts
    30
    Thanks
    5
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Re: Does three go into one?

    Cheers for the rapid reply. I had a vague recollection that you could spur from the breaker but as i mentioned all me books are locked in someone elses garage. Going back in a few days to satisfy my curiosity and to check that it is a spur.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.