Ze Query

Discuss Ze Query in the Electrical Wiring, Theories and Electrical Regulations at Electricians Forums Discussion Boards; Hi Could anyone answer this query? We are looking to replace a cable that has gone down. The cable is fed from a section board (protected by a a square ...
  1. #1
    New to Electricians Forums
    Join Date
    Jan 2011
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Ze Query

    Hi Could anyone answer this query? We are looking to replace a cable that has gone down. The cable is fed from a section board (protected by a a square "D" CNAE34125 125amp) which in turn is fed directly off the HV transformer (11kv-433V) in the adjacent room (max 3m metres length of cable).

    The supply cables to the section board are 500mm singles with approx 2X150mm earth.

    The Ze is reading 0.17 at the incoming main switch. The problem is the manufacturers Zs reading for the 125amp MCCB is 0.18. The Zs reading at the D.B which is fed from this breaker is 0.44.

    What Ze reading should we expect at the incoming supply? Under normal circumstances 0.17 would be great.

    Any help on this would be appreciated, Cheers


  2. #2
    Electricians Forums Senior
    Join Date
    Dec 2010
    Posts
    277
    Thanks
    2
    Thanked 4 Times in 4 Posts

    Default Re: Ze Query

    500mm single that 1 big ass cable! what is the feeding?


  3. #3
    New to Electricians Forums
    Join Date
    Jan 2011
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Ze Query

    Part of an Airport!!

  4. #4
    Electricians Arms Member IQ Electrical's Avatar
    Join Date
    Oct 2010
    Posts
    4,555
    Thanks
    89
    Thanked 1,191 Times in 883 Posts

    Default Re: Ze Query

    Quote Originally Posted by planetman View Post
    Hi Could anyone answer this query? We are looking to replace a cable that has gone down. The cable is fed from a section board (protected by a a square "D" CNAE34125 125amp) which in turn is fed directly off the HV transformer (11kv-433V) in the adjacent room (max 3m metres length of cable).

    The supply cables to the section board are 500mm singles with approx 2X150mm earth.

    The Ze is reading 0.17 at the incoming main switch. The problem is the manufacturers Zs reading for the 125amp MCCB is 0.18. The Zs reading at the D.B which is fed from this breaker is 0.44.

    What Ze reading should we expect at the incoming supply? Under normal circumstances 0.17 would be great.

    Any help on this would be appreciated, Cheers
    What is the supply system type?

    The ESQCR regulations 2002 suggest:

    TN-S Maximum 0.80 Ohms

    TN-C-S Maximum 0.35 Ohms

    Edit, your transformer is in the adjacent room?

    You're probably getting a bad reading on you EFLI tester due to the proximity of the transformer, check it's impedance on the rating plate and calculate Ze from that plus a negligible amount for the 3 metre cable run.


    BS 7671 calls for an accuracy level of 0.05 ohm (5%), when measuring impedance. Most test instruments available on the market achieve this level, or better. However, when very low readings below 0.1 of an ohm exist, the test instrument can be outside of this requirement. This is because of the 2nd digit tolerance, which can vary between 4 and even 10 digits in some cases. For example; a meter reading of 0.05 ohm, measured with a meter whose tolerance is +/- 2% (+/-4 digits), could have a true value anywhere between 0.01 and 0.09 ohms. The reading would also not be consistent, if measured a number of times.
    Last edited by IQ Electrical; 14-01-2011 at 09:27 AM. Reason: Read the post properly!
    Do it once, do it right....

    Fixed Wire Testing
    www.iqelectrical.co

  5. #5
    New to Electricians Forums
    Join Date
    Jan 2011
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Ze Query

    Thanks! Its TN-C-S, but whats causing me a headache is that Square "D" paper work says 0.18 max Zs, but i dont see how this is achievable without installing huge cabling!?!?!?!

    YEs tansformer is in the adjacent room> ta
    Last edited by planetman; 14-01-2011 at 09:28 AM.

  6. #6
    Appreciated Member

    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    25,843
    Thanks
    647
    Thanked 3,573 Times in 3,298 Posts

    Default Re: Ze Query

    if i read the post correctly, it appears that you have an increase from0.17 to 0.44 on a 3meter run , this seems high. possibility of a high resistance connection? thinking about it, taking the reading at the squareD breaker, you have the resistance of the breaker itself adding to the result. this sounds like a more likely cause.
    Last edited by telectrix; 14-01-2011 at 09:29 AM.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.
    I don't suffer from Insanity. I enjoy every minute of it.


  7. #7
    Electricians Arms Member IQ Electrical's Avatar
    Join Date
    Oct 2010
    Posts
    4,555
    Thanks
    89
    Thanked 1,191 Times in 883 Posts

    Default Re: Ze Query

    Quote Originally Posted by telectrix View Post
    if i read the post correctly, it appears that you have an increase from0.17 to 0.44 on a 3meter run , this seems high. possibility of a high resistance connection?
    I think the 3 metres is the transformer to main switch, he doesn't give a length for the distribution circuit.
    Do it once, do it right....

    Fixed Wire Testing
    www.iqelectrical.co

  8. #8
    Appreciated Member

    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    25,843
    Thanks
    647
    Thanked 3,573 Times in 3,298 Posts

    Default Re: Ze Query

    Quote Originally Posted by IQ Electrical View Post
    I think the 3 metres is the transformer to main switch, he doesn't give a length for the distribution circuit.
    just edited my last post. could it be the resistance of the squareD breaker pushing up the Zs
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.
    I don't suffer from Insanity. I enjoy every minute of it.


  9. #9
    New to Electricians Forums
    Join Date
    Jan 2011
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Ze Query

    Sorry for the confusion. 0.17 is read at the incomer to the Section board which is 3m away from the transformer. Th 0.44 reading is taken from the D.B being fed from the section Board which is 200m away and is fed on a 95mm 4-core. Cheers

  10. #10
    New to Electricians Forums
    Join Date
    Jan 2011
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Ze Query

    Just to add more! the 0.17 reading has been taken on the live side of the incoming supply off the tranny. So with 500m singles and the run being less than 3m it is basically the reading off the tranny.

    Just thinking about it< if a TN-C-S is allowed to be 0.35, how could we possibly expect a Zs reading as low as 0.18????? as the Square D paper work suggests (very confused )

  11. #11
    Appreciated Member

    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    25,843
    Thanks
    647
    Thanked 3,573 Times in 3,298 Posts

    Default Re: Ze Query

    beats me as well. if your Zeat origin were 0.35,a Zs of 0.18 would be impossible to achieve.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.
    I don't suffer from Insanity. I enjoy every minute of it.


Similar Threads

  1. generation meter query - display screen query
    By loser123 in forum Photovoltaic / Solar Panels & Green Energy Forum
    Replies: 2
    Last Post: 02-05-2012, 09:50 AM
  2. TT Query?
    By gottahugenoggin in forum Electrical Forum, General Electrical Forum
    Replies: 5
    Last Post: 03-02-2012, 07:00 PM
  3. PIR query
    By bangtest in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 4
    Last Post: 25-09-2011, 10:30 PM
  4. pir query
    By maveric50 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 3
    Last Post: 11-10-2010, 11:02 AM
  5. using metrel test sheets query and testing query
    By bobby101 in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 0
    Last Post: 22-09-2010, 05:27 PM
  6. R1+R2 query
    By Scooter in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 5
    Last Post: 02-06-2010, 08:45 PM
  7. Tax query
    By keith915 in forum Business Related
    Replies: 1
    Last Post: 26-05-2010, 11:29 PM
  8. RCD query
    By KevA in forum Electrical Forum, General Electrical Forum
    Replies: 2
    Last Post: 13-03-2010, 11:53 AM
  9. **** tt query ****
    By Sav in forum Electrical Forum, General Electrical Forum
    Replies: 4
    Last Post: 07-02-2010, 07:12 PM

Visitors found this page by searching for:

transformer ze calculation

square d mccb max zs

calculate ze from transformer impedance

ze of a transformer

calculating ze from transformer impedance

calculating ze from supply transformer resistance

square d cnae34125

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31