Ze Query
Discuss Ze Query in the Electrical Wiring, Theories and Electrical Regulations at Electricians Forums Discussion Boards; Hi Could anyone answer this query? We are looking to replace a cable that has gone down. The cable is fed from a section board (protected by a a square ...- 14-01-2011 #1New to Electricians Forums
- Join Date
- Jan 2011
- Posts
- 5
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Ze Query
Hi Could anyone answer this query? We are looking to replace a cable that has gone down. The cable is fed from a section board (protected by a a square "D" CNAE34125 125amp) which in turn is fed directly off the HV transformer (11kv-433V) in the adjacent room (max 3m metres length of cable).
The supply cables to the section board are 500mm singles with approx 2X150mm earth.
The Ze is reading 0.17 at the incoming main switch. The problem is the manufacturers Zs reading for the 125amp MCCB is 0.18. The Zs reading at the D.B which is fed from this breaker is 0.44.
What Ze reading should we expect at the incoming supply? Under normal circumstances 0.17 would be great.
Any help on this would be appreciated, Cheers
- 14-01-2011 #2Electricians Forums Senior
- Join Date
- Dec 2010
- Posts
- 277
- Thanks
- 2
- Thanked 4 Times in 4 Posts
Re: Ze Query
500mm single that 1 big ass cable! what is the feeding?
- 14-01-2011 #3New to Electricians Forums
- Join Date
- Jan 2011
- Posts
- 5
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Ze Query
Part of an Airport!!
- 14-01-2011 #4
Re: Ze Query
What is the supply system type?
The ESQCR regulations 2002 suggest:
TN-S Maximum 0.80 Ohms
TN-C-S Maximum 0.35 Ohms
Edit, your transformer is in the adjacent room?
You're probably getting a bad reading on you EFLI tester due to the proximity of the transformer, check it's impedance on the rating plate and calculate Ze from that plus a negligible amount for the 3 metre cable run.
BS 7671 calls for an accuracy level of 0.05 ohm (5%), when measuring impedance. Most test instruments available on the market achieve this level, or better. However, when very low readings below 0.1 of an ohm exist, the test instrument can be outside of this requirement. This is because of the 2nd digit tolerance, which can vary between 4 and even 10 digits in some cases. For example; a meter reading of 0.05 ohm, measured with a meter whose tolerance is +/- 2% (+/-4 digits), could have a true value anywhere between 0.01 and 0.09 ohms. The reading would also not be consistent, if measured a number of times.Last edited by IQ Electrical; 14-01-2011 at 09:27 AM. Reason: Read the post properly!
- 14-01-2011 #5New to Electricians Forums
- Join Date
- Jan 2011
- Posts
- 5
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Ze Query
Thanks! Its TN-C-S, but whats causing me a headache is that Square "D" paper work says 0.18 max Zs, but i dont see how this is achievable without installing huge cabling!?!?!?!
YEs tansformer is in the adjacent room> taLast edited by planetman; 14-01-2011 at 09:28 AM.
- 14-01-2011 #6Appreciated Member


- Join Date
- Sep 2010
- Location
- cheshire/staffordshire
- Posts
- 25,843
- Thanks
- 647
- Thanked 3,573 Times in 3,298 Posts
Re: Ze Query
if i read the post correctly, it appears that you have an increase from0.17 to 0.44 on a 3meter run , this seems high. possibility of a high resistance connection? thinking about it, taking the reading at the squareD breaker, you have the resistance of the breaker itself adding to the result. this sounds like a more likely cause.
Last edited by telectrix; 14-01-2011 at 09:29 AM.
TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.
I don't suffer from Insanity. I enjoy every minute of it.
- 14-01-2011 #7
Re: Ze Query
- 14-01-2011 #8
- 14-01-2011 #9New to Electricians Forums
- Join Date
- Jan 2011
- Posts
- 5
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Ze Query
Sorry for the confusion. 0.17 is read at the incomer to the Section board which is 3m away from the transformer. Th 0.44 reading is taken from the D.B being fed from the section Board which is 200m away and is fed on a 95mm 4-core. Cheers
- 14-01-2011 #10New to Electricians Forums
- Join Date
- Jan 2011
- Posts
- 5
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: Ze Query
Just to add more! the 0.17 reading has been taken on the live side of the incoming supply off the tranny. So with 500m singles and the run being less than 3m it is basically the reading off the tranny.
Just thinking about it< if a TN-C-S is allowed to be 0.35, how could we possibly expect a Zs reading as low as 0.18????? as the Square D paper work suggests (very confused )
- 14-01-2011 #11Appreciated Member


- Join Date
- Sep 2010
- Location
- cheshire/staffordshire
- Posts
- 25,843
- Thanks
- 647
- Thanked 3,573 Times in 3,298 Posts
Re: Ze Query
beats me as well. if your Zeat origin were 0.35,a Zs of 0.18 would be impossible to achieve.
TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.
I don't suffer from Insanity. I enjoy every minute of it.
Similar Threads
-
generation meter query - display screen query
By loser123 in forum Photovoltaic / Solar Panels & Green Energy ForumReplies: 2Last Post: 02-05-2012, 09:50 AM -
TT Query?
By gottahugenoggin in forum Electrical Forum, General Electrical ForumReplies: 5Last Post: 03-02-2012, 07:00 PM -
PIR query
By bangtest in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 4Last Post: 25-09-2011, 10:30 PM -
pir query
By maveric50 in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 3Last Post: 11-10-2010, 11:02 AM -
using metrel test sheets query and testing query
By bobby101 in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 0Last Post: 22-09-2010, 05:27 PM -
R1+R2 query
By Scooter in forum Inspection, Testing and Certification of Electrical InstallationsReplies: 5Last Post: 02-06-2010, 08:45 PM -
Tax query
By keith915 in forum Business RelatedReplies: 1Last Post: 26-05-2010, 11:29 PM -
RCD query
By KevA in forum Electrical Forum, General Electrical ForumReplies: 2Last Post: 13-03-2010, 11:53 AM -
**** tt query ****
By Sav in forum Electrical Forum, General Electrical ForumReplies: 4Last Post: 07-02-2010, 07:12 PM



LinkBack URL
About LinkBacks

Reply With Quote















5 kitchen sockets from 1 FSU
7 Hours Ago in Electrical Wiring, Theories and Electrical Regulations