Discuss Does the following installation require a fused 13A switched spur. in the Electrical Wiring, Theories and Electrical Regulations at Electricians Forums Discussion Boards; Does the following installation require a fused 13A switched spur before the SWA. 2.5mm T&E from ground floor ring to IP rated box on outside wall. then SWA 2.5mm from ...- 02-02-2011 #1Electricians Arms Member
- Join Date
- Sep 2008
- Posts
- 380
- Thanks
- 22
- Thanked 1 Time in 1 Post
Does the following installation require a fused 13A switched spur.
Does the following installation require a fused 13A switched spur before the SWA.
2.5mm T&E from ground floor ring to IP rated box on outside wall.
then
SWA 2.5mm from Ground floor ring to garage unit (40A RCD) 16A MCB.
then
from the garage unit to two metal clad double socket outlets.
Thanks
Last edited by sivoodoo; 02-02-2011 at 05:40 PM.
- 02-02-2011 #2Electricians Forums Respected
- Join Date
- Oct 2009
- Location
- Castlegate, Prestbury
- Posts
- 4,684
- Thanks
- 588
- Thanked 372 Times in 345 Posts
Re: Does the following installation require a fused 13A switched spur.
Yes. Otherwise your spurring off with 16 amps
- 02-02-2011 #3
Yes as you are effectively spurring more than one point from the ring final.
Sent from my iPhone using Tapatalk.I'm an Electrician not a Magician.
- 02-02-2011 #4Electricians Arms Member
- Join Date
- Dec 2010
- Location
- London East
- Posts
- 4,810
- Thanks
- 64
- Thanked 835 Times in 733 Posts
Re: Does the following installation require a fused 13A switched spur.
Yes because you are spuring to two double sockets.
- 02-02-2011 #5Electricians Arms Member
- Join Date
- Sep 2008
- Posts
- 380
- Thanks
- 22
- Thanked 1 Time in 1 Post
Re: Does the following installation require a fused 13A switched spur.
If i was to change the 16A in the garage unit to a 10A would this meet regs?
- 02-02-2011 #6Electricians Arms Member
- Join Date
- Dec 2010
- Location
- London East
- Posts
- 4,810
- Thanks
- 64
- Thanked 835 Times in 733 Posts
Re: Does the following installation require a fused 13A switched spur.
The 16A MCB is irrelevant.
It's the two double sockets that are a problem.
Your options are:
Use a larger cable 4mm˛ or 6mm˛.
Use one double socket.
Make the spur an extension to the ring.
Use a 13A FCU.
- 02-02-2011 #7Electricians Arms Member

- Join Date
- Oct 2010
- Location
- Bucks
- Posts
- 434
- Thanks
- 31
- Thanked 39 Times in 38 Posts
Re: Does the following installation require a fused 13A switched spur.
Don't get me going about 4mm radials off a ring!
- 02-02-2011 #8Electricians Arms Member
- Join Date
- Sep 2008
- Posts
- 380
- Thanks
- 22
- Thanked 1 Time in 1 Post
Re: Does the following installation require a fused 13A switched spur.
Mmmm. sorry Im well confused??!!?
Why would a 10A mcb be irrelevant?
The two skt outlets would be protected by 10A instead of 13A??
Its been a long day sorry
- 02-02-2011 #9Electricians Arms Member
- Join Date
- Dec 2010
- Location
- London East
- Posts
- 4,810
- Thanks
- 64
- Thanked 835 Times in 733 Posts
Re: Does the following installation require a fused 13A switched spur.
Sorry yes, if the distance from the origin of the spur is less than 3m, then yes you could use the 10A MCB.
I was assuming the distance would be greater than 3m.Last edited by spinlondon; 02-02-2011 at 06:06 PM.
- 02-02-2011 #10Electricians Arms Member
- Join Date
- Sep 2008
- Posts
- 380
- Thanks
- 22
- Thanked 1 Time in 1 Post
Re: Does the following installation require a fused 13A switched spur.
It is about 8 meters. Does it make any difference that it is SWA 2.5mm Ref Method C.
??
I dont mind adding a 13A FCU next to the double socket at origin, just more mess for the customer.
I could even take out one of the metal clad skt outlets but its all been done in SWA and looks rather nice!
- 02-02-2011 #11Electricians Arms Member
- Join Date
- Oct 2010
- Location
- North West
- Posts
- 395
- Thanks
- 42
- Thanked 86 Times in 65 Posts
Re: Does the following installation require a fused 13A switched spur.
IMHO, as far as the spur from a spur issue is concerned, I think I would be hard pressed to find a regulation that says it can't be done. There are a few other issues that may be relevent.
1)The existing socket ring should already be RCD protected at 30mA. Adding another RCD would not provide any discrimination for that circuit.
2)If the use of metal clad sockets is an indicator that the garage is subject to external influences that would require more protection than a standard white outlet offers, then I would personally not want to suffer the potential inconvenience of the main board RCD tripping due to garage earth leakage.
3)The garage is presumably a detatched building and may require it's own earth system.
- 02-02-2011 #12Electricians Arms Member
- Join Date
- Dec 2010
- Location
- London East
- Posts
- 4,810
- Thanks
- 64
- Thanked 835 Times in 733 Posts
Re: Does the following installation require a fused 13A switched spur.
Where there is a reduction in current carrying capacity of a conductor, either because of reduced CSA or a change in installation methods, overcurrent protection should be provided within 3m of where the reduction occurs. This can be ommited if appropriate overcurrent protection is provided at the origin of the conductor.
You can omit overload protection if there is no likelyhood of overload occuring, and fault protection is provided at the origin of the conductor.
As such, if you beleive that there is no likelyhood of overload occuring due to the use of a 10A MCB, and the conductors are protected against fault current by the ring CPD, then yes you could use the 10A instead of the 16A MCB.
-
The Following User Says Thank You to spinlondon For This Useful Post:
sivoodoo (02-02-2011)
Similar Threads
-
Domestic Single Pole Fused Switched Spur?
By Ocelot7 in forum Electrical Forum, General Electrical ForumReplies: 24Last Post: 14-09-2012, 09:43 PM -
Domestic Main Switched Fused
By Fig in forum Electrical Forum, General Electrical ForumReplies: 10Last Post: 12-04-2012, 10:36 PM -
Domestic Fused spur (switched) in outside zone
By Ombos in forum Electrical Forum, General Electrical ForumReplies: 6Last Post: 02-11-2011, 06:55 PM -
anyone sell a switched fused timed spur?
By ExArmy in forum Electrical Forum, General Electrical ForumReplies: 8Last Post: 26-08-2011, 06:23 PM -
Fused switched socket
By rutterkyn in forum Electrical Forum, General Electrical ForumReplies: 2Last Post: 14-02-2011, 09:48 PM -
Switched Fused Spurs
By Jon Bridges in forum Electrical Forum, General Electrical ForumReplies: 8Last Post: 08-06-2010, 09:47 PM -
Switched fused spur
By kduck in forum Electrical Forum, General Electrical ForumReplies: 5Last Post: 05-12-2009, 04:42 PM -
fused spur off an unfused spur
By sivoodoo in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 3Last Post: 21-04-2009, 11:05 AM -
double switched fused spur ?
By TONY JONES in forum Electrical Forum, General Electrical ForumReplies: 0Last Post: 06-07-2008, 06:47 PM



1Likes
LinkBack URL
About LinkBacks

Reply With Quote


















230v 3 Phase Covertor Wiring
32 Minutes Ago in Electrical Forum, General Electrical Forum