Does the following installation require a fused 13A switched spur.

Discuss Does the following installation require a fused 13A switched spur. in the Electrical Wiring, Theories and Electrical Regulations at Electricians Forums Discussion Boards; Does the following installation require a fused 13A switched spur before the SWA. 2.5mm T&E from ground floor ring to IP rated box on outside wall. then SWA 2.5mm from ...
  1. #1
    Electricians Arms Member
    Join Date
    Sep 2008
    Posts
    380
    Thanks
    22
    Thanked 1 Time in 1 Post

    Default Does the following installation require a fused 13A switched spur.

    Does the following installation require a fused 13A switched spur before the SWA.

    2.5mm T&E from ground floor ring to IP rated box on outside wall.

    then

    SWA 2.5mm from Ground floor ring to garage unit (40A RCD) 16A MCB.

    then

    from the garage unit to two metal clad double socket outlets.

    Thanks

  2. Last edited by sivoodoo; 02-02-2011 at 05:40 PM.

  3. #2
    Electricians Forums Respected
    Join Date
    Oct 2009
    Location
    Castlegate, Prestbury
    Posts
    4,684
    Thanks
    588
    Thanked 372 Times in 345 Posts

    Default Re: Does the following installation require a fused 13A switched spur.

    Yes. Otherwise your spurring off with 16 amps


  4. #3
    Moderator



    Sintra's Avatar
    Join Date
    Aug 2009
    Location
    Belfast
    Posts
    6,770
    Thanks
    311
    Thanked 854 Times in 614 Posts

    Default

    Yes as you are effectively spurring more than one point from the ring final.


    Sent from my iPhone using Tapatalk.
    I'm an Electrician not a Magician.

  5. #4
    Electricians Arms Member spinlondon's Avatar
    Join Date
    Dec 2010
    Location
    London East
    Posts
    4,810
    Thanks
    64
    Thanked 835 Times in 733 Posts

    Default Re: Does the following installation require a fused 13A switched spur.

    Yes because you are spuring to two double sockets.

  6. #5
    Electricians Arms Member
    Join Date
    Sep 2008
    Posts
    380
    Thanks
    22
    Thanked 1 Time in 1 Post

    Default Re: Does the following installation require a fused 13A switched spur.

    If i was to change the 16A in the garage unit to a 10A would this meet regs?

  7. #6
    Electricians Arms Member spinlondon's Avatar
    Join Date
    Dec 2010
    Location
    London East
    Posts
    4,810
    Thanks
    64
    Thanked 835 Times in 733 Posts

    Default Re: Does the following installation require a fused 13A switched spur.

    The 16A MCB is irrelevant.
    It's the two double sockets that are a problem.
    Your options are:
    Use a larger cable 4mm˛ or 6mm˛.
    Use one double socket.
    Make the spur an extension to the ring.
    Use a 13A FCU.

  8. #7
    Electricians Arms Member
    jaresquire's Avatar
    Join Date
    Oct 2010
    Location
    Bucks
    Posts
    434
    Thanks
    31
    Thanked 39 Times in 38 Posts

    Default Re: Does the following installation require a fused 13A switched spur.

    Don't get me going about 4mm radials off a ring!
    sivoodoo likes this.

  9. #8
    Electricians Arms Member
    Join Date
    Sep 2008
    Posts
    380
    Thanks
    22
    Thanked 1 Time in 1 Post

    Default Re: Does the following installation require a fused 13A switched spur.

    Mmmm. sorry Im well confused??!!?

    Why would a 10A mcb be irrelevant?
    The two skt outlets would be protected by 10A instead of 13A??

    Its been a long day sorry

  10. #9
    Electricians Arms Member spinlondon's Avatar
    Join Date
    Dec 2010
    Location
    London East
    Posts
    4,810
    Thanks
    64
    Thanked 835 Times in 733 Posts

    Default Re: Does the following installation require a fused 13A switched spur.

    Sorry yes, if the distance from the origin of the spur is less than 3m, then yes you could use the 10A MCB.
    I was assuming the distance would be greater than 3m.
    Last edited by spinlondon; 02-02-2011 at 06:06 PM.

  11. #10
    Electricians Arms Member
    Join Date
    Sep 2008
    Posts
    380
    Thanks
    22
    Thanked 1 Time in 1 Post

    Default Re: Does the following installation require a fused 13A switched spur.

    It is about 8 meters. Does it make any difference that it is SWA 2.5mm Ref Method C.
    ??
    I dont mind adding a 13A FCU next to the double socket at origin, just more mess for the customer.

    I could even take out one of the metal clad skt outlets but its all been done in SWA and looks rather nice!

  12. #11
    Electricians Arms Member
    Join Date
    Oct 2010
    Location
    North West
    Posts
    395
    Thanks
    42
    Thanked 86 Times in 65 Posts

    Default Re: Does the following installation require a fused 13A switched spur.

    IMHO, as far as the spur from a spur issue is concerned, I think I would be hard pressed to find a regulation that says it can't be done. There are a few other issues that may be relevent.
    1)The existing socket ring should already be RCD protected at 30mA. Adding another RCD would not provide any discrimination for that circuit.

    2)If the use of metal clad sockets is an indicator that the garage is subject to external influences that would require more protection than a standard white outlet offers, then I would personally not want to suffer the potential inconvenience of the main board RCD tripping due to garage earth leakage.

    3)The garage is presumably a detatched building and may require it's own earth system.

  13. #12
    Electricians Arms Member spinlondon's Avatar
    Join Date
    Dec 2010
    Location
    London East
    Posts
    4,810
    Thanks
    64
    Thanked 835 Times in 733 Posts

    Default Re: Does the following installation require a fused 13A switched spur.

    Quote Originally Posted by sivoodoo View Post
    It is about 8 meters. Does it make any difference that it is SWA 2.5mm Ref Method C.
    ??
    I dont mind adding a 13A FCU next to the double socket at origin, just more mess for the customer.

    I could even take out one of the metal clad skt outlets but its all been done in SWA and looks rather nice!
    Where there is a reduction in current carrying capacity of a conductor, either because of reduced CSA or a change in installation methods, overcurrent protection should be provided within 3m of where the reduction occurs. This can be ommited if appropriate overcurrent protection is provided at the origin of the conductor.
    You can omit overload protection if there is no likelyhood of overload occuring, and fault protection is provided at the origin of the conductor.
    As such, if you beleive that there is no likelyhood of overload occuring due to the use of a 10A MCB, and the conductors are protected against fault current by the ring CPD, then yes you could use the 10A instead of the 16A MCB.

  14. The Following User Says Thank You to spinlondon For This Useful Post:

    sivoodoo (02-02-2011)

Similar Threads

  1. Domestic Single Pole Fused Switched Spur?
    By Ocelot7 in forum Electrical Forum, General Electrical Forum
    Replies: 24
    Last Post: 14-09-2012, 09:43 PM
  2. Domestic Main Switched Fused
    By Fig in forum Electrical Forum, General Electrical Forum
    Replies: 10
    Last Post: 12-04-2012, 10:36 PM
  3. Domestic Fused spur (switched) in outside zone
    By Ombos in forum Electrical Forum, General Electrical Forum
    Replies: 6
    Last Post: 02-11-2011, 06:55 PM
  4. anyone sell a switched fused timed spur?
    By ExArmy in forum Electrical Forum, General Electrical Forum
    Replies: 8
    Last Post: 26-08-2011, 06:23 PM
  5. Fused switched socket
    By rutterkyn in forum Electrical Forum, General Electrical Forum
    Replies: 2
    Last Post: 14-02-2011, 09:48 PM
  6. Switched Fused Spurs
    By Jon Bridges in forum Electrical Forum, General Electrical Forum
    Replies: 8
    Last Post: 08-06-2010, 09:47 PM
  7. Switched fused spur
    By kduck in forum Electrical Forum, General Electrical Forum
    Replies: 5
    Last Post: 05-12-2009, 04:42 PM
  8. fused spur off an unfused spur
    By sivoodoo in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 3
    Last Post: 21-04-2009, 11:05 AM
  9. double switched fused spur ?
    By TONY JONES in forum Electrical Forum, General Electrical Forum
    Replies: 0
    Last Post: 06-07-2008, 06:47 PM

Visitors found this page by searching for:

rules for installing a spur

installing a switched spur

mcb for 13a fuse spur

wiring 13a switched spur

13a spur install

fused spur to swa

how to install switched fused spur

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31