Electricians & Electrical Forum - RCD Tripped by Cooker Circuit (Update)
Like Tree10Likes

RCD Tripped by Cooker Circuit (Update)

Discuss RCD Tripped by Cooker Circuit (Update) in the Electrical Wiring, Theories and Electrical Regulations at Tilers Forum; Many thanks for the numerous thoughtful responses to my initial post. I think the threads have become too long for members to spend time following. So I am starting a ...
  1. #1
    Member
    Join Date
    Jun 2011
    Posts
    43
    Thanks
    0
    Thanked 3 Times
    in 3 Posts

    Default RCD Tripped by Cooker Circuit (Update)

    Many thanks for the numerous thoughtful responses to my initial post. I think the threads have become too long for members to spend time following. So I am starting a new thread here to recap the story deleting redundant info and updating in the light of comments received.
    # I will not bore members with an account of my professional qualifications/career etc. Please kindly accept that, although I am not a qualified electrician, I am technically proficient and accustomed to trouble-shooting problems - 95% of which can be solved for oneself by logic and a step-by-step procedure to eliminate possible causes. Regarding DIY - I know what I can comfortably handle myself and where to draw the line and get in a qualified professional. I would NEVER work on an electrical mains board (CU) and, in this instance, my "work" has only been to disconnect an oldcooker from the cable coming from the output side of a cooker switch and then connect a replacement. The "expertise" required for that is the same as fitting a plug - be sure not to interchange line and neutral, ensure the earth is OK and that the connections are tight. In investigating the problem all that I have done is open the cooker switch to check that the original connections are tight and visually inspected the Consumer Unit.
    # When I came to live in this bungalow 5 years ago I soon realized that the electrics were sub-standard - no proper earthing system for a start. So I employed a registered electrician to upgrade the installation - new CU with rdc - complete rewiring of the power circuits - new earthing system -etc. The work was done on a cost of materials + daily rate basis so he had no motivation to cut any corners or to skive as I was on site fulltime. On completion and testing he issued an NCEIC certificate - I attach a copy as it just might be useful. Working closely with him for about 5 days I was more than satisfied that he was very competent and trustworthy. (You may wonder why I have not called him back in on this problem but unfortunately he has meanwhile left the area.)
    # Fast forward 4 trouble-free years to the present day. I am going to renovate my kitchen. The existing old cooker was not up to much (but no electrical problems) and I decided on a new layout that allows me to incorporate a top-notch multi-function oven and touch-control ceramic hob thatI had bought new and used in France and brought over with me and stored. The old cooker was getting on my wick so I decided, in anticipation of the project, to get rid of it and temporarily locate the oven and hob in the same position (oven below countertop) which also gave the opportunity to check everything was working OK. In the new layout the oven will be mounted in a tower cabinet on another wall to the hob and requires a separate connection. For the interim arrangement I have used the one existing cooker switch/circuit and connected both units to it via a 40A junction box. And here begineth the problem……….

    # I have done a number of connections/disconnections/switchoperations/ etc solely as a trouble-shooting exercise - I do NOT, for example, normally use a cooker isolation switch to turn an oven on/off - turns the clock off just for a start.
    # Although not chronologically precise, this sequence of events describes what I have found:
    There was no rcd trip problem for the 4 yearsthat the old cooker was connected.
    I now disconnect the old cooker from the cable supplying it ex the cooker switch and connect the cable to a 40A junction box and from there connect the ceramic hob. Still no problem.
    I disconnect the ceramic hob from the junction box and connect the oven in its place. (The oven still has its own cable as wired in by the manufacturer). RCD problem immediately. (Irrelevant whether both units are connected to the jb as it only happens when the oven is connected).
    # These are thesymptoms:
    With the cooker switch "on" there is NEVER a trip when switching on the oven or during use.
    Occasionally, when the oven is turned off it trips the rcd so that the two power circuits go down but not the oven itself. (In my last test yesterday I got a trip about once per 10 switch-offs.
    With the oven "off" (better said in"standby mode") the cooker switch frequently trips the rcd irrespective of whether it is being switched "on" or "off". (In my last test yesterday I got a trip about 9 times out of 10). Ex: Both switches are "off" - Turn cooker switch "on" - rcd trips - Reset rcd - Turn oven "on" and carry on cooking without problem.
    # As requested, I am attaching some photos of the CU. At the risk of being corrected by the more knowledgeable, it looks 100% to me. Only the two power circuits are on the rcd side and the cooker cable (a bit hard to see at the back in the photos) has its neutral correctly connected to the non-rcd side of the neutral busbar.
    # My tuppenceworth is that the problem is not anywhere in the only 4-year old professionally installed CU/rcd/distribution wiring and lies somewhere in what has been recently connected to it. The hob is not guilty. Prime suspects - the oven and its cable. Unlikely to be the oven as it switches on and functions without problem. That leaves the cable and the mystery why an event emanating anywhere in the cooker circuit from its MCB to the oven should trip an rcd to which it is not connected.
  2. Attached Images Attached Images
    Last edited by charlhu; 12-06-2011 at 05:42 PM. Reason: typos from word.doc copy and paste

  3. The Following User Says Thank You to charlhu For This Useful Post:

    sparkinlee (12-06-2011)

  4. #2
    Member
    Murdoch's Avatar
    Join Date
    Aug 2010
    Location
    Woking
    Posts
    11,901
    Thanks
    539
    Thanked 986 Times
    in 921 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    Wonder why the installer didn't complete the R1 + R2 or the R2 column on the schedule of tests/inspections? And other boxes on the cert?
  5. Last edited by Murdoch; 12-06-2011 at 05:42 PM.

  6. #3
    Member

    Join Date
    Oct 2009
    Location
    south uk
    Posts
    3,526
    Thanks
    357
    Thanked 508 Times
    in 418 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    Try carrying out an IR test on all circuits.

  7. #4
    Member
    Join Date
    Mar 2011
    Location
    Merseyside
    Posts
    1,487
    Thanks
    66
    Thanked 157 Times
    in 145 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    Quote Originally Posted by Murdoch View Post
    Wonder why the installer didn't complete the R1 + R2 or the R2 column on the schedule of tests/inspections? And other boxes on the cert?

    Very odd

  8. #5
    Electricians Arms Member

    Join Date
    May 2008
    Location
    home
    Posts
    5,886
    Thanks
    406
    Thanked 867 Times
    in 660 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    quote
    I am attaching some photos of the CU. At therisk of being corrected by the more knowledgeable, it looks 100% to me

    I
    am not normally one for making judgement of others standards,but only posting in order to question your perspective of a 100% effort

    That would not be a winner in a "How to fit a consumer unit" contest
    I am sorry to say,it would be hard pushed to "qualify" as a contestant
    nikmet likes this.

  9. #6
    Member

    Join Date
    Oct 2009
    Location
    south uk
    Posts
    3,526
    Thanks
    357
    Thanked 508 Times
    in 418 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    Quote Originally Posted by Murdoch View Post
    Wonder why the installer didn't complete the R1 + R2 or the R2 column on the schedule of tests/inspections? And other boxes on the cert?
    Wonder where he got 6.0mm with a 4.0mm cpc as well.

  10. #7
    Member
    Murdoch's Avatar
    Join Date
    Aug 2010
    Location
    Woking
    Posts
    11,901
    Thanks
    539
    Thanked 986 Times
    in 921 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    If the cooker IS tripping the RCD and its DEFINITELY not on the RCD side of the board I'd looking for a neutral connection from the cooker circuit to one of the rings.

    Could be a challange to locate the issue but rewarding when its sorted (and maybe expensive for you)!

  11. #8
    Member
    Join Date
    Jun 2011
    Posts
    43
    Thanks
    0
    Thanked 3 Times
    in 3 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    Quote Originally Posted by Murdoch View Post
    Wonder why the installer didn't complete the R1 + R2 or the R2 column on the schedule of tests/inspections? And other boxes on the cert?
    Has that any bearing on the problem which has come up now?

  12. #9
    Member
    Join Date
    Jun 2011
    Posts
    43
    Thanks
    0
    Thanked 3 Times
    in 3 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    Quote Originally Posted by wirepuller View Post
    Wonder where he got 6.0mm with a 4.0mm cpc as well.
    Has that any bearing on the problem which has come up now?

  13. #10
    Member
    Murdoch's Avatar
    Join Date
    Aug 2010
    Location
    Woking
    Posts
    11,901
    Thanks
    539
    Thanked 986 Times
    in 921 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    Quote Originally Posted by charlhu View Post
    Has that any bearing on the problem which has come up now?
    IMHO no, just a sign of somebody cutting corners.

    Bet he/she won't be too pleased to see you've posted his details online...... however it may just act as an example of what customers should expect to see on the reports they are given.

  14. #11
    Guest123
    Guest

    Default Re: RCD Tripped by Cooker Circuit (Update)

    I'm sorry I missed the other thread, but from what I gather here the new cooker is tripping the RCD......the cooker circuit is not protected by the RCD though......

  15. #12
    Member
    Join Date
    Jun 2011
    Posts
    43
    Thanks
    0
    Thanked 3 Times
    in 3 Posts

    Default Re: RCD Tripped by Cooker Circuit (Update)

    Quote Originally Posted by Des 56 View Post
    quote
    I am attaching some photos of the CU. At therisk of being corrected by the more knowledgeable, it looks 100% to me

    I
    am not normally one for making judgement of others standards,but only posting in order to question your perspective of a 100% effort

    That would not be a winner in a "How to fit a consumer unit" contest
    I am sorry to say,it would be hard pushed to "qualify" as a contestant
    Well, as I anticipated, lead with your chin and ...........!
    I suppose, at the end of the day, I was satisfied that everything was working and continued to do so until I got into the business of swapping cooking units.

Page 1 of 3 123 LastLast

Similar Threads

  1. dimmer circuit on cooker circuit.
    By thekingiam in forum Electrical Forum: General Electrical Forum
    Replies: 5
    Last Post: 21-03-2013, 03:56 PM
  2. getting 0M ohms L- N on Lighting Circuit and cooker Circuit...
    By iwantmyNVQ in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 22
    Last Post: 13-07-2012, 08:09 PM
  3. 32 Amp Cooker Circuit 13 Amp Cooker
    By firewalshy in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 10
    Last Post: 14-03-2012, 04:04 PM
  4. Cooker circuit
    By stu-rob in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 10
    Last Post: 10-09-2010, 08:12 AM
  5. cooker circuit
    By ijbswfc in forum Electrical Forum: General Electrical Forum
    Replies: 3
    Last Post: 07-06-2009, 08:22 PM

Visitors found this page by searching for:

cooker circuit tripping rcd

does cooker need rcd

cooker not working after tripping rcd

cooker cable discnnected from cooker

upgrading cooker rcd

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35