Page 1 of 2 12 LastLast
Results 1 to 15 of 21
Electricians & Electrical Forum - Metallic pipe with push fittings
Like Tree4Likes

Metallic pipe with push fittings

Discuss Metallic pipe with push fittings at Electricians Forums; If a metallic pipe work has push fit type fittings that dont provide electrical continuity what should be done A=Leave it as it is B=Increase the pipe size C=Bridge with ...
  1. #1
    Member
    Join Date
    Jun 2011
    Location
    Cambridge
    Posts
    34
    Thanks
    3
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Metallic pipe with push fittings

    If a metallic pipe work has push fit type fittings that dont provide electrical continuity what should be done

    A=Leave it as it is
    B=Increase the pipe size
    C=Bridge with a brown bonding conductor
    D=Bridge with a G/Y bonding conductor

    I was thinking A ?
    Thanks

    Last one then i can get my self in the workshop and try to put into practise what i have learnt in the past two months of studying.
    just one step closer to never picking up a paint brush again.

  2. #2
    Electricians Arms Member

    Join Date
    Oct 2009
    Location
    south uk
    Posts
    4,224
    Thanks
    388
    Thanked 569 Times
    in 473 Posts
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    There is insufficient information given to provide an answer.

  3. #3
    JUD
    JUD is offline
    Electricians Arms Member JUD's Avatar
    Join Date
    Jul 2009
    Location
    East Yorkshire
    Posts
    1,259
    Thanks
    33
    Thanked 192 Times
    in 151 Posts
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    I'd go with D

  4. #4
    Member
    Join Date
    Jun 2011
    Location
    Cambridge
    Posts
    34
    Thanks
    3
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    Quote Originally Posted by wirepuller View Post
    There is insufficient information given to provide an answer.
    Thats word for word what the TMA question reads.

    I did wonder what material the push fittings where made from but as it says dont provide electrical continuity i guessed the fitting must be of plastic.
    I dont no maybe im talking rubbish.

  5. #5
    Member
    Join Date
    Jun 2011
    Location
    Cambridge
    Posts
    34
    Thanks
    3
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    Quote Originally Posted by JUD View Post
    I'd go with D
    That was my second guess as if the matallic pipe did need bonding then at least its done by answer D.
    Last edited by Virtualcom13at; 23-06-2011 at 10:51 PM.

  6. #6
    Moderator


    Paul.M's Avatar
    Join Date
    Aug 2010
    Location
    In a Toolbox
    Posts
    9,527
    Thanks
    2,001
    Thanked 1,340 Times
    in 1,096 Posts
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    I'd agree with Jud as well. The reason being is that any fault current finding the water pipes would not be carried away (and therefore not tripping the mcb/fuse/rcd) and not finding earth (MET) at the cu hence the need to bridge the plastic push fit. An experiment was carried out in a Chris Kitcher testing book. He had two short pieces of copper pipe with a push fit connecting them, filled the pipe with water and put 230V on one end and tested the other end. Results showed only 3mA (0.003A) was conducted through the water. Just so you know why we bridge plastic push fittings. Any more questions, I can answer these whilst Telectrix is on another thread
    Last edited by Paul.M; 23-06-2011 at 11:23 PM.
    telectrix and Virtualcom13at like this.
    I do not have the energy nor the intellect to be able to write a signature!



  7. #7
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    42,148
    Thanks
    970
    Thanked 5,194 Times
    in 4,843 Posts
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    have to agree with jud and paul m on what the answer would be, but wirepuller is correct as the question does not stipulate whether or not the pipework is extraneous. so the question as it stands is unanswerable.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  8. #8
    Electricians Arms Member
    i=p/u's Avatar
    Join Date
    Dec 2010
    Location
    n.ireland/ Scotland
    Posts
    6,650
    Thanks
    377
    Thanked 280 Times
    in 275 Posts
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    id kick a fuss in the shop and say i wanted metal ones

  9. #9
    Member
    Join Date
    Jun 2011
    Location
    Cambridge
    Posts
    34
    Thanks
    3
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    Cheers guys
    Glad i found this forum

  10. #10
    Member
    Join Date
    Jun 2011
    Location
    Cambridge
    Posts
    34
    Thanks
    3
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    Quote Originally Posted by i=p/u View Post
    id kick a fuss in the shop and say i wanted metal ones
    Thats plumbers going for the easy option. he he

  11. #11
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    42,148
    Thanks
    970
    Thanked 5,194 Times
    in 4,843 Posts
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    Quote Originally Posted by Virtualcom13at View Post
    Cheers guys
    Glad i found this forum
    you won't be after a few weeks
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  12. #12
    Electricians Arms Member
    IQ Electrical's Avatar
    Join Date
    Oct 2010
    Posts
    4,578
    Thanks
    88
    Thanked 1,198 Times
    in 883 Posts
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    Unless the pipe is being used AS the bonding conductor, why would you wish to assist the distribution of fault voltages onto sections of pipework which because of the high resistance of water are, in effect, isolated sections?Wirepuller is right, the question as it stands can't be answered but I'll bet Mr Kitcher isn't advocating linking across push joints on pipework that isn't being used as the actual bonding conductor.
    Paul.M likes this.

  13. #13
    Moderator


    Paul.M's Avatar
    Join Date
    Aug 2010
    Location
    In a Toolbox
    Posts
    9,527
    Thanks
    2,001
    Thanked 1,340 Times
    in 1,096 Posts
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    I'm afraid Mr Kitcher does and has a nice photo in his book of him doing it. It's things like this that confuse people. I know there's a few mistakes in his books but these are what people use to pass tricky exams.
    I do not have the energy nor the intellect to be able to write a signature!



  14. #14
    Member
    Join Date
    Jun 2011
    Location
    Cambridge
    Posts
    34
    Thanks
    3
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    Who is this mr Kitcher he sounds like a man who knows. whats his book called??? as im going to be studying this possibly for the next two years and then working and learning for the rest of my working life i might as well get more books to add to my collection.

  15. #15
    Electricians Arms Member
    IQ Electrical's Avatar
    Join Date
    Oct 2010
    Posts
    4,578
    Thanks
    88
    Thanked 1,198 Times
    in 883 Posts
    Tagged
    0 Thread(s)

    Default Re: Metallic pipe with push fittings

    Quote Originally Posted by paul.m View Post
    I'm afraid Mr Kitcher does and has a nice photo in his book of him doing it. It's things like this that confuse people. I know there's a few mistakes in his books but these are what people use to pass tricky exams.
    I remember seeing the picture but again, I'm certain that this will be where the pipe IS the bonding conductor, check it out if you can Paul, I'll not be able to see the book until Monday.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Bonding metallic pipework
    By adammid in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 20
    Last Post: 27-12-2012, 05:01 PM
  2. plastic pipe fittings
    By redface in forum Electrical Forum: General Electrical Forum
    Replies: 5
    Last Post: 25-06-2011, 09:26 AM
  3. plastic pipe fittings
    By redface in forum Electrical Forum: General Electrical Forum
    Replies: 2
    Last Post: 24-06-2011, 09:53 PM
  4. Metallic Conduit Installation
    By bluesky in forum Electrical Forum: General Electrical Forum
    Replies: 1
    Last Post: 19-02-2011, 11:51 AM
  5. Push fit-type fittings
    By J4EY in forum Electrical Forum: General Electrical Forum
    Replies: 8
    Last Post: 06-01-2011, 10:16 PM

Visitors found this page by searching for:

push fit galv conduit site:www.electriciansforums.co.uk

How to use push fit metal conduit

does a water pipe provide electrical earth continuity

Electrical conductord

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.