weird lighting fault

Discuss weird lighting fault in the Electrical Wiring, Theories and Electrical Regulations at Tilers Forum; Hi folks while testing this theatre, i attempted to get a Zs from an emergency exit sign. The steel conduit is being used as cpc. when i connect my three ...
  1. #1
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default weird lighting fault

    Hi folks
    while testing this theatre, i attempted to get a Zs from an emergency exit sign. The steel conduit is being used as cpc.
    when i connect my three probes to l,n,earth i'm getting 110v on the screen and when i press test it comes up with about 160 ohms.
    i put a voltmeter across and found 110v between L and E but 230v between L and N.
    could this be a poor connection on the steel conduit cpc and if so, why does the voltage drop to approx 110v

    thanks...its a bit of a puzzle

  2. #2
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    40,251
    Thanks
    937
    Thanked 4,982 Times
    in 4,645 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    do a R2 test on the conduit end to end. then test to MET.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  3. #3
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    from the board to the fitting is about 300 metres...

  4. #4
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    40,251
    Thanks
    937
    Thanked 4,982 Times
    in 4,645 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    even if it's 3000m you've got to get it right, one way or another. do it in stages with a wander lead.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  5. #5
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    that will be fun, all the conduit is buried in walls and in ceilings to which there is no access. Thanks

  6. #6
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    assuming it is a bad earth, can someone please explain the science behind it...how does it become 110v???

  7. #7
    Electricians Arms Member
    Join Date
    May 2009
    Posts
    882
    Thanks
    21
    Thanked 40 Times
    in 35 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    sounds like a break in the conduit to the fitting, just code 1 it, and recommend rcbo

  8. #8
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    40,251
    Thanks
    937
    Thanked 4,982 Times
    in 4,645 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    code 1 it and FIX it. you don't put a band- aid on an arterial bleed.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  9. #9
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    thanks. the conduit is 35 years old!
    just dont understand why its 110v

  10. #10
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    i will....i just want to get my head round the reason as to why the voltage drops to 110v

  11. #11
    Electricians Arms Member
    Join Date
    May 2009
    Posts
    882
    Thanks
    21
    Thanked 40 Times
    in 35 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    probably getting a reading through the damp walls, and forgot to mention, you should not walk away from a code 1, without isolating or rectifying.

  12. #12
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    40,251
    Thanks
    937
    Thanked 4,982 Times
    in 4,645 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    floating earth?
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  13. #13
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    i'd be there forever and a day if i rectified all 76 code 1s that ive found so far!!!

  14. #14
    Electricians Arms Member
    Join Date
    May 2009
    Posts
    882
    Thanks
    21
    Thanked 40 Times
    in 35 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    There should be an agreement of what to do, as you find the code 1's

  15. #15
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    40,251
    Thanks
    937
    Thanked 4,982 Times
    in 4,645 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    only 76, must have been done on a good day.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  16. #16
    Electricians Arms Member mogga's Avatar
    Join Date
    Apr 2010
    Location
    Kirkintilloch by the canal
    Posts
    3,773
    Thanks
    82
    Thanked 380 Times
    in 333 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    FFS I realy hope you have a contract saying code 1s to be repaired

  17. #17
    Member
    Join Date
    Jun 2009
    Location
    St Helens Lancs
    Posts
    149
    Thanks
    2
    Thanked 21 Times
    in 20 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    I assume you are doing a PIR ?
    Conduit as CPC 35 years old
    76 code 1's so far I guess the recommendation is a full re-wire
    As for 110V L-E try testing much closer to the main DB
    I guess the conduit is badly corroded at various points and is a very high resistance compared to L-N insulated copper conductors

  18. #18
    Electricians Arms Member
    Join Date
    Dec 2010
    Location
    Manchester
    Posts
    232
    Thanks
    25
    Thanked 74 Times
    in 50 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    Quote Originally Posted by Dean Williams View Post
    assuming it is a bad earth, can someone please explain the science behind it...how does it become 110v???
    If you've got good Zs figures elsewhere you can rule out the earthing conductor itself.
    So if we're dealing with a fault on just this one conduit run, here goes:

    Let's assume:
    The conduit is completely open circuit quite near the origin.
    The insulation resistance L-E is 0.5Meg and N-E is 0.5 Meg. (measured at end of circuit)
    Voltmeter input impedance is 10Meg.

    Think of a potential divider, L to N, with the conduit in the middle
    For a 230V supply, you'd get a theoretical 115V
    But with the 10 Meg of your voltmeter in parallel with whichever 0.5Meg you were measuring across, the voltage seen would reduce slightly.

    Now if you've got a measured Zs of 160 Ohm and 110V L-E, sounds like something is corroded AND full of water

    Unless someone's made up an IT system, centre tap earthed through an impedance....

    Simon.

  19. #19
    Member
    Join Date
    Aug 2010
    Posts
    14,206
    Thanks
    727
    Thanked 1,489 Times
    in 1,172 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    Try using an old analogue meter and then check the voltage. I hate DVM’s give me an AVO any time!
    Des 56, cbw and telectrix like this.

  20. #20
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    Thanks for the explanation...i understand it more now.

    I'll try it with an analogue voltmeter tomorrow. Thanks

  21. #21
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    40,251
    Thanks
    937
    Thanked 4,982 Times
    in 4,645 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    Quote Originally Posted by Tony View Post
    Try using an old analogue meter and then check the voltage. I hate DVM’s give me an AVO any time!
    one like this? i've got 2 of them

    140.jpg
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  22. #22
    Electricians Arms Member

    Join Date
    May 2008
    Location
    EU
    Posts
    6,159
    Thanks
    419
    Thanked 891 Times
    in 681 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    An Electrician and his Avometer
    It was at one time, like the Lone ranger and his trusted horse Trigger , couldn't get anywhere without the other


    Sadly my own passed away quite a few years ago,stolen it was,sob,I still miss her though,sob

    That picture has an uncanny resemblence to mine,where did you happen upon it tel
    Guest5000 likes this.

  23. #23
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    40,251
    Thanks
    937
    Thanked 4,982 Times
    in 4,645 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    that particular one is at present on ebay. there's a few on. ranging from a few quid upwards. my 2 aran older model 8 ans a 7.

    edit: marston's pedigree is affecting my shpellinge
    Last edited by telectrix; 14-09-2011 at 07:49 PM.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  24. The Following User Says Thank You to telectrix For This Useful Post:

    Des 56 (14-09-2011)

  25. #24
    Member
    Join Date
    Sep 2011
    Posts
    5
    Thanks
    2
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    Check your meter, Ive had allsorts of strange voltages.
    Once had 382v on what should have been a 230 circuit just because the batteries running flat.

  26. #25
    Member
    Join Date
    Aug 2010
    Posts
    14,206
    Thanks
    727
    Thanked 1,489 Times
    in 1,172 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    Mine was a model 8 mk 3 complete with 200A shunt and 5KV Aux transformer, I was gutted when the kit was nicked.

    Both the add on bits were from about the 50’s, beautiful varnished teak cases. Bloody death traps, but impressive when you got them out of their leather cases. Never had the bottle to use the transformer above 1.5KV even though I bench tested it to 5KV DC to earth and between windings. I might be daft, I’m not suicidal!

  27. #26
    Member
    Join Date
    Aug 2010
    Posts
    14,206
    Thanks
    727
    Thanked 1,489 Times
    in 1,172 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    Quote Originally Posted by Dean Williams View Post
    Thanks for the explanation...i understand it more now.

    I'll try it with an analogue voltmeter tomorrow. Thanks
    Let us know how you go on please

  28. #27
    Electricians Arms Member
    Join Date
    Aug 2009
    Posts
    125
    Thanks
    0
    Thanked 11 Times
    in 11 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    Another thought, seeing as its an emergency light in a theatre, there is not a sort of central battery system supplying it is there??? this used to be used a lot for cinemas,theatres etc and would account for the 110V being so perfect on your meter.

    Just an idea to throw into the pot

    Nick

  29. #28
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    Hi
    there's no central battery unit. its a dedicated DB just for em lights.
    i've been told to Code 1 it as possible bad earth and that a different company will carry out the fault finding/repairs.
    by the way ive finished testing the theatre now. total of 94 DBs, 643 section F observations including 93 code 1s.

  30. #29
    Member
    Join Date
    Jun 2011
    Posts
    172
    Thanks
    1
    Thanked 9 Times
    in 8 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    could it be a lose/missing neutral?

  31. #30
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    no because there's 230v across l and n

Page 1 of 2 12 LastLast
Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Continuity on lighting circuit - weird results?
    By ray-bentos in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 10
    Last Post: 25-01-2014, 12:42 AM
  2. Domestic Weird Transformer Fault
    By AndrewMgan1976 in forum Electrical Forum: General Electrical Forum
    Replies: 7
    Last Post: 03-07-2013, 09:03 PM
  3. High Freq Ballast Lighting gone weird
    By Capn Ahab in forum Electrical Forum: General Electrical Forum
    Replies: 9
    Last Post: 24-10-2012, 06:44 PM
  4. Commercial weird problem on lighting in commercial offices.... HELP!
    By piperm in forum Electrical Forum: General Electrical Forum
    Replies: 9
    Last Post: 13-04-2010, 09:54 PM
  5. weird fault
    By ian in forum Electrical Forum: General Electrical Forum
    Replies: 7
    Last Post: 12-11-2008, 09:07 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36