    Default weird lighting fault

    Hi folks
    while testing this theatre, i attempted to get a Zs from an emergency exit sign. The steel conduit is being used as cpc.
    when i connect my three probes to l,n,earth i'm getting 110v on the screen and when i press test it comes up with about 160 ohms.
    i put a voltmeter across and found 110v between L and E but 230v between L and N.
    could this be a poor connection on the steel conduit cpc and if so, why does the voltage drop to approx 110v

    thanks...its a bit of a puzzle

  2. #2
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    42,149
    Thanks
    970
    Thanked 5,194 Times
    in 4,843 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    do a R2 test on the conduit end to end. then test to MET.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  3. #3
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    from the board to the fitting is about 300 metres...

  4. #4
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    42,149
    Thanks
    970
    Thanked 5,194 Times
    in 4,843 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    even if it's 3000m you've got to get it right, one way or another. do it in stages with a wander lead.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  5. #5
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    that will be fun, all the conduit is buried in walls and in ceilings to which there is no access. Thanks

  6. #6
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    assuming it is a bad earth, can someone please explain the science behind it...how does it become 110v???

  7. #7
    Electricians Arms Member
    Join Date
    May 2009
    Posts
    883
    Thanks
    21
    Thanked 43 Times
    in 38 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    sounds like a break in the conduit to the fitting, just code 1 it, and recommend rcbo

  8. #8
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    42,149
    Thanks
    970
    Thanked 5,194 Times
    in 4,843 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    code 1 it and FIX it. you don't put a band- aid on an arterial bleed.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  9. #9
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    thanks. the conduit is 35 years old!
    just dont understand why its 110v

  10. #10
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    i will....i just want to get my head round the reason as to why the voltage drops to 110v

  11. #11
    Electricians Arms Member
    Join Date
    May 2009
    Posts
    883
    Thanks
    21
    Thanked 43 Times
    in 38 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    probably getting a reading through the damp walls, and forgot to mention, you should not walk away from a code 1, without isolating or rectifying.

  12. #12
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    42,149
    Thanks
    970
    Thanked 5,194 Times
    in 4,843 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    floating earth?
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


  13. #13
    Electricians Arms Member Dean Williams's Avatar
    Join Date
    Nov 2010
    Location
    shotton, flintshire
    Posts
    377
    Thanks
    9
    Thanked 18 Times
    in 18 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    i'd be there forever and a day if i rectified all 76 code 1s that ive found so far!!!

  14. #14
    Electricians Arms Member
    Join Date
    May 2009
    Posts
    883
    Thanks
    21
    Thanked 43 Times
    in 38 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    There should be an agreement of what to do, as you find the code 1's

  15. #15
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    42,149
    Thanks
    970
    Thanked 5,194 Times
    in 4,843 Posts
    Tagged
    0 Thread(s)

    Default Re: weird lighting fault

    only 76, must have been done on a good day.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    Plumbers were put on this Earth for a reason...... so that evolution could start again from scratch.


Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Continuity on lighting circuit - weird results?
    By ray-bentos in forum Inspection, Testing and Certification of Electrical Installations
    Replies: 10
    Last Post: 25-01-2014, 01:42 AM
  2. Domestic Weird Transformer Fault
    By AndrewMgan1976 in forum Electrical Forum: General Electrical Forum
    Replies: 7
    Last Post: 03-07-2013, 09:03 PM
  3. High Freq Ballast Lighting gone weird
    By Capn Ahab in forum Electrical Forum: General Electrical Forum
    Replies: 9
    Last Post: 24-10-2012, 06:44 PM
  4. Commercial weird problem on lighting in commercial offices.... HELP!
    By piperm in forum Electrical Forum: General Electrical Forum
    Replies: 9
    Last Post: 13-04-2010, 09:54 PM
  5. weird fault
    By ian in forum Electrical Forum: General Electrical Forum
    Replies: 7
    Last Post: 12-11-2008, 10:07 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.