Is this practicable?
Discuss Is this practicable? in the Electrical Wiring, Theories and Electrical Regulations at Electricians Forums Discussion Boards; Is the following scenario practicable and does it meet regulations? A garage consumer unit with two 32A MCBs and one 63A/30maRCD main switch supplies two ring mains in 2.5mm T&E ...- 17-02-2009 #1Electricians Arms Member
- Join Date
- Sep 2008
- Posts
- 380
- Thanks
- 22
- Thanked 1 Time in 1 Post
Is this practicable?
Is the following scenario practicable and does it meet regulations?
A garage consumer unit with two 32A MCBs and one 63A/30maRCD main switch supplies two ring mains in 2.5mm T&E fom each 32A MCB.
This garage unit is fed from a 45A minitrip mcb in an old wylex board using 4mm T&E. (Distance from garrage unit is 300mm)
The main supply is PME
Each ring serves 6 twin socket outlets.
Your thoughts please
Simon.
- 17-02-2009 #2Appreciated on Electricians Forums
- Join Date
- Dec 2008
- Posts
- 12,661
- Thanks
- 631
- Thanked 2,369 Times in 1,453 Posts
Re: Is this practicable?
Hey there.
4mm on 45A doesn't sit right with me.
- 17-02-2009 #3Electricians Arms Member
- Join Date
- Sep 2008
- Posts
- 380
- Thanks
- 22
- Thanked 1 Time in 1 Post
Re: Is this practicable?
Yup! So if I fed the garage unit with 10mm that would meet requirements,
or I could just split the tails and Henley block.
- 17-02-2009 #4Appreciated on Electricians Forums
- Join Date
- Dec 2008
- Posts
- 12,661
- Thanks
- 631
- Thanked 2,369 Times in 1,453 Posts
Re: Is this practicable?
Hey.
Splitting the tails with henleys is best IMO. You can use a larger earthing conductor also, i.e 16mm tails and 10mm earth, as opposed to 10mm T+E with 4mm earth.
Cheers
- 17-02-2009 #5Electricians Arms Member
- Join Date
- Sep 2008
- Posts
- 380
- Thanks
- 22
- Thanked 1 Time in 1 Post
Re: Is this practicable?
Cheers Lenny, I shall go for that, so everyrhing else seems ok to you?
- 17-02-2009 #6Appreciated on Electricians Forums
- Join Date
- Dec 2008
- Posts
- 12,661
- Thanks
- 631
- Thanked 2,369 Times in 1,453 Posts
Re: Is this practicable?
Yeah, seems fine.