    Question Minimum degree of IP code protection to be afforded by....

    A. Front surface of distribution board

    B. Horizontal top surface of motor starter which is accessible

    C. Front surface of a conduit box containing live terminals


    I have had this question in one of my mock exams yesterday in my 2391 inspection and testing courses and I am not sure for the A and B answers:

    My trainer says that it's A. IP4X, B. IP4X, C. IP4X

    And I think it's: A. IP2X, B. IP4X, C. IP2X

    Please help, I need someone to shed some light here! So confused

    Thanks
    Last edited by gman67; 01-10-2011 at 12:39 AM.

  2. #2
    Electricians Arms Member
    IQ Electrical's Avatar
    Join Date
    Oct 2010
    Posts
    4,578
    Thanks
    88
    Thanked 1,198 Times
    in 883 Posts
    Tagged
    0 Thread(s)

    Default Re: Minimum degree of IP code protection to be afforded by....

    Sack your trainer and try his seat out for size, you're bang on.

  3. #3
    Electricians Arms Member MarkieSparkie's Avatar
    Join Date
    Feb 2011
    Location
    Weymouth
    Posts
    5,109
    Thanks
    45
    Thanked 1,106 Times
    in 853 Posts
    Tagged
    0 Thread(s)

    Default Re: Minimum degree of IP code protection to be afforded by....

    Seconded, you are correct and trainer is wrong.

  4. #4
    Electricians Arms Member
    malcolmsanford's Avatar
    Join Date
    Jul 2010
    Location
    Kent working back out there yet again
    Posts
    7,331
    Thanks
    792
    Thanked 1,674 Times
    in 1,400 Posts
    Tagged
    0 Thread(s)

    Default Re: Minimum degree of IP code protection to be afforded by....

    Point your instructor to reg section 416.2 for barriers and enclosures.

  5. #5
    Member
    Join Date
    May 2010
    Location
    Exmoor
    Posts
    794
    Thanks
    53
    Thanked 110 Times
    in 97 Posts
    Tagged
    0 Thread(s)

    Default Re: Minimum degree of IP code protection to be afforded by....

    Do his knuckles drag along the floor?

  6. #6
    Electricians Arms Member
    Richard Burns's Avatar
    Join Date
    Feb 2011
    Location
    Cambridgeshire
    Posts
    7,042
    Thanks
    655
    Thanked 1,515 Times
    in 1,371 Posts
    Tagged
    0 Thread(s)

    Default Re: Minimum degree of IP code protection to be afforded by....

    Yes you are right: horizontal accessible IP4X, vertical IP2X

  7. #7
    Member
    Join Date
    Sep 2010
    Posts
    31
    Thanks
    9
    Thanked 1 Time in 1 Post
    Tagged
    0 Thread(s)

    Default Re: Minimum degree of IP code protection to be afforded by....

    Thanks guys, it's all clear in my head now. The trainer has actually admitted he was wrong today!
    Richard Burns likes this.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. Degree of Protection
    By tbs1983 in forum Electrical Forum: General Electrical Forum
    Replies: 17
    Last Post: 07-03-2014, 09:40 PM
  2. -10 degree c
    By Baker1988 in forum Chit Chat - Off Topic
    Replies: 17
    Last Post: 18-01-2013, 02:57 AM
  3. EICR code, commercial socket protection
    By Welchyboy in forum Electrical Forum: General Electrical Forum
    Replies: 17
    Last Post: 15-05-2012, 07:52 AM
  4. degree
    By cmtate in forum Electrical Courses & Electrical NVQ's
    Replies: 2
    Last Post: 11-03-2009, 10:46 PM
  5. Minimum impedance protection & voltage balance protection
    By speedtronic in forum Electrical Forum: General Electrical Forum
    Replies: 1
    Last Post: 30-12-2008, 05:58 PM

Visitors found this page by searching for:

uk electrical ip codes

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.