Page 1 of 2 12 LastLast
Results 1 to 15 of 23
Electricians & Electrical Forum - 63A supply required for flat any thoughts on
Like Tree1Likes

63A supply required for flat any thoughts on

Discuss 63A supply required for flat any thoughts on at Electricians Forums; Hi We have to install a 63A supply to a new consumer unit on a 2nd floor studio flat. The supply at present looks like it may have to feed ...
  1. #1
    Member
    Join Date
    Mar 2009
    Location
    Bristol
    Posts
    121
    Thanks
    3
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default 63A supply required for flat any thoughts on

    Hi

    We have to install a 63A supply to a new consumer unit on a 2nd floor studio flat. The supply at present looks like it may have to feed from the switch on ground floor outside the property and up the wall before re-entering the 2nd floor studio flat.

    Any thoughts how best to go about this.

    SAW cable or trunking with 2 core and seprate earth. some advise and thoughts on this would be good.

    Cheers

  2. #2
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    43,061
    Thanks
    984
    Thanked 5,282 Times
    in 4,930 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    SWA for me.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    It is a wise man who ignores the advice of fools, and a fool who ignores the advice of wise men


  3. #3
    Member
    Join Date
    Mar 2009
    Location
    Bristol
    Posts
    121
    Thanks
    3
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    We were thinking 16mm 2 core SWA, use the armoured for cpc, clip it all up the side of the building.

    The only thing is what about the standard consumer units, they not really designed for swa as they are plastic. Any thoughts on termination into the D/B.

  4. #4
    Electricians Arms Member Dan23584's Avatar
    Join Date
    Oct 2011
    Location
    Bristol
    Posts
    276
    Thanks
    11
    Thanked 26 Times
    in 25 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    Trunking will probably look better but it will be much more cost effective to go with SWA. I would choose the latter.
    <<<<<<<< If my post was helpful then your thanks would be appreciated :teeth_smile:

  5. #5
    Member
    Join Date
    Apr 2010
    Location
    Deepest, Darkest, Sheen
    Posts
    343
    Thanks
    83
    Thanked 27 Times
    in 23 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    Quote Originally Posted by BristolSpark View Post
    We were thinking 16mm 2 core SWA, use the armoured for cpc, clip it all up the side of the building.

    The only thing is what about the standard consumer units, they not really designed for swa as they are plastic. Any thoughts on termination into the D/B.
    What about installing one of these flush next to the CU, right where the CU entry cutouts are:

    http://www.******************/Products/BX333.html

    You can then terminate the swa into this and then run the cores up and through into the CU.

  6. #6
    Member
    Join Date
    Apr 2010
    Location
    Deepest, Darkest, Sheen
    Posts
    343
    Thanks
    83
    Thanked 27 Times
    in 23 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    OK, just go to T L C and do a search for BX 333.
    Murdoch likes this.

  7. #7
    Appreciated Member


    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    43,061
    Thanks
    984
    Thanked 5,282 Times
    in 4,930 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    make sure the |SWA is switch/fuse protected, and a good 16mm fly lead from the gland at the CU.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.

    It is a wise man who ignores the advice of fools, and a fool who ignores the advice of wise men


  8. #8
    Member
    Join Date
    Mar 2009
    Location
    Bristol
    Posts
    121
    Thanks
    3
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    The client said the previous electrician on a different flat used the exisiting supply and just installed new consumer unit. But the cable looks like a 10mm rather than 16mm.

    Also is there any restriction on the height of the consumer unit. ie.....may have to install board around 500mm off the floor. Cant see anything in the on-site guide.

  9. #9
    Electricians Arms Member

    Join Date
    Jan 2011
    Location
    China (Zhuhai)
    Posts
    16,179
    Thanks
    56
    Thanked 1,534 Times
    in 1,354 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    Quote Originally Posted by BristolSpark View Post
    Hi

    We have to install a 63A supply to a new consumer unit on a 2nd floor studio flat. The supply at present looks like it may have to feed from the switch on ground floor outside the property and up the wall before re-entering the 2nd floor studio flat.

    Any thoughts how best to go about this.

    SAW cable or trunking with 2 core and seprate earth. some advise and thoughts on this would be good.

    Cheers
    How are you going to be able to support the single cores in the trunking with strain relieve?? You can't just have them hanging in the trunking!! I'd Use 3 core SWA cable, as my first choice too...

  10. #10
    Member
    Join Date
    Mar 2009
    Location
    Bristol
    Posts
    121
    Thanks
    3
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    I agree the SWA sounds a far better option. I just to find a way to terminate it into a consumer unit. hey guys thanks for the advise.

  11. #11
    Electricians Arms Member

    Join Date
    Jan 2011
    Location
    China (Zhuhai)
    Posts
    16,179
    Thanks
    56
    Thanked 1,534 Times
    in 1,354 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    Quote Originally Posted by BristolSpark View Post
    I agree the SWA sounds a far better option. I just to find a way to terminate it into a consumer unit. hey guys thanks for the advise.
    A steel adaptable box springs to mind!! lol

  12. #12
    Member
    Join Date
    Mar 2009
    Location
    Bristol
    Posts
    121
    Thanks
    3
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    Yes sounds ok, but presentation will look awful. This D/B is gonna be on view lol...with a metal box in your face lol. need to find another way....

  13. #13
    Member
    Join Date
    Nov 2010
    Posts
    17
    Thanks
    8
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    Use a SWA brass earthing ring.

    20mm hole for the cable gland and 5mm hole for nut bolt and crimp connection.

    http://www.*************/search.do?fh_search=swa

    2.09 including gland, connect earth cable inside plastic C.U via the bolt.

  14. #14
    Member
    Join Date
    Nov 2010
    Posts
    17
    Thanks
    8
    Thanked 0 Times
    in 0 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    Hmm blocked from posting links wonder why?

    go to screw fix and look for IP66 66 gland Kit 20mm

    63 Amps seem high for a small apartment is there a big power shower or hot air heaters?

  15. #15
    Electricians Arms Member
    Join Date
    Nov 2010
    Location
    Essex
    Posts
    1,420
    Thanks
    20
    Thanked 113 Times
    in 111 Posts
    Tagged
    0 Thread(s)

    Default Re: 63A supply required for flat any thoughts on

    Why does the armour need to be used at the cu as it will be earthed at switch fuse and it would be a 3 core.

Everybody loves a good deal: Deals and Discounts on Dozens of Powertools!

Similar Threads

  1. New flat supply
    By J.C.E in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 8
    Last Post: 01-03-2014, 05:39 PM
  2. Thoughts on a supply
    By Spoon242 in forum Electrical Forum: General Electrical Forum
    Replies: 22
    Last Post: 07-09-2011, 07:54 AM
  3. garage supply and flat supply from meter
    By ianbrookes in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 1
    Last Post: 29-06-2011, 07:08 AM
  4. Thoughts on nuisance trip - Caused from another supply !!
    By ssizen in forum Electrical Forum: General Electrical Forum
    Replies: 9
    Last Post: 29-01-2011, 08:09 PM
  5. Any thoughts please.... flickering supply
    By sythai in forum Electrical Forum: General Electrical Forum
    Replies: 22
    Last Post: 13-10-2010, 07:47 AM

Visitors found this page by searching for:

running 63a supply to flats

Tags for this Thread


If you like our electrical forum, then perhaps checkout our Tiling Forum or even our professional and DIY Plumbing Forum.
Tens of thousands of tradesmen and over 2 million combined posts.


Electricians Forums is a Trading Style of Untold Developments Ltd.