Washing machine in bathroom issues

Discuss Washing machine in bathroom issues in the Electrical Wiring, Theories and Electrical Regulations at Electricians Forums Discussion Boards; During a PIR last week I found that the flat has its washing machine in an alcove/old airing cupboard with no door, in the bathroom. (I am going to try ...
  1. #1
    New to Electricians Forums
    Join Date
    Mar 2011
    Posts
    16
    Thanks
    18
    Thanked 0 Times in 0 Posts

    Default Washing machine in bathroom issues

    During a PIR last week I found that the flat has its washing machine in an alcove/old airing cupboard with no door, in the bathroom. (I am going to try and include a diagram of the bathroom with this post).
    FLAT 505 BATHROOM.jpg

     
    It is currently supplied via a dedicated RCD protected /circuit and single socket outlet.

    After double checking the regs, it seems it might be possible for it to remain in the cupboard if the following improvements are made.-
    1) A solid door with a keyed lock is fitted to alcove (then technically outside zone 2).
    2) The socket outlet changed to a switched fused connection unit.

    This mainly leaves only the ‘equipment must be suitable for the environment’ reg.
    To completely cover myself I am very much leaning towards saying to the owner that they need to re site the washing machine out side the bathroom, and disconnect the circuit. That’s easy to say in writing, and not impossible, but it is a small flat and it would require remodelling the fairly new looking kitchen.

    I was at a trade fair last week (Elex2011) and put the question to both NICEIC and ELECSA.
    One agreed with my suggestions of improvement above and said it would be ok, but document as such in report, and also said it would be a bit harsh to record as unsatisfactory for one non compliance/code1.

    The other said its not permitted due to the fact that the washing machine has been deemed not suitable for that environment (I confirmed this with manufacturer). Saying that although it would be technically outside the zone, condensation would/could form internally etc etc.

    Thanks for reading this, and I welcome all views, I need to conclude this asap, and sorry if this has been covered many time before, or posted in the wrong bit.


  2. #2
    Electricians Arms Member trev's Avatar
    Join Date
    Aug 2011
    Location
    Democratic People's Republic Of South Shields
    Posts
    6,345
    Thanks
    155
    Thanked 469 Times in 422 Posts

    Default Re: Washing machine in bathroom issues

    I was once asked to install a washing machine in a cupboard in a bathroom and because of the ambiguity I said flat out no.


  3. #3
    Electricians Arms Member mogga's Avatar
    Join Date
    Apr 2010
    Location
    Kirkintilloch by the canal
    Posts
    3,767
    Thanks
    81
    Thanked 379 Times in 332 Posts

    Default Re: Washing machine in bathroom issues

    this issue usually occurs from small one,2beds like my old grans where bathrooms have been added
    Personaly Id go for fitting a door to the alcove puting it outwith zones it is hard telling someone that the appliance they have had there for years and been using for years is deemed unsafe
    WONDERS WHEN niceic WILL HAVE A BOX ON CERTS "I WAS TOLD THIS IS OK BY GUYS ONLINE WHO HAVE NEVER SEEN THE INSTALLATION"

  4. #4
    Appreciated Member

    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    25,858
    Thanks
    647
    Thanked 3,576 Times in 3,300 Posts

    Default Re: Washing machine in bathroom issues

    IMO, the only thing tat should concern you re. a PIR is the position of the socket outlet. if it's within 3m of the bath, then it's a code 2. the washing machine itself is irrelevant.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.
    I don't suffer from Insanity. I enjoy every minute of it.


  5. #5
    DurhamSparky
    Guest

    Default Re: Washing machine in bathroom issues

    agreed with TEL

  6. #6
    Appreciated Member

    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    25,858
    Thanks
    647
    Thanked 3,576 Times in 3,300 Posts

    Default Re: Washing machine in bathroom issues

    thanks for that steve. when i saw you had posted, i thought i was going to get a torp. up the jacksie. lol.
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.
    I don't suffer from Insanity. I enjoy every minute of it.


  7. #7
    DurhamSparky
    Guest

    Default Re: Washing machine in bathroom issues

    im just getting my post count up...!!

    but if the washing machine was pushed right back and it was fitted with an IP outlet i might turn a blind eye and make it a 4

  8. #8
    Electricians Arms Member

    yellowvanman's Avatar
    Join Date
    Oct 2010
    Location
    Dorset
    Posts
    854
    Thanks
    32
    Thanked 138 Times in 126 Posts

    Default Re: Washing machine in bathroom issues

    As the washing machine is in zone 2 it needs to be splash proof (IPx4), if the manufacturer says its not then it shouldn't be there. Socket is the bathroom is a no no when less than 3m from bath.

    Not sure what is meant by
    ' bit harsh to record as unsatisfactory for one non compliance/code1.'
    a) the washing machine in zone 2 isn't a code 1
    b) the socket within 3m of bath is a code 1 in my view

    code 1 is a code 1 and presents an immediate danger no ifs or buts so unsatisfactory, not harsh in my view. Change to a SFS (i assume outside zone 2) and if manufacturer says washing machine is splash proof then all OK.

  9. #9
    Appreciated Member

    telectrix's Avatar
    Join Date
    Sep 2010
    Location
    cheshire/staffordshire
    Posts
    25,858
    Thanks
    647
    Thanked 3,576 Times in 3,300 Posts

    Default Re: Washing machine in bathroom issues

    i would still give it a code 2 as IMO it is not a real and immediate danger ( unless someone does something stupid like using a hair dryer in the bath. )
    TEL. Phd, MSc., Astro-physicist, Mathematical Genius, Compulsive Liar.
    I don't suffer from Insanity. I enjoy every minute of it.


  10. #10
    Electricians Arms Member

    yellowvanman's Avatar
    Join Date
    Oct 2010
    Location
    Dorset
    Posts
    854
    Thanks
    32
    Thanked 138 Times in 126 Posts

    Default Re: Washing machine in bathroom issues

    Quote Originally Posted by telectrix View Post
    i would still give it a code 2 as IMO it is not a real and immediate danger ( unless someone does something stupid like using a hair dryer in the bath. )
    Its a close call and its this sort of process that produces inconsistencies between different people, not that I'm saying your wrong!

    I hope the new Condition Report is able to provide a bit more consistency.

  11. #11
    New to Electricians Forums
    Join Date
    Mar 2011
    Posts
    16
    Thanks
    18
    Thanked 0 Times in 0 Posts

    Default Re: Washing machine in bathroom issues

    Thanks to all of you who have replied so far, if a door with a lock requiring a key to open it was fitted, could it be considered as not in zone 2? Ok so then they put a washing load in, set it off, cupboard door is still propped open with the laundry basket and they jump in the shower, very possible i think.

  12. #12
    Electricians Arms Member
    Join Date
    Jan 2011
    Location
    China (Zhuhai)
    Posts
    9,715
    Thanks
    41
    Thanked 1,135 Times in 981 Posts

    Default Re: Washing machine in bathroom issues

    Haha, ...This is an everyday common occurance in Cyprus, to have washing machines/tumble dryers in cupboards within bathrooms and upstairs landing cupboards. Never once heard of anyone getting belted or dying from the practice. Not particually what i would like in a bathroom or anywhere upstairs , but it's just normal over there. Were not talking about tiny apartments here either, think anything from 1 to 5 bed flats and villas/houses...

  13. #13
    Electricians Arms Member spinlondon's Avatar
    Join Date
    Dec 2010
    Location
    London East
    Posts
    4,810
    Thanks
    64
    Thanked 835 Times in 733 Posts

    Default Re: Washing machine in bathroom issues

    The cupboard doesn't require a lock and key, just a door for the cupboard to be outside of the location.
    The washing machine is very likely to be IPX4.
    Either replace door, or change socket-outlet to an FCU rated at IPX4.

  14. #14
    Electricians Arms Member MarkieSparkie's Avatar
    Join Date
    Feb 2011
    Location
    Weymouth
    Posts
    5,026
    Thanks
    45
    Thanked 1,075 Times in 837 Posts

    Default Re: Washing machine in bathroom issues

    If the bathroom is force ventilated the condensation issue should be minimal. Whilst putting a door on the alcove to create a utility cupboard/room seems a good idea. My main worry and concern about doing so, is the unattended operation of a washing machine located in a cupboard, although this prevents direct access to the equipment, it could increase the fire risk by reducing the airflow in and around the machine and the possibility of poor venting, leading to increased operating temperatures. If the machine is a washer/drier the build up and trapping of cotton lint from the clothing leading to a combustible atmosphere would increase the fire risk. There are about 1400 washing machine and tumble drier related fires in domestic premises every year so this is a real and potential risk.
    Please click the 'Like' button if you found this post helpful, witty or interesting.

  15. #15
    New to Electricians Forums
    Join Date
    Aug 2010
    Posts
    16
    Thanks
    1
    Thanked 3 Times in 3 Posts

    Default Re: Washing machine in bathroom issues

    Even a code 2 could be un satisfactory, looking at your drawing I would suggest removal.

Page 1 of 2 12 LastLast

Similar Threads

  1. Hi
    By Chris in forum New Member Introductions
    Replies: 12
    Last Post: 07-01-2013, 05:23 PM
  2. Washing machine brushes
    By Richard Burns in forum Electrical Forum, General Electrical Forum
    Replies: 10
    Last Post: 07-08-2012, 07:25 PM
  3. Domestic Washing machine.
    By mickys86 in forum Electrical Forum, General Electrical Forum
    Replies: 6
    Last Post: 14-06-2012, 06:23 PM
  4. Domestic Washing machine tripping RCD
    By joolzhaines in forum Electrical Forum, General Electrical Forum
    Replies: 23
    Last Post: 07-06-2012, 04:41 PM
  5. Washing Machine not on RCD
    By Ed Solder in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 14
    Last Post: 11-01-2012, 07:21 AM
  6. is this the best way to connect a washing machine?
    By salopboy in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 2
    Last Post: 02-02-2011, 05:07 PM
  7. washing machine into a fcu?
    By Gerry24 in forum Electrical Forum, General Electrical Forum
    Replies: 4
    Last Post: 18-12-2010, 09:50 PM
  8. Hog roast from a washing machine...
    By a12jpm in forum Electrical Forum, General Electrical Forum
    Replies: 16
    Last Post: 29-06-2010, 02:10 AM
  9. Washing Machine in bathroom!
    By andrew692003 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 13
    Last Post: 20-01-2010, 10:45 PM
  10. washing machine in bathroom
    By lister in forum Electrical Forum, General Electrical Forum
    Replies: 5
    Last Post: 02-02-2009, 12:06 AM

Visitors found this page by searching for:

can you put a washing machine in a bathroom

washing machine in bathroom ideas

washing machine in bathroom

washing machine in bathroom cupboard

washing machine in bathroom regulations

washing machine cupboard bathroom

can a washing machine be put in a bathroom

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Electricians Forums is a Trading Style of Untold Developments Ltd. Search Engine Optimisation, Web Development and Online Marketing for the UK.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31