- 30-06-2009 #1
New consumer unit on TT Supply - whats the regs.
Hi , Got to replace consumer unit on my property (to use as my part p assesment !) At the moment its TT Supply (with earth rod) and feeds to the consumer unit through a 100mA RCD. It is only a small cottage and has the following circuits - Garage supply,cooker,2 x socket ring mains,central heating boiler and 1 lighting circuit.
In order to please the part p assesors whats the best way to play it after ensuring the Ze to be less than 200 ohms (i'm working on this !). Is the 100mA rcd ok or do I need to dropdown to 30mA ?
Can anyone tell me / explain the best /cheapest way to fit new consumer unit to meet current regs on a small domestic TT Supply ?
Thanks - Chris.
- 30-06-2009 #2
Re: New consumer unit on TT Supply - whats the regs.
What we offered here... Earth fault loop impedance reading on TT System in domestic premises
...still stands, Chris. The Regs aint changed in 4 days!
Is there a specific question you don`t feel has been answered satisfactorily?
Re: the Q`s in this post; as already stated you`ll need 30mA RCD`s for any bathroom/shower room circuits + socket outlets + for ccts with cables installed in walls at less than 50mm. As that`s likely gonna include your lighting circuits (& you`ll need 2 or more) you`ll require 2 or more RCD devices (could alternatively be RCCB or RCB0) so as to provide discrimination between devices.
Basically, nowadays TT`s are much the same as TN`s in requirements for CU`s
The 100mA is required only for ccts not requiring the `Additional Protection` of 30mA RCDs, would have to be of the `S` type (delayed) for discrimination of devices, & may be done away with entirely if you can meet the applicable criteria listed at table 41.1 of the Regs. (then you adopt TN values)
Seriously mate, you`ll have to read up on the Regs to get thru your assessment, so have a peak now
On the Ze front, while the official figure is min 200ohms, i`m pretty sure the NIC require 100 (which i`d always look to get even tho` i aint with them) so if it`s an NICe assessment you`ll need <100ohms
Hope that clarifies it further for youLast edited by electricAl; 30-06-2009 at 10:58 PM.
Two heads are better than one - even when they`re sheep`s
- 15-11-2009 #3
Re: New consumer unit on TT Supply - whats the regs.
like Al said. as long as your Ze is less than 100 ohms and you fit a dual Rcd board (1 80 amp and one 63 amp rcd, both 30mA) you will be fine. if i was you id put the, garage, cooker and one ring on the 1st rcd, the other ring, heating and lights on the other. The MK sentry split load board is a gd one to use.
- 15-11-2009 #4Senior Member
- Join Date
- Nov 2007
- Location
- Somewhere near Reading
- Posts
- 135
- Thanks
- 0
- Thanked 0 Times in 0 Posts
Re: New consumer unit on TT Supply - whats the regs.
Seen as you only have 6 circuits why not put in rcbo's & if you use an insulated cu do away with the 100mA rcd.
- 15-11-2009 #5
Re: New consumer unit on TT Supply - whats the regs.
rcbo's do cost abit more tho but yh that is another option. the mk split load board will come with the main switch and the 2 rcd's.
also make sure the earth to the rod is 16mmLast edited by willosparky; 15-11-2009 at 08:36 PM.
- 15-11-2009 #6Super Moderator
- Join Date
- Dec 2008
- Location
- South Wales
- Posts
- 5,524
- Thanks
- 2
- Thanked 7 Times in 2 Posts
Re: New consumer unit on TT Supply - whats the regs.
My guess is he'll have sorted it by now as the thread is 6 months old.
- 15-11-2009 #7
- 15-11-2009 #8
Re: New consumer unit on TT Supply - whats the regs.
Fair enough but accuracy is always appreciated by those looking for help.
The board you are referring to would actually be classed as a `High Integrity` board - not split load which offer some ways Rccb protected and some unprotected - as in 16th Edition.Two heads are better than one - even when they`re sheep`s
Similar Threads
-
New Consumer unit advise
By tickover in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 11Last Post: 06-11-2009, 03:24 PM -
Assesing suitability for RCD Consumer unit
By whitebeetle in forum Electrical Forum | General Electrical ForumReplies: 5Last Post: 30-06-2009, 10:29 PM -
Installing new consumer unit. Cables too short.
By Dave0098 in forum Electrical Wiring, Theories and Electrical RegulationsReplies: 26Last Post: 07-06-2009, 05:42 PM -
Supply to con unit?
By ian t in forum Electrical Forum | General Electrical ForumReplies: 9Last Post: 19-01-2009, 12:47 AM -
Electric Shower & Consumer Unit within my flat
By Southsider in forum Electrical Forum | General Electrical ForumReplies: 11Last Post: 04-08-2008, 10:46 PM



LinkBack URL
About LinkBacks



Reply With Quote







Bookmarks