    Default New consumer unit on TT Supply - whats the regs.

    Hi , Got to replace consumer unit on my property (to use as my part p assesment !) At the moment its TT Supply (with earth rod) and feeds to the consumer unit through a 100mA RCD. It is only a small cottage and has the following circuits - Garage supply,cooker,2 x socket ring mains,central heating boiler and 1 lighting circuit.

    In order to please the part p assesors whats the best way to play it after ensuring the Ze to be less than 200 ohms (i'm working on this !). Is the 100mA rcd ok or do I need to dropdown to 30mA ?

    Can anyone tell me / explain the best /cheapest way to fit new consumer unit to meet current regs on a small domestic TT Supply ?

    Thanks - Chris.

  2. #2
    Electricians Arms Member electricAl's Avatar
    Join Date
    Dec 2008
    Posts
    388
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: New consumer unit on TT Supply - whats the regs.

    What we offered here... Earth fault loop impedance reading on TT System in domestic premises

    ...still stands, Chris. The Regs aint changed in 4 days!

    Is there a specific question you don`t feel has been answered satisfactorily?



    Re: the Q`s in this post; as already stated you`ll need 30mA RCD`s for any bathroom/shower room circuits + socket outlets + for ccts with cables installed in walls at less than 50mm. As that`s likely gonna include your lighting circuits (& you`ll need 2 or more) you`ll require 2 or more RCD devices (could alternatively be RCCB or RCB0) so as to provide discrimination between devices.

    Basically, nowadays TT`s are much the same as TN`s in requirements for CU`s

    The 100mA is required only for ccts not requiring the `Additional Protection` of 30mA RCDs, would have to be of the `S` type (delayed) for discrimination of devices, & may be done away with entirely if you can meet the applicable criteria listed at table 41.1 of the Regs. (then you adopt TN values)

    Seriously mate, you`ll have to read up on the Regs to get thru your assessment, so have a peak now

    On the Ze front, while the official figure is min 200ohms, i`m pretty sure the NIC require 100 (which i`d always look to get even tho` i aint with them) so if it`s an NICe assessment you`ll need <100ohms

    Hope that clarifies it further for you
    Last edited by electricAl; 30-06-2009 at 10:58 PM.
    Two heads are better than one - even when they`re sheep`s

  3. #3
    Junior Member willosparky's Avatar
    Join Date
    Nov 2009
    Posts
    23
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: New consumer unit on TT Supply - whats the regs.

    like Al said. as long as your Ze is less than 100 ohms and you fit a dual Rcd board (1 80 amp and one 63 amp rcd, both 30mA) you will be fine. if i was you id put the, garage, cooker and one ring on the 1st rcd, the other ring, heating and lights on the other. The MK sentry split load board is a gd one to use.

  4. #4
    Senior Member not clever's Avatar
    Join Date
    Nov 2007
    Location
    Somewhere near Reading
    Posts
    135
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: New consumer unit on TT Supply - whats the regs.

    Seen as you only have 6 circuits why not put in rcbo's & if you use an insulated cu do away with the 100mA rcd.

  5. #5
    Junior Member willosparky's Avatar
    Join Date
    Nov 2009
    Posts
    23
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: New consumer unit on TT Supply - whats the regs.

    rcbo's do cost abit more tho but yh that is another option. the mk split load board will come with the main switch and the 2 rcd's.

    also make sure the earth to the rod is 16mm
    Last edited by willosparky; 15-11-2009 at 08:36 PM.

  6. #6
    Super Moderator Lenny's Avatar
    Join Date
    Dec 2008
    Location
    South Wales
    Posts
    5,524
    Thanks
    2
    Thanked 7 Times in 2 Posts

    Default Re: New consumer unit on TT Supply - whats the regs.

    My guess is he'll have sorted it by now as the thread is 6 months old.

  7. #7
    Junior Member willosparky's Avatar
    Join Date
    Nov 2009
    Posts
    23
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: New consumer unit on TT Supply - whats the regs.

    Quote Originally Posted by lennytheloon View Post
    My guess is he'll have sorted it by now as the thread is 6 months old.
    true but was replying just incase also may help someone else with same question

  8. #8
    Electricians Arms Member electricAl's Avatar
    Join Date
    Dec 2008
    Posts
    388
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: New consumer unit on TT Supply - whats the regs.

    Fair enough but accuracy is always appreciated by those looking for help.

    The board you are referring to would actually be classed as a `High Integrity` board - not split load which offer some ways Rccb protected and some unprotected - as in 16th Edition.
    Two heads are better than one - even when they`re sheep`s

Similar Threads

  1. New Consumer unit advise
    By tickover in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 11
    Last Post: 06-11-2009, 03:24 PM
  2. Assesing suitability for RCD Consumer unit
    By whitebeetle in forum Electrical Forum | General Electrical Forum
    Replies: 5
    Last Post: 30-06-2009, 10:29 PM
  3. Installing new consumer unit. Cables too short.
    By Dave0098 in forum Electrical Wiring, Theories and Electrical Regulations
    Replies: 26
    Last Post: 07-06-2009, 05:42 PM
  4. Supply to con unit?
    By ian t in forum Electrical Forum | General Electrical Forum
    Replies: 9
    Last Post: 19-01-2009, 12:47 AM
  5. Electric Shower & Consumer Unit within my flat
    By Southsider in forum Electrical Forum | General Electrical Forum
    Replies: 11
    Last Post: 04-08-2008, 10:46 PM

Visitors found this page by searching for:

Nobody landed on this page from a search engine, yet!

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24